We're aiming to put an electrically heated (as well as CH heated)
towel rail in the new shower/wet room. How are these normally switched
on and off?

Possibilities seem to me to be:-

1 Pull switch, but this feels wrong for a towel rail somehow, also
difficult to provide a clear indicator, a little glow by the
switch on the ceiling isn't very obvious.

2 Normal switch outside the wet-room. Possible but again seems
rather counter-intuitive, though one could at least have a nice
obvious 'on' indicator.

3 A switch in the wet room but outside the zones. This is fairly
easy in this case as the switch could be positioned on the soil
pipe casing on the opposite side of the wet-room from the shower.

4 A Quinetic switch, but this doesn't have an indicator so I'd have
to add that as well, a rather expensive solution in total. Can
one get 'indicator' lamps as stand-alone accessories?

5 One could get all clever and have a low voltage (SELV) switch and
circuit controlling a contactor/relay but this does seem a bit
OTT.

The third option seems most "easy to use and find" but is it actually
OK? Can one get switches which are particularly suitable for
damp[ish] locations?

If I go for the Quinetic switch option it would make sense to get a
dual controller as I'm aiming to use a Quinetic switch for the lights.
However this raises the issue of what to connect it all to. All the
towel radiator electric heaters say they must be run from an FCU but I
guess they are assuming being connected to a power circuit with 32A or
20A breaker. Can I connect the heater direct to a lighting circuit as
this is what I would be connecting the lighting Quinetic switch to.
It will have a 6A breaker so I can't really se an issue with this.
The instructions for the Screwfix ones say "The fused spur should be
fitted with at least a 5 amp fuse to the appropriate standard." which
doesn't make a lot of sense! Would a 13 amp fuse be better?? :-)

--
Chris Green
·

spuorg...@gowanhill.com

unread,
Aug 22, 2019, 2:33:43 PM8/22/19
to
On Thursday, 22 August 2019 19:16:05 UTC+1, Chris Green wrote:
> Can one get 'indicator' lamps as stand-alone accessories?

Gridswitch plate with a neon module.

> The third option seems most "easy to use and find" but is it actually
> OK? Can one get switches which are particularly suitable for
> damp[ish] locations?

You can but they tend to be a bit horticultural :-)

I would probably go for a pull switch with a separate indicating module outside the room door, if leaving the thing on and forgetting it is an issue. Or even a runback timer switch so it runs for eg 2 hours to warm the room / dry the towels, then turns off.

Owain

Bill Wright

unread,
Aug 22, 2019, 3:57:06 PM8/22/19
to
On 22/08/2019 19:09, Chris Green wrote:
> We're aiming to put an electrically heated (as well as CH heated)
> towel rail in the new shower/wet room. How are these normally switched
> on and off?

In the end I simply fitted a 30A DP with neon switched spur outside the
room next to the shower switch. This was a few years ago. In reality we
never use the electric because when it's cold enough to need extra
heating in the wet room because the central heating is on. The thing we
did right was to have a big radiator in the wetroom, so it's always
really warm in there. This is what you need when you are bathing a
disabled person. Wetrooms need to be really warm.

Bill

David

unread,
Aug 22, 2019, 5:00:34 PM8/22/19
to
On Thursday, 22 August 2019 19:16:05 UTC+1, Chris Green wrote:
> We're aiming to put an electrically heated (as well as CH heated)
> towel rail in the new shower/wet room. How are these normally switched
> on and off?

A relative of mine has an electric towel radiator. It takes hours to heat up, so he leaves it on 24/7. Otherwise he'd have to plan in advance, which isn't going to happen...

ARW

unread,
Aug 22, 2019, 5:28:52 PM8/22/19
to
On 22/08/2019 19:09, Chris Green wrote:
> We're aiming to put an electrically heated (as well as CH heated)
> towel rail in the new shower/wet room. How are these normally switched
> on and off?
>
> Possibilities seem to me to be:-
>
> 1 Pull switch, but this feels wrong for a towel rail somehow, also
> difficult to provide a clear indicator, a little glow by the
> switch on the ceiling isn't very obvious.

So fit one with an ON/OFF flag

> 2 Normal switch outside the wet-room. Possible but again seems
> rather counter-intuitive, though one could at least have a nice
> obvious 'on' indicator.


Normal switches have a on and off position.

> 3 A switch in the wet room but outside the zones. This is fairly
> easy in this case as the switch could be positioned on the soil
> pipe casing on the opposite side of the wet-room from the shower.


Why not?

> 4 A Quinetic switch, but this doesn't have an indicator so I'd have
> to add that as well, a rather expensive solution in total. Can
> one get 'indicator' lamps as stand-alone accessories?

Overkill

> 5 One could get all clever and have a low voltage (SELV) switch and
> circuit controlling a contactor/relay but this does seem a bit
> OTT.

Overkill


> The third option seems most "easy to use and find" but is it actually
> OK? Can one get switches which are particularly suitable for
> damp[ish] locations?

Is the switch likely to get wet?


--
Adam

Chris Green

unread,
Aug 22, 2019, 5:33:05 PM8/22/19
to
Yes, I'm aiming to get a 400 watt or 600 watt heater which shoudn't
take a huge time to get hot.

--
Chris Green
·

Chris Green

unread,
Aug 22, 2019, 5:33:05 PM8/22/19
to
Bill Wright <wrights...@f2s.com> wrote:
> On 22/08/2019 19:09, Chris Green wrote:
> > We're aiming to put an electrically heated (as well as CH heated)
> > towel rail in the new shower/wet room. How are these normally switched
> > on and off?
>
> In the end I simply fitted a 30A DP with neon switched spur outside the
> room next to the shower switch.

Overkill for a 400 watt heater! :-)

> This was a few years ago. In reality we
> never use the electric because when it's cold enough to need extra
> heating in the wet room because the central heating is on. The thing we
> did right was to have a big radiator in the wetroom, so it's always
> really warm in there. This is what you need when you are bathing a
> disabled person. Wetrooms need to be really warm.
>
The electric heater is really to get towels dry in the summer.

--
Chris Green
·

John Rumm

unread,
Aug 22, 2019, 6:52:35 PM8/22/19
to
On 22/08/2019 19:09, Chris Green wrote:
> We're aiming to put an electrically heated (as well as CH heated)
> towel rail in the new shower/wet room. How are these normally switched
> on and off?

How about a runback timer triggered either from a pipe stat (mixer
shower), or a current operated switch [1] (electric shower)?

That way it would turn on when the shower starts, and off a few hours
after its finished. No need to remember to turn it on or off.

[1] http://wiki.diyfaq.org.uk/index.php/Current_activated_switch



--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Bill Wright

unread,
Aug 22, 2019, 11:36:21 PM8/22/19
to
On 22/08/2019 22:16, Chris Green wrote:
> Bill Wright <wrights...@f2s.com> wrote:
>> On 22/08/2019 19:09, Chris Green wrote:
>>> We're aiming to put an electrically heated (as well as CH heated)
>>> towel rail in the new shower/wet room. How are these normally switched
>>> on and off?
>>
>> In the end I simply fitted a 30A DP with neon switched spur outside the
>> room next to the shower switch.
>
> Overkill for a 400 watt heater! :-)

It was 600W. And it was an appearance match to the main shower switch
and the one for the extractor. And I couldn't be arsed buying different
ones.


>>
> The electric heater is really to get towels dry in the summer.
>


I see. I know I'm weird but I take towels to the wash as soon as they're
significantly damp. I'm very profligate with the washing machines.

Sort of moving on a bit, it's surprising how much washing is generated
by certain types of disability. It comes down to having a lot of
garments in circulation and just not worrying about the electric bill.
That's what PIP is for I guess.

The amount of clinical waste and soiled incontinence products is also
vast. Doncaster Council could offer no help; no big surprise.

I went through this twice, once with my dad and once with my wife.

Anyway, these matters are now behind me. I suppose this is as good a
place to mention it as any, but my beloved wife Hilary died on the 7th
August. I am utterly heartbroken.

Bill

Bill Wright

unread,
Aug 22, 2019, 11:37:29 PM8/22/19
to
They aren't quick. And they don't do much to dry towels unless you leave
them on 24/7.

Bill

Tim+

unread,
Aug 23, 2019, 2:24:46 AM8/23/19
to
So sorry to hear this Bill. I don’t think your father could have had a
more loving son or your wife a more loving husband.


Tim

--
Please don't feed the trolls

spuorg...@gowanhill.com

unread,
Aug 23, 2019, 4:13:04 AM8/23/19
to
On Friday, 23 August 2019 04:36:21 UTC+1, Bill Wright wrote:
> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.

*** condolences ***

Owain

Chris Green

unread,
Aug 23, 2019, 4:16:08 AM8/23/19
to
Bill Wright <wrights...@f2s.com> wrote:
>
> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.
>
I'm sorry to hear that Bill, I don't always agree with you but I still
feel for your loss.

--
Chris Green
·

charles

unread,
Aug 23, 2019, 4:48:55 AM8/23/19
to

On Friday, 23 August 2019 04:36:21 UTC+1, Bill Wright wrote:
> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.


Bill

I'm very sorry to hear that.

Charles

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle

Tim Lamb

unread,
Aug 23, 2019, 4:51:52 AM8/23/19
to
In message <qjnmvi$cnk$1...@gioia.aioe.org>, Bill Wright
<wrights...@f2s.com> writes
>Anyway, these matters are now behind me. I suppose this is as good a
>place to mention it as any, but my beloved wife Hilary died on the 7th
>August. I am utterly heartbroken.

Bill. I am sorry. Look back on the good times and consider she would not
have wanted you to suffer.

--
Tim Lamb

Andy Burns

unread,
Aug 23, 2019, 4:58:33 AM8/23/19
to
Bill Wright wrote:

> my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.

Very sorry to hear that Bill, take care of yourself.

Dave Liquorice

unread,
Aug 23, 2019, 5:23:11 AM8/23/19
to
On Fri, 23 Aug 2019 04:36:20 +0100, Bill Wright wrote:

> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.

Sorry to hear that Bill, Unfortunately one of very few cast iron
guarantees that comes with life. I hope you can draw strength from
the support shown by your uk.d-i-y friends.

--
Cheers
Dave.



Adrian Caspersz

unread,
Aug 23, 2019, 5:30:16 AM8/23/19
to
On 22/08/2019 19:09, Chris Green wrote:
> We're aiming to put an electrically heated (as well as CH heated)
> towel rail in the new shower/wet room. How are these normally switched
> on and off?

>
> 5 One could get all clever and ...

Drill a 5inch hole in the wall.

With automation and string, drag the wet though and up a flag pole to
dry in the wind. On timer bring towels back, or swap to backup towel, if
outside humidity or wind don't present ideal drying conditions.

--
Adrian C

Dave Liquorice

unread,
Aug 23, 2019, 5:35:51 AM8/23/19
to
On Fri, 23 Aug 2019 04:37:29 +0100, Bill Wright wrote:

>>>> We're aiming to put an electrically heated (as well as CH
heated)
>>>> towel rail in the new shower/wet room. How are these normally
>>>> switched on and off?
>>>
>>> A relative of mine has an electric towel radiator. It takes hours
to
>>> heat up, so he leaves it on 24/7.
>>
>> Yes, I'm aiming to get a 400 watt or 600 watt heater which
shoudn't
>> take a huge time to get hot.
>
> They aren't quick. And they don't do much to dry towels unless you leave
> them on 24/7.

That surprises me but made me think: Why?

2 seconds of engaged brain and it obvious that the heat input has to
be *significantly* more than the rated heat output of the towel rail
otherwise it'll be losing heat almost as fast as it's been supplied.

Position/orientation of the heater might be important as well, you
want to set up a decent gravity flow within the towel rail to shift
the heat from the vicinty of the element to the rest of the rail.

Switches, you can get dedicated towel rail "run back" type switches.
Sort of thing where you press a button and it cycles through 1hr,
2hr, 3hr, off.

--
Cheers
Dave.



Jeff Layman

unread,
Aug 23, 2019, 6:22:41 AM8/23/19
to
On 23/08/19 04:36, Bill Wright wrote:

> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.
>
> Bill

Sincere condolences Bill.

--

Jeff

The Natural Philosopher

unread,
Aug 23, 2019, 6:38:53 AM8/23/19
to
Fuck thats crap.


--
"I guess a rattlesnake ain't risponsible fer bein' a rattlesnake, but ah
puts mah heel on um jess the same if'n I catches him around mah chillun".

John Rumm

unread,
Aug 23, 2019, 7:15:49 AM8/23/19
to
On 23/08/2019 04:36, Bill Wright wrote:

> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.

So sorry to hear that Bill. Not much I can say that can make it any
better I am sure, but hang on in there!

Bill Wright

unread,
Aug 23, 2019, 12:01:03 PM8/23/19
to
On 23/08/2019 07:24, Tim+ wrote:

>> Anyway, these matters are now behind me. I suppose this is as good a
>> place to mention it as any, but my beloved wife Hilary died on the 7th
>> August. I am utterly heartbroken.
>>
>> Bill
>>
>
> So sorry to hear this Bill. I don’t think your father could have had a
> more loving son or your wife a more loving husband.
>
>
> Tim
>

Thank you. It's been hard, and now in some ways it's harder. I have a
hard road ahead.

The funeral collection raised £702.50 for the Rotherham Hospice. It's a
very good cause. I chatted with the secretary for a while and she told
me that they get a grant of £2.5 million per annum from the NHS, but
their running costs are over five million, so all the rest has to come
from fund raising and donations.

Bill

Bill Wright

unread,
Aug 23, 2019, 12:01:37 PM8/23/19
to
Well you'd be a right old nutter if you agreed with me!

Bill

Bill Wright

unread,
Aug 23, 2019, 12:02:31 PM8/23/19
to
On 23/08/2019 09:41, charles wrote:
> On Friday, 23 August 2019 04:36:21 UTC+1, Bill Wright wrote:
>> Anyway, these matters are now behind me. I suppose this is as good a
>> place to mention it as any, but my beloved wife Hilary died on the 7th
>> August. I am utterly heartbroken.
>
>
> Bill
>
> I'm very sorry to hear that.
>
> Charles
>

Thanks Charles.

Bill

Bill Wright

unread,
Aug 23, 2019, 12:03:57 PM8/23/19
to
I'm just glad she went first because I can't bear to think of her
suffering the sadness and desolation I now feel.

Bill

Bill Wright

unread,
Aug 23, 2019, 12:05:22 PM8/23/19
to
Thank you. The kids are being absolutely great. Both girls seem to think
I need 3,000 calories per day, and both are providing it.

Fat Bill

Bill Wright

unread,
Aug 23, 2019, 12:05:45 PM8/23/19
to
Yes I think I will.

Bill

Bill Wright

unread,
Aug 23, 2019, 12:06:01 PM8/23/19
to
Thank you.

Bill

Bill Wright

unread,
Aug 23, 2019, 12:06:38 PM8/23/19
to
On 23/08/2019 12:15, John Rumm wrote:
> On 23/08/2019 04:36, Bill Wright wrote:
>
>> Anyway, these matters are now behind me. I suppose this is as good a
>> place to mention it as any, but my beloved wife Hilary died on the 7th
>> August. I am utterly heartbroken.
>
> So sorry to hear that Bill. Not much I can say that can make it any
> better I am sure, but hang on in there!
>
>
Thank you John.

Bill

ARW

unread,
Aug 23, 2019, 1:28:02 PM8/23/19
to
On 23/08/2019 04:36, Bill Wright wrote:

> Anyway, these matters are now behind me. I suppose this is as good a
> place to mention it as any, but my beloved wife Hilary died on the 7th
> August. I am utterly heartbroken.

Sorry to hear that. You said she was ill when I called in for that
printer for the Scouts that you gave away.


--
Adam
0 new messages