On 09/01/2012 19:42, Mathew Newton wrote:
That sounds to me like too high a charge pressure if the static pressure
of the incoming mains is only 2 bar. When cold, the water in the
cylinder will be at 2 bar, but when it heats up it will very rapidly
reach 3 bar in order to be able to compress the air in the expansion
vessel. A more gentle expansion would be better.
Is there a pressure relief valve which spills water to the outside world
once a certain pressure is exceeded? What is that set at?
I would be inclined to reduce the charge pressure to 2 bar, and see what
happens.
If all else fails, you may need to do some calculations! If you know the
capacities of the cylinder and of the expansion vessel and the charge
pressure, you can work out what the rise in pressure will be when the
water is heated from (say) 5 degrees to 60 degrees - and make sure that
this is below the blow-off pressure.
--
Cheers,
Roger