Would 10 mm microbore be ample to feed a 5 ring range cooker or would i need
15mm copper tubing.

have built extension so need to reroute gas suppply by about 15 m so
microbore would be easier on my proposed route. would this beableto feed
enough gas through

thanks

mick


Dave Jones

unread,
Oct 6, 2005, 3:05:04 PM10/6/05
to

"mick" <mickmo...@blueyonder.co.uk> wrote in message
news:Mte1f.58238$VI6....@fe1.news.blueyonder.co.uk...

I take it your not a competent person then!


Brian G

unread,
Oct 6, 2005, 4:22:12 PM10/6/05
to


Mick,

Bear in mind that you are legally responsible for the work that you do on
the gas side if things if it goes wrong. And if they do, you will be
standing before the fella with red robes and white wig who could give you a
spell at her majesty's pleasure - presuming of course you survive the
'bang'.

If your post was a light hearted send-up - fair enough. If it WAS a serious
question, then please seek some professional advice from a qualified gas
fitter.

Oh! And to answer the question - no!

All the best

Brian G


Ed Sirett

unread,
Oct 6, 2005, 5:29:18 PM10/6/05
to

It can support (assuming the pipe came straight from the meter)
0.3 m^3/hr which is 38,600/3600 *0.3 = 3.2kW

If you don't what that means then get some in to do it in 15mm.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


mick

unread,
Oct 7, 2005, 3:27:30 PM10/7/05
to
Thanks Ed.
The main burner puts out 3.7Kw so i guess 15mm it is
Thank you

"Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
news:pan.2005.10.06...@makewrite.demon.co.uk...

Andy Wade

unread,
Oct 8, 2005, 8:35:57 AM10/8/05
to
Ed Sirett wrote:

> It can support (assuming the pipe came straight from the meter)
> 0.3 m^3/hr

Surely the length of the pipe has to come into the calculation (flow
rate for 1 mb end-end pressure drop)?

--
Andy

Rob Morley

unread,
Oct 8, 2005, 9:56:04 AM10/8/05
to
In article <4347bd2d$0$30311$da0f...@news.zen.co.uk>,
spamb...@ajwade.clara.co.uk says...
OP mentioned 15 metres

Ed Sirett

unread,
Oct 8, 2005, 4:59:19 PM10/8/05
to


Which is the length I took and used to look up.

Rob Morley

unread,
Oct 8, 2005, 6:22:56 PM10/8/05
to
In article <pan.2005.10.08....@makewrite.demon.co.uk>,
e...@makewrite.demon.co.uk says...

> On Sat, 08 Oct 2005 14:56:04 +0100, Rob Morley wrote:
>
> > In article <4347bd2d$0$30311$da0f...@news.zen.co.uk>,
> > spamb...@ajwade.clara.co.uk says...
> >> Ed Sirett wrote:
> >>
> >> > It can support (assuming the pipe came straight from the meter)
> >> > 0.3 m^3/hr
> >>
> >> Surely the length of the pipe has to come into the calculation (flow
> >> rate for 1 mb end-end pressure drop)?
> >>
> > OP mentioned 15 metres
>
>
> Which is the length I took and used to look up.
>
>
I thought you probably did :-)

Andy Wade

unread,
Oct 9, 2005, 5:12:54 AM10/9/05
to
Rob Morley wrote:

> In article <pan.2005.10.08....@makewrite.demon.co.uk>,
> e...@makewrite.demon.co.uk says...
>
>>On Sat, 08 Oct 2005 14:56:04 +0100, Rob Morley wrote:
>>
>>>In article <4347bd2d$0$30311$da0f...@news.zen.co.uk>,
>>>spamb...@ajwade.clara.co.uk says...
>>>
>>>>Ed Sirett wrote:
>>>>
>>>>>It can support (assuming the pipe came straight from the meter)
>>>>>0.3 m^3/hr
>>>>
>>>>Surely the length of the pipe has to come into the calculation (flow
>>>>rate for 1 mb end-end pressure drop)?
>>>
>>>OP mentioned 15 metres
>>
>>
>>Which is the length I took and used to look up.
>
> I thought you probably did :-)

And which I missed. Apologies.

--