On 20/04/2012 10:04, Adam Funk wrote:
> On 2012-04-19, ARWadsworth wrote:
>
>>
tin...@isbd.co.uk wrote:
>>> I am installing a new built-in oven and hit the usual problem of the
>>> horrible connectors they always seem to come with
>>
>>
>>> The oven is rated 2.3kw so 2.5sq mm is perfectly adequate, the problem
>>> is that it's not ideal for allowing the oven to be slid in and out and
>>> it's not properly protected by the 32amp MCB.
>>
>> There is a very good chance the 2.5 T&E will be adequately protected by the
>> 32A MCB.
>>
>>
>> However I now suspect that you have just unleashed the pillock from
>> Birmingham and we can now expect a load of ranting and bollocks about the
>> dangers (made up ones) of installing unfused spurs using 2.5 T&E on a 32A
>> circuit.
>
> I'm not looking for an argument (or even a good session of
> contradiction), but I was under the impression that 2.5 T&E wasn't
> rated for 32 A in any situation,
You are right its not...
However in this case, we are not designing that part of the installation
to carry 32A, or anything close to it.
This is one of those situations where the responsibility for fault and
overload protection can be split. The fault protection must always be at
the origin of the circuit, and must in the event of a fault ensure that
the circuit is disconnected quickly enough to avoid (possibly further)
cable damage (5 secs typically on a fixed appliance). Overload
protection is also usually at the origin of the circuit and provided by
the same protective device. However in some cases the overload
protection can be placed elsewhere in the circuit, or for that matter
omitted altogehter, if it can be imposed by some other design criterion.
In this circumstance the fault protection for the 2.5mm^2 cable will be
adequately provided by the 32A MCB (much the same situation as applies
with a spur in 2.5mm^2 from a 32A radial wired in 4mm^2 for example).
There is however no need for explicit overload protection since in this
case it is imposed by the design i.e. the oven can only draw a maximum
of 10A, and there is no way for someone to unwittingly add additional
load to the end of its cable.
> and that you ought to use
> heat-resistant (rather than "ordinary") cable coming into an oven.
Ideally it should be - and high temperature flex would be the cable of
choice. However there are two common problems with that, its not always
easy to buy in the required size[1], and second it won't always fit in
the connector on the oven. This means that in practice many ovens /
cookers etc get wired in T&E. By selecting a size significantly in
excess of that indicated just by the current demand, you also allow for
significant de-rating due to the high ambient temperature. While it gets
warm in the oven enclosure, its unlikely to actually go above the
insulation temperature limit of the "normal" PVC.
[1] Most wholesalers have stock of 2.5mm^2 which will cover pretty much
any oven, however many do not carry the 4.0mm^2 that would be required
for many hobs.
> I'd like to know why those notions are wrong.
Your notions are not actually wrong as rules of thumb, its just there is
a little more design finesse one can apply to take into account the
specifics of the situation.