On 01/02/2012 09:26, Lee Nowell wrote:
> Thanks John.
>
> The bit I don't quite understand is why there is a sudden drop then it
> stabilises? Is this the boiller modulating? Also, when I run the
No... the boiler will only usually modulate as the system warms up and
the return temperature starts to rise.
When the boiler initially fires, it may do it at full power, or it may
do it at a slightly reduced power and then ramp up to full power.
The governor is in the end a mechanical device which will take a finite
time to react to a sudden change in demand. Hence why you see the dip in
pressure at the hob as the boiler fires.
> test, there was a time delay already between the boilers which was
> seen with the "I'm fired" lights going one after the other as well as
> 2 dips in the hob pressure. I guess the former could just mean that
> both boilers turn their gas on at the same time just 1 took a little
> longer to ignite. Doesn't emplain the latter though I guess.
Are you sure that they are just wired directly to the same demand -
without any delay mechanism between them?
> What I should have done is switched one of the boilers off and
> repeated the test.... Maybe one for tonight
Yup, that certainly ought to be within the capability of the supply.
Do you know what power the hob is?
> Do you have a link to a suitable tmie delayer by any chance? I guess
> I could imagine something which is wired into the wiring centre to
> switch one, wait for a few seconds then switch the other but how would
> it work when something is calling for heat , water has reached temp so
> boilers are off, then the water reduces in temp and both boilers fire
> again?
Well at the moment, it sounds like you have a call for heat signal that
is fed to both boilers. This will be derived in the control wiring in
the normal way from the outputs of the stats, programmers, valve switch
positions etc.
A simple delay timer like:
http://cpc.farnell.com/jsp/level5/module.jsp?moduleId=cpc/261786.xml
could be introduced prior to this signal being fed to one of the
boilers. So when the call for heat goes live, the directly attached
boiler fires then, and the delayed one will not see the live signal
until a preset number of seconds later. When the call is satisfied, both
boilers will turn off.
> Not sure what a regulator looks like but can they stick or something.
Typically a round silver thing about 4" in diameter that sits between
the incoming pipe and your meter.
> It almost seems as though you get a constant static pressure then when
> there is demand (or extra demand) it takes a few seconds for the
> regulator to react and send out the right pressure/ flow. Whilst it is
> reacting, the overall output is the same/ simlar to before but now
> shared with more devices?
Yup - exactly. Some are better with high demands than others, however
all will require a small amount of time to do their job when there are
large step changes in demand.