As others have said, this looks like an S-Plan system with the hot
boiler/pump feed on the left, and then splitting into 2 circuits at the
tee - with one valve for hot water and the other for central heating.
To answer the original question, you should be able to separate the
actuator from the wet part of the valve by removing a couple of screws
which are probably under the cover.
You can then check whether the spindle of the valve moves freely. The
actuator doesn't provide all that much torque so even if you can move
the valve with the manual lever, the actuator may not be able to move it
if it is stiff. If is *is* stiff, you may be able to free it by rotating
it backwards and forwards a few times with a pair of pliers.
While the actuator is off, you can check whether that works by calling
for heat in whichever circuit it controls and seeing whether the bit
which connects to the valve shaft rotates as expected, and then returns
to the closed position when the demand is removed.
--
Cheers,
Roger