On Mon, 20 Jul 2015 12:49:00 +0100, John Rumm wrote:
> On 7/18/2015 1:00 AM, Johnny B Good wrote:
>
>> This now brings me to the expense (or not) of flushing out and
>> refilling
>> the system with a suitable mix of corrosion inhibitor. If I choose to
>> use Fernox MB1 as I've done on previous occasions, it's going to cost
>> well more than the 45 quid I spent on parts (and that's excluding the
>> flushing/
>> cleaning additive cost).
>>
>> I figure my system must have a 50% larger capacity than the typical
>> ballpark figure of 100 litres oft quoted for a 10 rad 3 bedroomed semi-
>> detached property so will need to buy a couple of 4 litre packs of
>> Fernox to properly dose the system with.
>
> Its interesting that Fernox require a greater concentration than other
> inhibitors (4% vs say the 1% recommended for Sentinal X100)
I noticed that too, although their F1 product is supplied in a more
concentrated form. This may simply mean they're offering a fourfold extra
dosing at the same maximum concentration limit as the others, effectively
forcing you into creating a full strength mix which will outlast the
competitors' offerings thus gaining a "Reputation for Quality" that
despite its potential to outlast 4 or 5 dosings worth of the cheaper
stuff, stands a very good chance of being chucked down the drain in the
event of any maintenance tasks requiring partial or full drain downs
frequently enough for them to make an overall gain in profitability.
However, if that's the case, they didn't reckon against my (admittedly
new) policy of collecting any such valuable water/inhibitor mix in a 100
and a 50 litre drum to be recycled in the event of such frequency of
drain downs. :-)
>
>> ISTR seeing 4 litre packs of MB1 at a reduced price circa 27 quid or
>> so
>> somewhere on the internet a day or two back. Looking at the Plumb
>> Centre web site, I see it priced at a whopping £54.37!!! a far cry from
>> the price of the products sold in Toolstation around the 7 or 8 quid
>> mark for a 1 litre quantity required to dose the eponymous 100 litre 10
>> rad system (MB1 uses a 4% dilution hence their 4 litre pack size).
>>
>> The 7 to 1 price differential does rather beg the question as to
>> whether
>> or not the quality of the Fernox products can be 7 times or more
>> greater than that of "The Cheap Stuff"(tm). There surely can't be
>> *that* much disparity between these products, can there?
>
> I can only give you an anecdotal answer... about three years ago I
> converted my vented system to sealed, did a complete mains water flush
> of my whole system (21 rads), then treated with 2L of X100. I fitted a
> Fernox TF1 magnetic/cyclonic filter at the same time. Since then, the
> filter has collected in total around a desert spoon's full of "stuff" -
> mainly magnetite. I added another litre of X100 recently as a top up.
>
> So it does seem to be effective in my system so far.
>
> keep in mind this is what was coming out of the system previously:
>
>
http://wiki.diyfaq.org.uk/index.php?title=File:DirtyFlushWater.jpg
>
> TMMV and all that...
Ok, anecdotal evidence seems to be the only type available, if it's well
considered anecdotal evidence as yours seems to be, it's a damn sight
better than no evidence at all, or worse still, manufacturers' claims.
I did eventually have a google for reviews on the effectiveness of CH
inhibitors, something I could have done beforehand although it wouldn't
have saved me the need to pose the question as it turned out.
As well as an earlier uk.d-i-y discussion on the subject about 8 years
ago, I came across a few web forum discussions which, like the uk,d-i-y
one, failed to come to any obvious conclusion regarding a "Best Product
Choice" although Fernox and Sentinel both seemed to be highly regarded.
>
>> Anyhow, as I'd previously mentioned. on the two recent occasions when
>> I'd part drained the system down to deal with the 3 port valve, the
>> water exited the ground floor drain port looking crystal clear (it
>> might be a different story when it comes to a complete drain down
>> involving buckets in the basement). Enquiring at the Plumb Centre
>> counter suggests this is no bad thing.
I actually got around to taking a sample from the boiler drain port
(lowest part of the system) late last night and it was only the first few
cc which splashed onto the concrete floor that looked as black as your
picture showed.
I was using a pint glass and the first half pint after that showed a
murky yellow liquid with just a thin layer of black particles at the
bottom of the glass. The second sampling was a lot less murkier and paler.
I've transferred this to a resealable glass jar with some wirewooled/
degreased nails and a penny coin chucked in by way of a test of the
inhibitor strength. It's sat on a shelf in the basement alongside a small
glass of tap water with nails and a coin by way of a 'Control'.
Obviously with a test like this, it can take weeks to months before you
can draw any conclusions but it's a damn sight cheaper than shelling out
on a tub of test strips.
>>
>> I've not experienced any of the classic symptoms associated with a
>> sludged up system (no cold spots in any of the rads, no kettling in our
>> ancient Ideal Mexico Super 100 boiler) so I'm left wondering if the
>> prior use of Fernox MB1 has been the reason for our thirty year old
>> system still functioning so well despite the complete lack of any
>> regular annual maintenance work in all of that time.
>
> We used to have a Mexico. I did not get rad cold spots etc, but the
> boiler did kettle, and needed treatment every other year with a noise
> reducer. I don't know how often if ever the system had been treated
> prior to my ownership, but it was obviously not spotless as the above
> pic will attest!
Well, quite! One of the things that seems to save this open vented
system from kettling issues in the boiler is the sheer height of the
header tank relative to the boiler providing higher static water pressure
which will suppress kettling more effectively than it would in a modern 3
bedroom semi-detached system. I was well aware of this when I specified
the use of a floor standing boiler in the basement. :-)
>
>> As far as I can recall, the last time I flushed the system out and
>> re-
>> dosed it with MB1 must be a good 10 years ago when I replaced the pump
>> where I was forced to do a part drain down in order to replace the
>> isolator valves which had started leaking at the spindle glands.
>>
>> Unfortunately, the only definite clue I have is that I dosed the
>> system
>> back in 1998 or so according to the labels I tied to the pipework by
>> the boiler and in the airing cupboard, I find it hard to believe that
>> this *was* actually the last time I treated the system (but it's a
>> possibility).
Actually, when I took another look at the Fernox labels, it goes even
further back than that, November 1994! I had another look for "Evidence"
of my presumed later dosing due to the drain down forced on me by events
when I came to replacing the faulty pump about ten years ago (the weepy
isolator valve spindles turned into little gushers when I tried shutting
them off so had to turn them back on and fiddle them about to slow their
gushing back down to just a slightly faster weeping rate than previously
before shopping around for replacements to let me finish the job).
The *only* evidence I found was one of the original pair of Fernox MB1
boxes (presumed by the tear off label having already been torn off)
alongside the header tank along with a one eighth full container of MB1
sat next to that.
The best I can piece together from this is that I must have had a couple
of litres left over from the 1994 dosing (I only needed to use 6 litres
out of the 8 litre total I'd bought at the time) and only got round to
'freshening up' the system after replacing the pump and the isolator
valves. Even then, it looks as though I still kept a half litre back for
dosing the header tank, a part of the job I never got round to completing
(possibly waiting on my buying another 4 litre pack of MB1 which I also
forgot to sort out).
>>
>> Bearing all that in mind, does anyone have any sage advice to offer
>> in
>> regard of product recommendations?
>
> Only yes use some - preferably a recognised brand. Not sure if the cost
> difference between MB1 and say X100 is really justified - but it may
> well be.
In the end, after seeing how clean the system fill has kept over the
past 20 years since its last proper dosing, I decided to stick with the
expensive MB1 and bought a 4 litre pack from Screwfix this afternoon for
a not quite so eye-watering £29.00 (at least I got change out of thirty
quid! :-).
Our water supply is classed as 'Soft' which I think has contributed to
the remarkably long life of the MB1 inhibitor's effectiveness. We've no
signs of sludging induced problems nor, indeed, sludge itself so rather
than completely flush the system through with an alternative cheaper
brand of cleaner and a fill with same brand inhibitor, I might as well
save myself a lot of grief and just freshen the existing inhibitor back
to a strength that approximates what it was to begin with 20 years ago.
TBH, I'm worried I might give myself a heart attack running around the
system twiddling rad valves and bleed nipples and everything else
associated with draining down/flushing/ refilling with cleaner and then
inhibitor that such a change in the system chemistry dictates.
I'm not as fit as I was ten years ago when I fixed the pump and even
then I only managed to complete a half assed job of refreshing the
inhibitor! The extra 11 quid over my cheapest option is well justified in
the circumstances, especially if it's going to avoid the risk of a heart
attack!
I did see that wiki page in my googlings around the net. Interesting to
note how badly the Protex fared in this test, indistinguishable from the
tap water only control sample.
It's a pity that there seems to have been no further testing work as
suggested at the end of that article. It's been a good eleven years since
John Stumbles did those tests.
All I can add to the discussion is my experience with the seeming
effectiveness over the last 20 years of the 30 year life of my system (it
was given the Fernox treatment from day one by the installers). If it's
normally the practice with the cheaper brands to have to refresh every 2
or 3 years, I'd say the extra cost of Fernox is justified (bearing in
mind that my being on a soft water supply may have played no small part
in this extended life of the inhibitor).
My decision to carry on with the Fernox treatment, it has to be
admitted, is in large part due to it being the 'Path of Least
Resistance'. It's worked just fine thus far so there seems every chance
of enjoying another ten years of trouble free heating and hot water
supply. We'll see how it goes.
>
> However, as you said, the full story is a tad more complicated.
Unfortunately so. Maybe my experience will add some more data points for
others to work with. In the meantime, I'll close with thanks to all who
offered the benefit of their own experience.
I've chosen 'my poison' now so I've only got to apply it, hopefully some
time tomorrow, so that will be an end to this thread for the time being.
If anything worth mentioning does happen to come up from my final
ministrations to the system, I'll report back to this thread by way of
'final closure', otherwise I bid you all adieu.
--
Johnny B Good