paulfoel wrote:
> So if I plug into socket in house (with RCD plug) this is OK? As you can
> see an electrician I am not....
Half the population would run a bit of extension lead down the garden in the
grass or ties to rusty nails along the fence.
At least you are proposing armoured cable and RCD protection, so you're on
the winning team to start with :)
It comes down to physics, and a bit of common sense:
1) The RCD will detect any fault to earth > 30mA and trip in less than 40mS
- these are to do with the probability of the human body staying alive after
such a shock.
2) The RCD will also give you enhanced fault protection for faults to earth
- not wholly relying on the fuse to blow - this can be a problem with very
long cables, but 10m is not that long.
3) You've only got a 13A circuit with a very low expected load at the other
end.
There are some deeply weird technical considerations to do with what they
call "exporting the earth" from the house to an outbuilding, but these are
only a serious concern with metal buildings where the house earth will be
bonded to the metal of the building[1] or similar cases. Assuming you are
talking wooden shed and not metal greenhouse, not really a problem.
Correction on cable size: I am not an encylopedia, so I checked:
http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
1.5mm2 3 core armoured would be more than adequate at 13A (3kW in the web
page form above).
Worst voltage drop is 3.26V which is neglible and the cable is fine for 13A.
I think the only remaining bit you may need help with is terminating the
armoured cable and making sure the armour is bonded to the earth core at
both ends.
You can use 2 core armoured and use the armour as the earth core (in fact
this is typical) but there's not much in the cost and my incination is to go
for 3 core because if one of your terminations is weak, you will not not
lose integretity of the earth.
HTH
Tim
[1] Under some very weird fault cases, the house earth could rise to some
highish voltage above the actual wet ground outside. Inside the house this
is not a problem (mostly) as metal pipes and Class I (earthed) appliance all
rise together due to the bonding - so there is no potential difference to
stick yourselve across. However, if you cause your greenhouse to rise to
100V above the wet ground next to it, you have a problem.