On 01/03/2012 16:08, Adam Funk wrote:
> On 2012-03-01, John Rumm wrote:
>
>> On 01/03/2012 15:09, Adam Funk wrote:
>>> On 2012-02-28, John Rumm wrote:
>>>
>>>> As a rough rule of thumb, single ovens will usually run from a socket,
>>>> and double ones usually need a dedicated supply.
>>>>
>>>> (look at the power rating<= 3kW can go on a socket)
>>>
>>> I'm not sure it's that simple these days. I've just found one with
>>
>> Well it is quite simple really...
>>
>>> the following in different parts of the specifications:
>>>
>>> "Total load rating 2.85 kW"
>>
>> 2.85 is getting close to the limit for a socketed connection, however it
>> is still just inside (assuming that quoted 2.85kW at 240V). In reality
>> because its a quite diverse load, the average current will be well below
>> the 12.4A that the numbers would suggest.
>
> True when the oven element cycles on& off. I'm not sure how much
> power the grill draws,& what happens if you happen to use the kettle
The grill may be similar to a "single oven", so probably less than 2kW
> & toaster at the same time ... but the fuse has never blown in our
> existing set-up.
Kettle and toaster are unlikely to matter on a 30/32A circuit - they are
not on long enough to cause any significant heating in the circuit.
(the MCB will tolerate 45A pretty much indefinitely, and 50A for 15 mins
or so).
> And I found a Zanussi model where the manufacturer's PDF states "This
> appliance is supplied without a main plug and a main cable" and then
> has this table:
>
> Applicable types of cables for UK only
> Connection via Min. size Cable/flex type Fuse
> Cable/flex
>
> • 13 A socket outlet 2,5 mm2 Three core butyl insulated 13 A min.
Which is tricky since you will have a hard job getting 2.5mm cored flex
into a plug. You also don't need 2.5mm^2 to carry 13A!
> • 13 A spur box
>
> Oven Control Circuit 2,5 mm2 PVC/PVC twin and earth 15 A min.
> 20 A min.
>
> but then a retailer's website says for the same model "Requires
> hardwiring by an electrician Needs to be wired directly in to a cooker
> socket". Are they just over-specifying it to err well on the safe
> side?
Partly... specifying cable CSAs is without also knowing what the circuit
protective device is also a bit vague.
In many cases, where you have say a 7kW hob, then you will need a
dedicated circuit, and at that point you may find it easy to stick the
oven on it as well...
An integrated "cooker" rather than separate oven and hob will always be
over what you could power from a socket.
>> There is obviously no harm in running from a dedicated circuit, and when
>> wiring a cooker point (without an integral socket), its often quite
>> handy to make the switch control not only a cooker flex outlet, but also
>> a socket in the oven enclosure.
>
> I may just give up and get the cooker circuit installed to make
> selection easier and to cover the longer term.
If having an electric hob as well, then yes you will need to. If its say
a gas hob, and electric oven, its not essential unless going for a
particularly powerful double oven...