It seems to me that there are two possibilities. Either the boiler is
cycling on its own built-in stat which has too little hysteresis between
on and off temperature, or the Nest thermostat is telling it to turn on
and off.
If this problem started when the Nest and 3-port valve were installed,
you should first make sure that the valve is wired correctly. Can you
trace all the connections and reconcile them with a Y-Plan wiring
diagram. In particular, the programmer (Nest in this case) must have a
HW OFF output which makes the valve's grey wire live when hot water is
not required. Similarly, the cylinder stat must have 3 contacts - with
the HW Satisfied contact again connected to the valve's grey wire.
I don't know about the internal logic of the Nest, but many digital
thermostats cycle their boiler output on and off when approaching the
temperature set-point in order to avoid overshoot. There is usually
something buried in an advanced menu somewhere which enables you to
specify minimum on and off times in order to minimise short-cycling.
With a Y-Plan system, when the HW demand is switched off and/or
satisfied, the boiler and pump are switched on and off by a micro-switch
in the valve - which connects the white and orange wires together. So,
in your case, the CH demand from the Nest will go to the valve's white
wire. That being the case, if the Nest is causing the short-cycling, I
would expect to hear the valve whirring away every time the boiler goes
on and off, because the microswitch only operates when the valve moves
to a different position.
When you talk about measuring voltages on Pin 3, is that in the box
which connects the Nest to the system? If so, that box is switching
mains (or not) to CH ON, and to one or other (but not both) of HW ON and
HW OFF. It is never *generating* 120v. However, if you are measuring
120v, this is almost certainly being fed back by the valve when it is
*not* receiving a CH demand. So, if that voltage is going from 240v to
120v in time with the boiler going on and off, it is pretty certainly
the Nest which is causing the short cycling - in which case you need to
see whether you can fine tune the way in which it operates.
Hope that helps!
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.