On 04/04/2012 10:03, Reentrant wrote:
For anyone with an acl-drayton 679H340-30LO valve, ie the old type
without the removable actuator, it IS possible to completely disassemble
it as follows;
TURN OFF ALL POWER TO THE CENTRAL HEATING IF YOUR NOT SURE HOW TO DO
THIS YOU SHOULD NOT READ ANY FURTHER. CONTINUE AT YOUR OWN RISK.
1. Undo the screw and take off the cover.
2. to remove the motor there are two screws, ones probably hiding behind
the orange wires. remove the screws and pull the motor away from the
body with the earth plate and heatsink/cover then carefully unplug the
connectors from the circuit board. If you need to replace the motor just
plug and screw in your new one.
3. to remove the circuit board, slide off the white cover, and undo the
two small screws that go through the micro switches. You can now remove
the circuit board. (If you havent already you'll also need to remove the
cable clip).
4. if you want to go any further, (I didnt), you can remove the actuator
bits and springs and there are two screws to remove the actuator body
from the valve body. And thats pretty much it.
I replaced the valve motor with one from screw fix and had the exact
same problem. So I took the circuit board out to see if anything had
burned out. And discovered that both micro switches were faulty.
They both had very dirty contacts and one of them had a bent contact
causing it to arc when energised. I cleaned them both up resoldered them
to the circuit board plugged it all back together and its all working again.