The fault lights suggest 'fault with fan/flue'.
I have checked the fan is turning fine, and have checked that the
micro-switch on the flu pressure sensor is operating correctly. I
have also traced the wiring back from the microswitch on the pressure
sensor to the PCB and that seems OK to.
My guess is that it must be the PCB which is faulty.
The symptoms are...
After resetting the boiler and setting the CH Demand on, the boiler
pump and fan run up, and after about 10 seconds the flu/fan fault
light starts flashing. The pump and fan continue to run.
Should I go ahead and replace the PCB or could it be something else?
The key question is does the microswitch operate inside the 10 second
window?
If it does then the PCB is suspect. I expect that maybe cetltd has one.
If it doesn't then the problem might be that there is dirt near the inlet
tube to the pressure switch. It might still operate but not quickly
enough.
--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Solo 2?
>
>If it doesn't then the problem might be that there is dirt near the inlet
>tube to the pressure switch. It might still operate but not quickly
>enough.
>
--
geoff
Yes the switch operates within the 10 second window.
I got a new board from http://www.heatcel.co.uk/ today - it cost £72 +
Vat and this has cured the problem.
However I now have a new issue, which I think may be due to disturbed
wiring. See me new post today 'Baxi system 35/60 Wiring'. The problem
is that under CH demand the boiler operates perfectly. Under DHW
demand the pump runs etc but the flame never lights.
Many thanks to those who helped!
-Kenny