Bizarre central heating problem

141 views
Skip to first unread message

Simon (Dark Angel)

unread,
Mar 12, 2009, 8:27:31 AM3/12/09
to
Right, my central heating system consists of a Potterton Suprima 30 balance
flue boiler and EP2000 programmer, with a Myson MPE322 3-port valve and a
Myson compact CP35 pump.

All was fine until yesterday, however now the boiler refuses to fire up when
it's supposed to come on and the pump just seems to run continuously, even
when the heating/water isn't programmed to be on.

The only way to stop it is to turn the power off to the system at the fused
spur plate, otherwise the pump will just continue pumping cold water round
the system.

Any suggestions? I did have a similar problem about 2 years ago, which I was
told was probably due to the 3 port valve head (which also kept jamming
itself onto either heating or DHW and required you to flip the ports
override switch to get it to move). I changed the head and all seemed well,
but now the system has started playing up again, though the head hasn;t been
jamming like before.

Could it be the 3-port valve head again, or perhaps something to do with the
boiler or programmer?

Thanks in advance, hope I've not left anything off the description (I'm
quite handy with a screwdriver, but plumbing and heating is not exactly my
forte).


--
Best Wishes
Simon Taylor


Tim Downie

unread,
Mar 12, 2009, 8:51:40 AM3/12/09
to
Simon (Dark Angel) wrote:
> Right, my central heating system consists of a Potterton Suprima 30

To paraphrase Bridget Jones, you had me at "Potterton". ;-)

There's been heaps of discussion about Potterton Suprima boilers (here's a
typical thread from a web forum
http://www.howtomendit.com/answers.php?id=63114) . I'm sure you can google
for plenty more on uk.d-i-y. A lot of dodgy PCBs that Potterton have been
replacing free in the past (dunno if this is still the case for your boiler)

User guide here.
http://www.potterton.co.uk/docs/Potterton_Suprima_HE_User_Guide.pdf

HTH

Tim

RobertL

unread,
Mar 12, 2009, 9:59:55 AM3/12/09
to
On Mar 12, 12:27 pm, "Simon \(Dark Angel\)"

<darkangel5STOPTHES...@lineone.net> wrote:
> Right, my central heating system consists of a Potterton Suprima 30 balance
> flue boiler and EP2000 programmer, with a Myson MPE322 3-port valve and a
> Myson compact CP35 pump.
>
> All was fine until yesterday, however now the boiler refuses to fire up when
> it's supposed to come on and the pump just seems to run continuously, even
> when the heating/water isn't programmed to be on.
>
> The only way to stop it is to turn the power off to the system at the fused
> spur plate, otherwise the pump will just continue pumping cold water round
> the system.
>
> Any suggestions? I did have a similar problem about 2 years ago, which I was
> told was probably due to the 3 port valve head (which also kept jamming
> itself onto either heating or DHW and required you to flip the ports
> override switch to get it to move). I changed the head and all seemed well,
> but now the system has started playing up again, though the head hasn;t been
> jamming like before.


I'd guess its' the value. I think the pump is typically controlled by
the a inside the motorised value so it comes on when the value is
actually open, whether or not the valve is supposed to be open. If
it's stuck open the pump will run continuously. But I don't know why
the boielr does not fire as well. perhaps it's cleverer than that.

Robert

RobertL

unread,
Mar 12, 2009, 10:02:58 AM3/12/09
to
On Mar 12, 1:59 pm, RobertL <robertml...@yahoo.com> wrote:
> On Mar 12, 12:27 pm, "Simon \(Dark Angel\)"
>
>
>
>
>
> <darkangel5STOPTHES...@lineone.net> wrote:
> > Right, my central heating system consists of a Potterton Suprima 30 balance
> > flue boiler and EP2000 programmer, with a Myson MPE322 3-port valve and a
> > Myson compact CP35 pump.
>
> > All was fine until yesterday, however now the boiler refuses to fire up when
> > it's supposed to come on and the pump just seems to run continuously, even
> > when the heating/water isn't programmed to be on.
>
> > The only way to stop it is to turn the power off to the system at the fused
> > spur plate, otherwise the pump will just continue pumping cold water round
> > the system.
>
> > Any suggestions? I did have a similar problem about 2 years ago, which I was
> > told was probably due to the 3 port valve head (which also kept jamming
> > itself onto either heating or DHW and required you to flip the ports
> > override switch to get it to move). I changed the head and all seemed well,
> > but now the system has started playing up again, though the head hasn;t been
> > jamming like before.

Sorry: I meant...

I'd guess it's the valve. I think the pump is typically controlled
by
a switch inside the motorised value so it comes on when the valve is


actually open, whether or not the valve is supposed to be open. If
it's stuck open the pump will run continuously. But I don't know why

the boiler does not fire as well.
Robert

John Stumbles

unread,
Mar 12, 2009, 10:52:40 AM3/12/09
to
On Thu, 12 Mar 2009 07:02:58 -0700, RobertL wrote:

> I'd guess it's the valve. I think the pump is typically controlled
> by
> a switch inside the motorised value so it comes on when the valve is
> actually open, whether or not the valve is supposed to be open. If
> it's stuck open the pump will run continuously. But I don't know why
> the boiler does not fire as well.

Because it's a Suprima. Do pay attention in the back! ;-)


--
John Stumbles

How odd of God But not so odd as those who choose
To choose the Jews A Jewish god, yet spurn the Jews

Ed Sirett

unread,
Mar 12, 2009, 2:14:25 PM3/12/09
to

The normal operation would be for the pump to run for a few seconds and
then stop. If there is a heating demand then the pump will run.
Ergo the problem is in the boiler it might be the PCB (balance of odds it
is) or it could be something like fan. More info , what lights are on.

Is the fan running?


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

Roger Mills

unread,
Mar 12, 2009, 3:26:12 PM3/12/09
to
In an earlier contribution to this discussion,
RobertL <rober...@yahoo.com> wrote:

>
> I'd guess it's the valve. I think the pump is typically controlled
> by
> a switch inside the motorised value so it comes on when the valve is
> actually open, whether or not the valve is supposed to be open. If
> it's stuck open the pump will run continuously. But I don't know why
> the boiler does not fire as well.
> Robert

No, this is *not* a problem with the valve. Under some - but not all -
circumstances the valve tells the boiler to fire. The pump is either wired
in parallel with the boiler, or controlled by the boiler - in cases where
pump over-run is required.

The valve *never* tells the pump to run without firing the boiler. The
problem is in the boiler itself - which is being told to fire but isn't
doing so. As others have said, the PCB in this particular boiler is a
frequent cause of failure - so is probably the first place to look.
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!


geoff

unread,
Mar 12, 2009, 3:42:19 PM3/12/09
to
In message <KZCdncHOaOIoYiXU...@bt.com>, "Simon (Dark
Angel)" <darkangel5...@lineone.net> writes

>Right, my central heating system consists of a Potterton Suprima 30 balance
>flue boiler and EP2000 programmer, with a Myson MPE322 3-port valve and a
>Myson compact CP35 pump.
>
>All was fine until yesterday, however now the boiler refuses to fire up when
>it's supposed to come on and the pump just seems to run continuously, even
>when the heating/water isn't programmed to be on.
>
>The only way to stop it is to turn the power off to the system at the fused
>spur plate, otherwise the pump will just continue pumping cold water round
>the system.
>
Hardly bizarre - its one of the standard pcb faults

I presume that the red light is flashing too


As Ed Sirett said, its the only boiler where you change the pcb then
look to see if there are any other faults


--
geoff

Doctor Drivel

unread,
Mar 12, 2009, 5:23:37 PM3/12/09
to

"geoff" <ra...@kateda.org> wrote in message
news:2yQ7RCLb...@demon.co.uk...

Well said Maxie. The best thing he can do is:

1. Drain down,
2. Remove boiler off the wall,
3. Take into the garden
4. Attack boiler with a sledge hammer.
5, Buy new proper boiler like a Broag.

geoff

unread,
Mar 12, 2009, 5:19:08 PM3/12/09
to
In message <71t5uhF...@mid.individual.net>, Roger Mills
<watt....@googlemail.com> writes

>In an earlier contribution to this discussion,
>RobertL <rober...@yahoo.com> wrote:
>
>>
>> I'd guess it's the valve. I think the pump is typically controlled
>> by
>> a switch inside the motorised value so it comes on when the valve is
>> actually open, whether or not the valve is supposed to be open. If
>> it's stuck open the pump will run continuously. But I don't know why
>> the boiler does not fire as well.
>> Robert
>
>No, this is *not* a problem with the valve. Under some - but not all -
>circumstances the valve tells the boiler to fire. The pump is either wired
>in parallel with the boiler, or controlled by the boiler - in cases where
>pump over-run is required.
>
>The valve *never* tells the pump to run without firing the boiler. The
>problem is in the boiler itself - which is being told to fire but isn't
>doing so. As others have said, the PCB in this particular boiler is a
>frequent cause of failure - so is probably the first place to look.

Exactly

boilers are not something where people who don't actually know the
boiler in question should make guesses based on their (different) system

The pump relay on the pcb is controlled by a microcontroller, The only
controlling inputs to the pcb are switched live and temperature sensor

If the pcb goes into lockout (a common problem), the pump relay is
continuously activated as a safety function

it's the 'kin pcb


--
geoff

YAPH

unread,
Mar 12, 2009, 6:36:59 PM3/12/09
to
On Thu, 12 Mar 2009 21:23:37 +0000, Doctor Drivel wrote:

> Well said Maxie. The best thing he can do is:
>
> 1. Drain down,
> 2. Remove boiler off the wall,
> 3. Take into the garden
> 4. Attack boiler with a sledge hammer.
> 5, Buy new proper boiler like a Broag.

I shall have to save this as one of the few posts where I come close to
agreeing with Dr D. ;-)

However my own procedure is:

1. suck teeth
2. say Oh Dear That'll Cost Yer
3. get a properly fixed PCB cheap from Geoff
4. fit it and charge customer an arm and a leg
5. blame Potterton


--
John Stumbles -- http://yaph.co.uk

Who's *really* behind all these conspiracy theories?

Simon (Dark Angel)

unread,
Mar 13, 2009, 8:08:10 AM3/13/09
to

"geoff" <ra...@kateda.org> wrote in message...

> Hardly bizarre - its one of the standard pcb faults I presume that the red
> light is flashing too

Yes it was, but the reset button failed to do any good.

However, I still had the OLD 3 port valve head kicking around, so swapped it
back and now the system seems to be working again (for the time being
anway).

Incidentally, I did get a reconditioned board from someone advertising on
this very newsgroup about 3-4 years ago, so I hope it's not that that's gone
wrong.

geoff

unread,
Mar 13, 2009, 3:06:17 PM3/13/09
to
In message <daqdnTj7y_kw0SfU...@bt.com>, "Simon (Dark
Angel)" <darkangel5...@lineone.net> writes
>

>"geoff" <ra...@kateda.org> wrote in message...
>> Hardly bizarre - its one of the standard pcb faults I presume that the red
>> light is flashing too
>
>Yes it was, but the reset button failed to do any good.
>
>However, I still had the OLD 3 port valve head kicking around, so swapped it
>back and now the system seems to be working again (for the time being
>anway).
>

Strange, the pcb has no direct interface with the 3 port valve

>Incidentally, I did get a reconditioned board from someone advertising on
>this very newsgroup about 3-4 years ago, so I hope it's not that that's gone
>wrong.
>
>

That would have been me


--
geoff

Simon (Dark Angel)

unread,
Mar 13, 2009, 5:37:48 PM3/13/09
to

"geoff" <ra...@kateda.org> wrote in message...
> Strange, the pcb has no direct interface with the 3 port valve

Co-incidence maybe? I'll swap them back again tomorow and see what happens.

> That would have been me

Oh well, might be ordering another one from you in the not too distant
future.


--
Best Wishes
Simon (aka Dark Angel)
Dark Angel's Realm of Horror - http://www.realmofhorror.co.uk


David Taylor

unread,
Jan 3, 2010, 3:34:10 PM1/3/10
to
My daughter has a Potterton EP2002 system with a Potterton Suprima 40L
boiler and a MPE322 diverter valve.
The system seems to be working OK for hot water but has developed a fault
with the CH.
The CH will not come on unless the HW is on and the radiators will only heat
up for as long as it takes for the water tank to reach temperature. When the
tank stat says enough, the system stops heating, no matter that the room
stat is still calling for heat.
I have remove the diverter actuator and checked that it moves according to
demand. The valve is free to turn by hand.
The boiler fires when hot water is required (green light on) but will not
fire for CH only (red light on). We did get it to fire for CH only by
returning both controller sliders to 'off', switching the system off, then
switching it on and sliding the CH control to 'on'. The boiler fired for a
few seconds then shut off again.
Can anyone point me in the right direction to get this fixed?
Thanks.

url:http://myreader.co.uk/msg/1391142635.aspx

Andrew Gabriel

unread,
Jan 3, 2010, 4:23:19 PM1/3/10
to
In article <1066d832b93a4724...@newspe.com>,

My first guess would be the microswitch which should operate at full
travel (CH only) of the mid-position valve is not actually operating.
Maybe because it's faulty, or maybe because the actuator isn't
moving far enough to operate it.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]

Roger Mills

unread,
Jan 3, 2010, 4:47:42 PM1/3/10
to
In an earlier contribution to this discussion,
David Taylor <da...@taylormoran.nospam.com> wrote:

I assume from the fact that it is capable of heating the CH and the HW at
the same time that it is a Y-Plan system - so that the 3-port valve is a
mid-position jobby and not a simple diverter valve, as used by W-Plan
systems. Is that right?

If so, the problem is pretty certainly associated with the valve. My first
thoughts were that the 'wet' part of the valve was seized in the
mid-position - preventing the actuator from moving far enough to be able to
switch the boiler on in CH mode. But you say that the valve is free, so it
can't be that!

The next most likely cause is that one of the microswitches in the actuator
has failed. In HW-only and HW+CH modes, the boiler is driven by the cylinder
stat. But once the HW demand is satisfied, the valve moves to the CH-only
position, and relies on one of its internal microswitches to switch the
boiler on. If the micro-switch fails to make, you get the problem you
describe.

*But*, there's one more possibility. The cylinder stat is a change-over
switch and, when the demand is satisfied, it provides a live 'HW satisfied'
feed to the actuator - without which the actuator can't switch the boiler
on. If the change-over contact on the cyl stat fails, you will also get your
symptoms. The way to check it is to turn the HW off at the programmer -
causing the programmer to provide a 'HW not required' live feed to the
actuator, which does the same as the 'HW satisfied' feed from the cyl stat.

If the CH heating works ok with HW switched off at the programmer, the
problem is in the cyl stat (or its wiring). If it doesn't, the problem is in
the actuator - which needs to be replaced (or repaired - you like fiddly
jobs!).

Mike

unread,
Jan 3, 2010, 5:02:26 PM1/3/10
to

Now I know your boiler is not the same make as mine (Baxi), but the
symptons are the same when I had your problem. I understand it was a
small "circuit board" that sensed (or was supposed to) if the gas was
was flowing. Tap water .. no probs but when CH selected, it ran for 10
secs and shut down.
It was an intermittant fault, but changing the board sorted it.

Mike P

geoff

unread,
Jan 3, 2010, 4:59:55 PM1/3/10
to
In message <1066d832b93a4724...@newspe.com>, David Taylor
<da...@taylormoran.nospam.com> writes

For once someone has a problem with a Suprima which is not pcb related

The boiler doesn't know whether it is heating for DHW or CH, so that's
not where to look

The fact that it actually reacts to the programmer would indicate that
the relays in the programmer are OK

This leaves the diverter valve - I would suspect that you have a problem
with the microswitches, they can melt the case or the contacts can weld
themselves together


--
geoff

Roger Mills

unread,
Jan 3, 2010, 5:23:00 PM1/3/10
to
In an earlier contribution to this discussion,
Mike <Mi...@wherever.co.uk> wrote:

I don't think that's the same thing at all! I assume that you have a combi
boiler - which provides 'instant' hot water *or* central heating, but not
both at the same time? This uses internal sensors to select the desired
function.

The OP has *stored* HW and *external* controls to direct the boiler's output
to the HW circuit or CH circuit or both. The boiler itself neither knows -
nor cares - which it is heating at any given moment. The OP's problem is in
the external controls, *not* in the boiler.