The cables will not be grouped together at any point other than passing
through the joist - they will be side by side when going up the wall.
Does the thermal insulation factor come into this anywhere (e.g. when
buried under the plaster?). Does the grouping factor come into account for
where the two go through the joist together?
Thanks
Roger
>The cables will not be grouped together at any point other than passing
>through the joist - they will be side by side when going up the wall.
>
Well, if cables are briefly grouped, e.g. running through joists then
no, grouping doesn't apply. In a domestic situation though,
calculations are generally not required as 2.5mm is well in for
sockets, as is 1.5mm for lighting etc... are you overthinking a job
there?
--
SJW
A.C.S. Ltd.
Grouping can be ignored if the point at which the cables are running together is less
than 1.5 mtrs. When two cables are popping side by side through a joist the grouping
factor is totally negligible to the final circuit as the effect is so small that you'd
need very accurate test gear to find it.
---
http://www.basecuritysystems.no-ip.com
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.687 / Virus Database: 448 - Release Date: 16/05/04
[...]
>
> The cables will not be grouped together at any point other than passing
> through the joist - they will be side by side when going up the wall.
>
> Does the thermal insulation factor come into this anywhere (e.g. when
> buried under the plaster?). Does the grouping factor come into account for
> where the two go through the joist together?
>
As others have said, grouping doesn't really come into the equation
through a hole in a joist - but don't try to squeeze cables through a
too-small hole, eh? Apart from anything else it'll be a pig of a job
pulling them :-)
As no-one seems to have covered the point, buried in plaster counts as
practically the same as clipped direct, so no derating needed there
either.
One thing you haven't mentioned is Voltage drop, but again in general
you'd have to have a very big house, or an extremely tortuous wiring
route in order to hit problems with that domestically. You haven't
mentioned thermal effects either - none of this route is to be alongside
heating pipes is it?
As for the wider comment someone made about domestic circuits being
generally over specified anyway, this is of course true (you wouldn't
expect anything else on uk.d-i-y, would you? :-). 2.5mm2 cable for
example is rated for a full-size ring (32A MCB, 20A cable) even when
buried in conduit in a thermally insulating wall. This is installation
method 6. Buried in plaster is method 2, and is to be treated as method
1- clipped direct. For completeness:
(From table 4D5A BS7671 or 6F in the OSG)
Cable Current capacity
Size method 1 method 6 Comment (mine)
1mm2 16A 11.5A Generally used on 5A/6A lighting
1.5mm2 20A 14.5A 6A or 10A lighting
2.5mm2 27A 20A 20A radial or 32A ring
These next two are the ones you need to be careful about:
4mm2 37A 26A 20A or 32A radial
6mm2 47A 32A Showers and cookers up to 45A
It is more usual to use:
10mm2 64A 44A for very heavy (10kW, 45A) showers
--
Martin Angove: http://www.tridwr.demon.co.uk/
Two free issues: http://www.livtech.co.uk/ Living With Technology
... DOS Tip #3 : Don't use DOS.
> I am running standard twin & earth PVC cable.
> [...]
> The cables will not be grouped together at any point other than
> passing through the joist - they will be side by side when going up
> the wall.
>
> Does the thermal insulation factor come into this anywhere (e.g. when
> buried under the plaster?).
No, for all the cases you've mentioned the 'clipped direct' (M1) ratings
would apply without any derating for thermal insulation. Cables embedded in
plaster count as 'clipped direct' unless the plaster is a special thermal
insulating type (containing polystyrene beads).
If the cables in the wall are touching (side-by-side), the grouping factors
(Cg) are 0.85, 0.79, 0.75, 0.73 for 2, 3, 4, 5 cables (falling to 0.70 for 9
cables). However if you space them out so as to have one cable width's
clearance between them the Cg becomes 0.94 for 2 cables and 0.90 for 3 or
more. With 2 widths clearance no grouping has to be applied.
> Does the grouping factor come into account for
> where the two go through the joist together?
I'll take issue slightly with what the others have said here since, if you
are passing through several joists on a run, the cables will tend to remain
bunched between the joists. The 'bunched' Cg for two cables is then 0.80.
For a 30/32 A ring circuit you need to achieve 20 A installed rating (or 27
A with a rewireable fuse). So the Cg can be as low as 0.74 except for the
rewireable fuse case, where no grouping at all is allowable!
It sounds as if you ought to get yourself a copy of the On-Site Guide (new
brown one).
HTH
--
Andy
Thanks for the comments on this.
I am currently rewiring my house in stages.
Last year I added an isolating switch and replaced the existing fused CU
with two larger split ones, so the circuits are now protected with mcbs
(and an RCD where necessary). I also replaced the existing storage
radiator CU and relay arrangement for a new CU with MCBs and a modular
contactor. The relay that had originally been fitted was an open relay
bolted to a piece of asbestos sheet and contained in a perspex sandwich
box with the lid held on by insulating tape! There were two relays like
this, one for the immersion heater. However I wired the immersion cable
direct to the mcb and the immersion is now controlled via an immersion
timer in the airing cupboard.
The existing wiring was done by a previous owner about 28 years ago and
although not really in need for renewal, I am not happy with it. Rewired
by a previous owner (an electrician), the methods leave a lot to be
desired by today's standards.
One thing that really bugs me is that most of the lighting cables - about
16 - end up in a large adaptable box under the floorboards joined together
in a spaghetti junction of chocolate blocks. Whilst there is nothing wrong
with this, it is almost impossible to identify the cables. More worrying,
although there are two two way circuits (one for the landing light and one
for the hall light (which also has an intermediate switch)), only two core
cable is used. L1 and L2 are on one cable and the common for the landing
light (red) is on the same cable (black) as the hall light. To me this is
downright dangerous as it means that the cable is effectively fed from two
mcbs.
The only place 3core and earth was used was from the landing light switch
to the landing light - the yellow connected to the switch, the blue
connected via a chocolate block in the light switch box to a cable coming
from the adaptable box neutral and the red connected via a chocolate block
in the switch to another cable from the adaptable box that was live. I.e.
the 3 core cable wasn't being used for it's correct purpose but, again,
being used to share circuits. At the junction box for the ceiling rose,
the yellow and blue were used as the supply for the light and the red was
connected to the red of a T&E whose black was connected to the blue and
this went to another box that had the upstairs lighting circuit supply.
Now you see why I want to rewire :-)
There is an infra red heater in the bathroom which is currently wired into
the upstairs light circuit, which I believe is / was common practice.
However I am going to extend the up ring main into the loft (still as part
of the ring and not a spur) to give a socket there for future use, and at
the same time will wire the bathroom heater to this.
One of the jobs I have to do is to replace the cable feeding a brick built
shed in the garden. The cable is, I suspect, 1.5mm T&E PVC and is taken
from a fused spur on the down ring main. It terminated in a fused CU in
the shed. I've replaced the CU with one that has mcbs and is RCD
protected, I just need to replace the T&E with a much higher rated SWA
cable and take it to the CU.
I have always done my own wiring and I have John Whitfield's guide to the
IEE wiring regulations which I find useful. However I was rather stuck on
the correction factors as I didn't know how they related to what I was
doing. If unsure, I would have erred on the side of caution, however that
may have meant using larger cable than necessary. The only place ambient
temperature might be a problem is for the cables in the loft. The cables
would be clipped to the surface, but it does get quite hot up there and I
assume that I should allow for a 50 degree summer temperature and the
necessary correcting factor. This might limit me extending the ring main
as a ring to the loft.
Am I right in assuming that if a spur was taken to a single socket in the
loft (the actual ring main would be at bedroom floor level), it would be
quite alright to use 2.5mm as, even with the corrective factor for 50
degrees, the cable would not be carrying more than could be drawn from the
socket?
Voltage drop shouldn't be a problem as there are no overlong runs of
cable.
The shower cable size I'll bear in mind as I currently have a 8 or 9Kw
shower in 6mm, but I want to rewire for the possibility of a 10Kw one - so
I'll rewire using 10mm.
Sorry, just realise how long this post has got :-)
Roger
[snip all to familiar tale of woe!]
>Am I right in assuming that if a spur was taken to a single socket in the
>loft (the actual ring main would be at bedroom floor level), it would be
>quite alright to use 2.5mm as, even with the corrective factor for 50
>degrees, the cable would not be carrying more than could be drawn from the
>socket?
>
Yep, 2.5mm all the way is fine.
>The shower cable size I'll bear in mind as I currently have a 8 or 9Kw
>shower in 6mm, but I want to rewire for the possibility of a 10Kw one - so
>I'll rewire using 10mm.
>
Good idea, although even 9KW on 6mm is tight, but if it's coming out
soon it'll probably last a bit longer!
--
SJW
A.C.S. Ltd.