On 27/06/2017 20:49, Graham. wrote:
>
> My kitchen currently has a dedicated cooker circuit, 6mm cable from a
> 32A MCB.
So far, so normal ;-)
> New kitchen planned, I now want a new induction hob and a double oven
> fitted, the max ratings are 7.2 & 4.2 kW respectively, lets call it a
> total of 12kW or 52.17A
>
> AIUI you apply diversity by subtracting 10A then reducing the
> remaining figure by 30% that's 22.65A, about a third of the carrying
> capacity of 6mm.
Indeed. Allow an additional 5A if there is a socket fitted to the cooker
point...
> The thing is that the electrician is telling me that my 6 mil cable is
> not big enough for both appliances, and he wants to run a new cct for
> one of them.
For domestic applications, its likely to be fine. Its certainly big
enough in the sense that it won't suffer damage while protected by a 32A
MCB.
The only question that remains is could you get nuisance tripping of the
MCB under full load if you turn on all the hot plates and the ovens at
full chat. The reality is the MCB is unlikely to trip at full load for
going on for a quarter of an hour, and that seems like ample time for
the heating elements to start cycling on their stats.
> Total length of run is about 14m, run in the void under the floor
> except the last 4m in a duct through a chase in a concrete floor. I'm
> not sure what derating to apply, but surely I've got ample headroom.
You could probably count that as installation reference method B, which
gives you a 38A max continuous load capacity.
> The electrician saw the oven I am to use, but to be fair, he had no
> idea which hob I had chosen, but I can't imagine any ordinary 4 ring
> induction that would break this power budget.
>
> So, sanity check time. Have I got anything wrong? Any advice? (Apart
> from the obvious).
I can't fault your logic. So it really comes down to discussion with the
electrician...
Personally I have seen plenty of double oven + 6 - 7kw ish hobs
installed on the single circuit, and don't recall tripping being an issue.