Noisy combi boiler? (Ideal Logic 24)

4,115 views
Skip to first unread message

Phil K

unread,
Nov 15, 2012, 8:20:50 AM11/15/12
to

I just had an Ideal Logic 24 combi boiler installed in the ground floor
coat cupboard of my 3-bed semi. It's all working properly, but it sounds
quite noisy from within upstairs rooms. Surprisingly, if you stand right
outside the boiler cupboard, it sounds very quiet - even if the cupboard
door is open. From upstairs, it sounds like a Boeing 747 just prior to
takeoff. I guess it must be sending its sound waves directly upwards rather
than outwards. Or could the sound be the actual copper pipework resonating?

I've been thinking about installing some kind of soundproof ceiling in the
cupboard. Or is there some other remedy I should try first?

TIA

PK

Phil K

unread,
Nov 16, 2012, 2:43:10 AM11/16/12
to
Phil K <p...@xxdd44.com> wrote in
news:XnsA10C8731...@130.133.4.11:
PS... Correction!: The boiler DOES sound noisy at its location in the coat
cupboard. (I just checked again, during a period when the rest of the house
is quiet). In fact, its location in the cupboard, is the place where the
noise is loudest, as you'd expect. I've noticed that the noise doesn't stop
as soon as the "burner on" LED goes out. And if I switch the boiler's front
knob to off (i.e., from 'central heating' to completely 'off', the noise
continues for approximately 4 minutes afterwards. The noise starts again
instantly, as soon as I switch the boiler back on to "C" mode or "C+D"
(ie., c/h + dhw). The noise sounds to me like the sound of a main burner -
hence my earlier reference to a jet engine.

TIA

PK

Phil K

unread,
Nov 16, 2012, 4:11:07 AM11/16/12
to
Phil K <p...@xxdd44.com> wrote in
news:XnsA10D4DF1...@130.133.4.11:


> PS... Correction!: The boiler DOES sound noisy at its location in the
> coat cupboard. (I just checked again, during a period when the rest of
> the house is quiet). In fact, its location in the cupboard, is the
> place where the noise is loudest, as you'd expect. I've noticed that
> the noise doesn't stop as soon as the "burner on" LED goes out. And if
> I switch the boiler's front knob to off (i.e., from 'central heating'
> to completely 'off', the noise continues for approximately 4 minutes
> afterwards. The noise starts again instantly, as soon as I switch the
> boiler back on to "C" mode or "C+D" (ie., c/h + dhw). The noise sounds
> to me like the sound of a main burner - hence my earlier reference to
> a jet engine.


PPS... Since the noise seems to be constant, while the c/h is turned on,
and continues 4 minutes after it is turned off, and dos not disappear when
the burner LED goes out, does this suggest that it is the flue fan that is
making all the noise? Is this normal?

RJH

unread,
Nov 16, 2012, 3:30:34 PM11/16/12
to
I've got the Logic 30, newly installed. I don't think it's overly noisy
as these things go, but I will box it in when the time comes.

The 4 minute thing is either 'fan purge' or 'pump overrun' - does it not
say that on the display? This suggests to me that the noise is more pump
than burner.

My main complaint is a high pitched tone that can be heard in the
bathroom, directly above the boiler, and throughout the house in the
dead of night. Previous house with identical boiler did the same.

Rob

Phil K

unread,
Nov 17, 2012, 6:15:56 AM11/17/12
to
RJH <rep...@gmail.com> wrote in news:50a6a26c$0$15072$c3e8da3
$33a0...@news.astraweb.com:

> I've got the Logic 30, newly installed. I don't think it's overly noisy
> as these things go, but I will box it in when the time comes.
>
> The 4 minute thing is either 'fan purge' or 'pump overrun' - does it not
> say that on the display? This suggests to me that the noise is more pump
> than burner.


Hi,
Thanks for the input.
>
> My main complaint is a high pitched tone that can be heard in the
> bathroom, directly above the boiler, and throughout the house in the
> dead of night. Previous house with identical boiler did the same.

I hear similar occasionally, just as something inside the boiler is
shutting off (valve or burner flame; I'm not sure which). That's what it
sounds like to me, anyway.

PK

Doctor Drivel

unread,
Nov 20, 2012, 10:04:55 AM11/20/12
to
Have a length of plastic pipe on the flow & return at the boiler to reduce
noises running through the copper pipes.

Ideal are not the best of boilers.

Phil K

unread,
Nov 20, 2012, 12:38:17 PM11/20/12
to
"Doctor Drivel" <inv...@not-for-mail.invalid> wrote in
news:k8g64f$nhe$1...@dont-email.me:

>
> Have a length of plastic pipe on the flow & return at the boiler to
> reduce noises running through the copper pipes.

I wondered about that. Has anyone else here found that to make a
significant improvement? It would be good if someone made a special
vibration-dampening pipe for this purpose.

PK

JakeD

unread,
Nov 21, 2012, 6:09:27 AM11/21/12
to
Phil K <p...@xxdd44.com> wrote in news:XnsA111B2D4...@130.133.4.11:

> I wondered about that. Has anyone else here found that to make a
> significant improvement? It would be good if someone made a special
> vibration-dampening pipe for this purpose.


I'm looking at the copper pipes coming from my boiler, and am thinking
about embedding them in concrete to subdue the sound waves in the pipes.


JakeD

Jonathan

unread,
Nov 21, 2012, 6:18:52 AM11/21/12
to
On Nov 21, 11:09 am, JakeD <j...@milkobilko.net> wrote:
> Phil K <p...@xxdd44.com> wrote innews:XnsA111B2D4...@130.133.4.11:
Won't that risk corroding the copper pipes?

Jonathan

Fredxx

unread,
Nov 21, 2012, 6:59:57 AM11/21/12
to
On 16/11/2012 09:11, Phil K wrote:
To me that sounds like a pump and water noise. If there is circulating
air signified by a sound of small tacks in the heating system then it
would be prudent to remove this air if at all possible. The pump is
generally powered through the boiler and will run for an extra few
minutes to remove heat from the heat exchangers after the flame is out.

The pump is in the boiler and I'm not sure if you can alter the pump
speed. If you can it might be worth reducing it by one notch.

polygonum

unread,
Nov 21, 2012, 9:38:37 AM11/21/12
to
No - not until round tuits convert looking into action.:-)

--
Rod

JakeD

unread,
Nov 21, 2012, 12:42:12 PM11/21/12
to
polygonum <rmoud...@vrod.co.uk> wrote in news:ah47bjFsvc4U1
@mid.individual.net:

>> Won't that risk corroding the copper pipes?

Any more so than, say having a copper pipe outside, exposed to the
elements? If so, I suppose the pipes could be painted first, to protect
them from whatever corrosives might be present in concrete...

JakeD

polygonum

unread,
Nov 21, 2012, 12:45:43 PM11/21/12
to
Actually, from what I have read, I think it entirely possible that
concrete/cement could be far more aggressive than "weather".

--
Rod

Doctor Drivel

unread,
Nov 22, 2012, 5:19:10 AM11/22/12
to

"Phil K" <p...@xxdd44.com> wrote in message
news:XnsA111B2D4...@130.133.4.11...
The vibration-dampening pipe is called plastic pipe.

buil...@hotmail.com

unread,
Sep 8, 2013, 1:49:52 AM9/8/13
to
the noise is fan purge i fit these all the time in social housing crap boilers but hey if you have a heat 12 for the price of a memory chip you can turn it into a 24kw

carst...@gmail.com

unread,
Jan 30, 2014, 4:48:21 AM1/30/14
to
Hi
I had one of these boilers fitted last September only realised when the winter months arrived how noisy it is. I described it exactly as you did quiet enough at the boiler but sounds like a plane taking off throughout the house. The noise goes on for hours and is driving me mad, I had someone come out but he just said they fit the boiler not my system and it is the power of the boiler causing this throughout the system. I said I'll have to learn to live with it but I can't. It was put in through the government scheme so I feel I should not complain, but I am 68 and wish I still had my old boiler.

gregwh...@googlemail.com

unread,
Feb 6, 2014, 6:17:12 AM2/6/14
to
On Thursday, November 15, 2012 1:20:51 PM UTC, Phil K wrote:
> I just had an Ideal Logic 24 combi boiler installed in the ground floor coat cupboard of my 3-bed semi. It's all working properly, but it sounds quite noisy from within upstairs rooms. Surprisingly, if you stand right outside the boiler cupboard, it sounds very quiet - even if the cupboard door is open. From upstairs, it sounds like a Boeing 747 just prior to takeoff. I guess it must be sending its sound waves directly upwards rather than outwards. Or could the sound be the actual copper pipework resonating? I've been thinking about installing some kind of soundproof ceiling in the cupboard. Or is there some other remedy I should try first? TIA PK

HI,
I've recently had an ideal boiler fitted and it's making a constant high pitch noise like you describe. Did you manage to do anything to stop the noise?
Thanks

darren...@gmail.com

unread,
Feb 26, 2014, 3:55:43 AM2/26/14
to
I fit around 40 of these boilers a year and am an accredited installer. Chasing pipe work into the wall or taking pipes outside is madness.. These boilers are one of the quietest on the market. Obviously boilers make noise but not like a 747.
You either have air or crap in the system or a faulty boiler. I had a customer with a noisy Boiler and Ideal came straight out & replaced the gas valve..(these boilers come with a 7-5 year warranty..
If fitted properly they won't be noisy, that's one of the reasons we Powerflush a system. If there's a whooshing noise when the boiler fires then it's a faulty gas valve or the gas pipe work is undersized..
If there's a high pitched noise whilst boiler is working then it's either air in the pump or the fan squeeling.. The pump can be bleed of air, if it's the fan then it's an Ideal problem.
Don't put up with a noisy boiler!!!
The old chestnut ' I can't guarantee the system I only fitted the boiler' is a crock of crap..
If an installer has fitted the boiler & it's making a noise get them back to sort it..
We make enough money to be able to warrant a happy customer!!
Ideal Logic boilers are fantastic for the money..

Martin Brown

unread,
Feb 26, 2014, 4:35:06 AM2/26/14
to
You don't want concrete apart from causing corrosion that will just
couple the noise into the brick structure of the house!

You can cast a reasonable bell out of concrete if you try hard enough
(or make springs out of it).

Something like a HDPE foam sleeve tie wrapped onto the pipes or
sorbothane might damp out some of the noise. My CH pump is supported
this way. You might need to experiment to find the right separation of
supports to damp out the worst resonance(s) in the pipework.

A noisy new install boiler is most likely air in the system somewhere
allowing it to kettle. When everything is off bleeding the system at the
highest point ought to fix it after a couple of goes.

Sound transmission is astonishingly difficult to prevent. The dense rock
wool sold for cavity wall insulation works fairly well as an acoustic
damper that is not flammable and has reasonable acoustic mass.

--
Regards,
Martin Brown

RJH

unread,
Feb 26, 2014, 4:42:27 AM2/26/14
to
I have the same boiler, and work elsewhere meant I had the opportunity
to place some plastic pipe in the run. This all but solved the ringing.
But after a few weeks it came back. My own theory is sludge in the
radiators and air. Not urgent.

--
Cheers, Rob

lizpe...@gmail.com

unread,
Feb 28, 2014, 3:29:00 PM2/28/14
to
I had one of these boilers fitted today, I am also 68 and got it through a government scheme. It is very noisy, it has the sort of sound my old boiler made when I was running water. It is in a GF utility room with door and there is a long kitchen between it and where I am sitting with my laptop. I then went up stairs and I could hear it slightly still in the bathroom but thankfully not in my bedroom. I turned my boiler off an hour ago and the noise continued for at least 15 minutes then suddenly silence. I think that if I had the TV on or some music I wouldn't notice is but I like sitting in peace and quiet. They are coming to install the installation next week so I will have a word them. I feel like you, my old boiler was not efficient but it was quiet unless water was being tun.

hinch...@gmail.com

unread,
Apr 26, 2014, 2:56:15 AM4/26/14
to
I know its a long time ago. But have any of thd problem's been sorted. We had a logic 24 fitted as our vokera blew up so needed something gitted quickl, without research. It is driving me mad, I cant have the boiler running when im in ghe house because of the same noise described. I has been put in the same place as our old one which I never heard.

ray.al...@mail.com

unread,
Feb 12, 2015, 6:42:02 AM2/12/15
to
That's really ironic, I've got an Ideal at home and it's used to make a noise for ages!!!. I was wondering if my system was 'power flushed' before the boiler was fitted, just in case there's some gunk got in it from the pipes - though I suspect that's unlikely.

Sounds like a local heating engineer might be worth a call, those guys are great at fixing niggles like that - I should know as I got STL Heating out to take a look, turns out it was something they were able to fix (I think it was a part) - but yeah had no probs since. So might be worth getting in touch with them.

Geo

unread,
Feb 12, 2015, 12:02:47 PM2/12/15
to
5 posts today in this group from this spammer for STL -
"amazed at how much I'd ended-up saving "
"blog that someone made"
"rang some local North West based firms"

- I smell a rat.

John Rumm

unread,
Feb 12, 2015, 7:27:12 PM2/12/15
to
On 12/02/2015 11:42, ray.al...@mail.com wrote:

> Sounds like a local heating engineer might be worth a call, those

Bit late I would have thought - the question was over two years ago...

> guys are great at fixing niggles like that - I should know as I got
> STL Heating out to take a look, turns out it was something they were

Na I would steer clear of that lot - I have heard one of the owners is a
prolific newsgroup spammer.


--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Esther Wood

unread,
Sep 14, 2019, 11:14:03 PM9/14/19
to
replying to Fredxx, Esther Wood wrote:
Hi I just moved in had new boiler last year .the boiler constantly make noise
been serviced

--
for full context, visit https://www.homeownershub.com/uk-diy/noisy-combi-boiler-ideal-logic-24-850848-.htm


Brian Gaff

unread,
Sep 15, 2019, 5:12:29 AM9/15/19
to
How old is this post, anyway, most likely cause is the system is now old
full of gunge and probably causing issues.
Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...
bri...@blueyonder.co.uk
Blind user, so no pictures please
Note this Signature is meaningless.!
"Esther Wood" <caedfaa9ed1216d60ef...@example.com> wrote in
message news:15c47e1f04c948ab$6$13566$4206...@news.newsgroupdirect.com...

Fredxx

unread,
Sep 15, 2019, 5:19:21 AM9/15/19
to
On 15/09/2019 04:14, Esther Wood wrote:
> replying to Fredxx, Esther Wood wrote:
> Hi I just moved in had new boiler last year .the boiler constantly make
> noise
> been serviced


Wow, you reply to a post 7 years old.

Can I recommend you become versed with usenet. This might assist:
http://wiki.diyfaq.org.uk/index.php/Home_owners_hub
and
http://wiki.diyfaq.org.uk/index.php/Newsgroup_access_tips

Andrew

unread,
Sep 15, 2019, 5:33:00 AM9/15/19
to
2012, so it's probably already been recycled into some more
Lidl, middle isle tat by now.

Andrew

Bigman

unread,
Jan 29, 2020, 8:14:05 AM1/29/20
to
replying to Doctor Drivel, Bigman wrote:
Ideal are well made good old UK made in Hull

Craig Leman

unread,
Jan 14, 2023, 5:19:24 AM1/14/23
to
The only remedy would be to move the boiler.

Animal

unread,
Jan 14, 2023, 2:02:47 PM1/14/23
to
On Saturday, 14 January 2023 at 10:19:24 UTC, Craig Leman wrote:
> The only remedy would be to move the boiler.

or soundproof the cupboard. Or fix what's wrong in the boiler. But as the q was asked in 2012, who cares?