On 13/02/2013 14:27, Bob Minchin wrote:
> F Murtz wrote:
>> Nightjar wrote:
>>> On 13/02/2013 09:39, RobertL wrote:
>>>> I've noticed recently that my 15mm compression joints seem to leak
>>>> more often than they used to. There seems to be a smaller region
>>>> between "too loose" and "overtight" when doing them up.
>>>>
>>>> Has the wall thickness of standard 15mm copper tube been reduced
>>>> recently as an economy measure perhaps?
>>>
>>> Which 'standard' copper tube are you buying? BS EN 1057 copper tube
>>> comes in three different recommended thickness of wall (0.7mm, 0.8mm and
>>> 1.0mm) and three more that are recognised but not recommended.
>>>
>>> Colin Bignell
>>>
>>>
>> The wall thickness does vary according to the aplication but the outside
>> diameter remains the same.
> Some grades are not suitable for bending either. I suspect more to do
> with the hardness than the absolute thickness.
Most plumbing applications use half hard tube, but microbore normally
uses fully annealed and for some applications fully hard tube is
available. The harder the tube, the more difficult it is to bend for a
given size.
>
> I seem to recall different 'tables' in the spec. Table X and table Y
> seem to ring a bell but I can't recall which was the bendable and which
> was not.
That is from the older BS 2871:1972. Table X was thin wall tube - 0.7mm
for 15mm tube. Table Y was thick wall tube - 1.0mm for 15mm tube.
Colin Bignell