I intend to have one vertical run of 2.5M, with 3 x 2 gang boxes and
sockets contained within this run. I then want to elbow the top and
place another 2 gang box and socket at the end of a 1.5M horizontal
run, which will then form an inverted L shape. To maintain the ring
structure I'll need to return the cable to the extension starting
point.
Is it common practice to return the cable down the same conduit that
it came up in, or is it better to form a conduit loop?
The latter option is going to require twice as much conduit, so I'd
rather use the former method if practical.
--
Kind regards,
Geoff Mills
>Is it common practice to return the cable down the same conduit that
>it came up in,
Yes.
Assuming metal conduit, if there is not a copper protective
conductor drawn into the conduit then you need to be particularly
careful about making proper joints to maintain the continuity of the
trunking which forms the protective conductor.
--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
> On Wed, 16 Sep 2009 16:09:50 +0100 someone who may be Geoff Mills
> <GMi...@privacy.net> wrote this:-
>
>> Is it common practice to return the cable down the same conduit that
>> it came up in,
>
> Yes.
>
> Assuming metal conduit, if there is not a copper protective
> conductor drawn into the conduit then you need to be particularly
> careful about making proper joints to maintain the continuity of the
> trunking which forms the protective conductor.
He explicitly said he'd be using plastic conduit!
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!
> Is it common practice to return the cable down the same conduit that
> it came up in, ...
It is acceptable, but if you are using twin and earth cable, rather than
individual conduit wires, you may find it a bit of a tight fit around elbows
in 20mm conduit. I prefer 25mm conduit if I am running two 2.5mm T&E cables.
Colin Bignell
>He explicitly said he'd be using plastic conduit!
Apologies. I didn't spot the orphaned word.
>On Wed, 16 Sep 2009 16:09:50 +0100 someone who may be Geoff Mills
><GMi...@privacy.net> wrote this:-
>
>>Is it common practice to return the cable down the same conduit that
>>it came up in,
>
>Yes.
>
>Assuming metal conduit, if there is not a copper protective
>conductor drawn into the conduit then you need to be particularly
>careful about making proper joints to maintain the continuity of the
>trunking which forms the protective conductor.
Thanks,
I hadn't considered metal conduit before, nor that the conduit itself
could be used for earthing. Lots to learn.
Thanks, I started out with the idea that I'd be using T&E cable though
perhaps individual wires are more suitable. But then again, if that is
so, why would anyone be running 2 T&E cables through conduit?
Individual wires is the better choice. However, it probably depends upon
whether you are doing enough to justify buying three reels of conduit wire.
Colin Bignell
Much stronger if in the sort of place where it could get bashed.
The minimum you'd need is a die to thread the cut ends. Assuming you can
do it all in straight runs.
--
*Nothing is foolproof to a sufficiently talented fool*
Dave Plowman da...@davenoise.co.uk London SW
To e-mail, change noise into sound.
Saves buying the singles? They have thicker insulation than stripped TW&E.
And IIRC only come in 100 mtr drums - dunno anyone that sells cut lengths.
--
*No hand signals. Driver on Viagra*
Metal conduit is excellent if you need more mechanical protection than heavy
duty plastic offers, but it is not easy to work with. You need a pipe
threader and, if you want to make pretty shapes, which you can do with care
and a hot air gun in PVC, a pipe bender. As noted, the earthing it offers
can be unreliable, so I always run earth wires in it as well.
Colin Bignell
Are individual wires not usually sold by the metre? I like the idea of
these because only one earth wire would be needed. Trouble is the girl
who answered the phone at the local Peco said she'd never heard of
using individual wire. She always sells T&E for the purpose and this
with 20mm conduit, as 25mm is special order and only sold in bulk.
Fortunately there is a local Screwfix now.
>As noted, the earthing it offers
>can be unreliable, so I always run earth wires in it as well.
If it is installed and maintained improperly. However, that is true
of other ways of doing the same thing.
> Are individual wires not usually sold by the metre? I like the idea of
> these because only one earth wire would be needed. Trouble is the girl
> who answered the phone at the local Peco said she'd never heard of
> using individual wire. She always sells T&E for the purpose and this
> with 20mm conduit, as 25mm is special order and only sold in bulk.
> Fortunately there is a local Screwfix now.
TLC cut most cables - but not this one. Probably no demand. You could
check Ebay, though.
Just for info you used to be able to get it in stranded too - which made
pulling through conduit that much easier. Dunno if you still can.
--
*It's this dirty because I washed it with your wife's knickers*
I always buy frrom my local electrical wholesaler, who would probably give
me a very odd look if I asked to buy anything other than armoureed cable in
cut lengths. I usually buy conduit wire in 100m reels. I think 50m is also
available, but I used more than one of the 100m reeels last time I did a
factory rewire, so it wasn't worth buying less.
> I like the idea of
> these because only one earth wire would be needed. Trouble is the girl
> who answered the phone at the local Peco said she'd never heard of
> using individual wire. She always sells T&E for the purpose and this
> with 20mm conduit, as 25mm is special order and only sold in bulk.
Again, my local electrical wholesaler (Newey & Eyre) will supply 25mm in
single lengths. It is to order only, but delivery is next day, to my
address.
Colin Bignell
For the marginal cost of an extra wire run, it is safer to assume that it
will, at some point, not be properly maintained.
Colin Bignell
Yes. Conduit into BESA boxes will usually maintain good conductivity for
ages. The problem is with ordinary surface mount steel boxes etc where you
rely on a backing ring or nut.
--
*The longest recorded flightof a chicken is thirteen seconds *
Plastic conduit is fine with 6491X, FTE is an exercise in frustration
if you are a suitable masochist (6242YH is bad, 6242BH with its
tougher sheath would be friggin hilarious around a few bends).
You can buy cut lengths of 6491X online. TradingDepot, perhaps
AlertElectrical, Gil-Lec, TLC for gr/ye, a few others.
The problem with stocking cut lengths of 6491X is volume & having
sufficient reels set up to meet demands without wastage. Would be
better if they sold say 10m of large & 25m of small multiples which
would not be a bad idea (enough for a shed or garage basically which
is where 6491X does get used domestically).
If there is no real requirement to use conduit, I would use oval.
Where conduit & flexible conduit can come into its own - even with
6491X is for kitchens, particularly with stud walling. Very easy to
create an unpopulated network of conduit ready for any future changes
so making kitchen refurbs a lot simpler (remember tile trim for on
worktop so apes don't destroy the tiling). You could extend it to
network drops and throughout the house - even if not used the oval/
conduit saves plaster :-) Makes it a lot easier than "damn, I wished
I'd..." having decorated vs simply having to measure & cut out a box
over pre-existing oval/conduit.
<...>
>You can buy cut lengths of 6491X online. TradingDepot, perhaps
>AlertElectrical, Gil-Lec, TLC for gr/ye, a few others.
Thanks for the leads. I'll follow them up.
<...>
>If there is no real requirement to use conduit, I would use oval.
Does oval marry up with the surface mounted back boxes in a similar
way to conduit?
>Where conduit & flexible conduit can come into its own - even with
>6491X is for kitchens, particularly with stud walling. Very easy to
>create an unpopulated network of conduit ready for any future changes
>so making kitchen refurbs a lot simpler (remember tile trim for on
>worktop so apes don't destroy the tiling). You could extend it to
>network drops and throughout the house - even if not used the oval/
>conduit saves plaster :-) Makes it a lot easier than "damn, I wished
>I'd..." having decorated vs simply having to measure & cut out a box
>over pre-existing oval/conduit.
That is a state of excellence which I'm unlikely to achieve in this
lifetime. Fascinating to read though.
>In article <ctg3b5pl36hii24fb...@4ax.com>,
> Geoff Mills <GMi...@privacy.net> wrote:
>> I hadn't considered metal conduit before, nor that the conduit itself
>> could be used for earthing. Lots to learn.
>
>Much stronger if in the sort of place where it could get bashed.
>The minimum you'd need is a die to thread the cut ends. Assuming you can
>do it all in straight runs.
Good points. I'm usually a belt and braces man but the relative ease
of working with plastic conduit is going to swing it on this occasion.
<...>
>TLC cut most cables - but not this one. Probably no demand. You could
>check Ebay, though.
Only found 100M drums of it so far on ebay. Thanks to this thread I
have a few more keywords for searches now, so I'll have another go.
>Just for info you used to be able to get it in stranded too - which made
>pulling through conduit that much easier. Dunno if you still can.
Stranded seems like a useful feature, though if it's possible to pull
2 T&E cables through the conduit, individual wires must be somewhat
easier by comparison.
<...>
>I always buy frrom my local electrical wholesaler, who would probably give
>me a very odd look if I asked to buy anything other than armoureed cable in
>cut lengths. I usually buy conduit wire in 100m reels. I think 50m is also
>available, but I used more than one of the 100m reeels last time I did a
>factory rewire, so it wasn't worth buying less.
The joys of being a pro. I'm barely a d-i-yer so I'll have to admire
that sort of relationship with wholesalers from afar.
>> I like the idea of
>> these because only one earth wire would be needed. Trouble is the girl
>> who answered the phone at the local Peco said she'd never heard of
>> using individual wire. She always sells T&E for the purpose and this
>> with 20mm conduit, as 25mm is special order and only sold in bulk.
>
>Again, my local electrical wholesaler (Newey & Eyre) will supply 25mm in
>single lengths. It is to order only, but delivery is next day, to my
>address.
>
>Colin Bignell
I'll renew my search for a similar local supplier.
>In article <d7h3b51akpofvcuvk...@4ax.com>,
> Geoff Mills <GMi...@privacy.net> wrote:
>> Thanks, I started out with the idea that I'd be using T&E cable though
>> perhaps individual wires are more suitable. But then again, if that is
>> so, why would anyone be running 2 T&E cables through conduit?
>
>Saves buying the singles? They have thicker insulation than stripped TW&E.
>And IIRC only come in 100 mtr drums - dunno anyone that sells cut lengths.
Is stripped T&E a realistic option for a small job? If so, does the
earth wire have to be sheathed throughout it's length?
> On Thu, 17 Sep 2009 11:37:00 -0700 (PDT), "js.b1" <js...@ntlworld.com>
> wrote:
>
> <...>
>>You can buy cut lengths of 6491X online. TradingDepot, perhaps
>>AlertElectrical, Gil-Lec, TLC for gr/ye, a few others.
>
> Thanks for the leads. I'll follow them up.
>
> <...>
>
>>If there is no real requirement to use conduit, I would use oval.
>
> Does oval marry up with the surface mounted back boxes in a similar
> way to conduit?
No - you'd probably want mini trunking for that.
Although you could use 20mm oval to 20mm round adapters and metal clad
surface boxes (with 20mm conduit knockouts) - though such adapters are as
rare as hen's teeth.
Also, oval conduit is not as robust as round - it really forms a tube in the
plaster. On the surface it would be easy to squidge.
> Is stripped T&E a realistic option for a small job?
> If so, does the earth wire have to be sheathed throughout it's length?
No.
- Singles (6491X) have thicker insulation than FTE
- Earth MUST be sheathed throughout its length
> Does oval marry up with the surface mounted
> back boxes in a similar way to conduit?
No.
- For surface sockets use round conduit or mini-trunking.
- Round conduit suits "warehouse bare brick" or looks odd.
Options...
- Run FTE in mini-trunking between surface backboxes
- Sink FTE into wall in ZONE between sunk backboxes w/grommets, cover
the plaster cutout cutout with flat wooden bead until redecorated
The latter is much prettier and "lower profile" than mini-trunking
which is a ghastly abomination even in d-line.
In general.
- Capping & Oval require sheathed cable (Flat Twin & Earth, FTE).
- Round Conduit can use singles (6491X) or sheathed cable (Flat Twin &
Earth, FTE).
- With oval fit a grommet to the backbox, butt the oval up against the
grommet
- With plastic round conduit fit female bushes into the backbox, slide
the conduit into the bushes
- With steel round conduit you need proper Die (£25) & Bender (Hilmor
£250)
- Conduit must be installed prior to cable draw in (so enforcing the
rule that if someone got the damn stuff in then when it goes time for
replacement someone else can get it out and back in again!)
- Conduit must be continuous where Singles (6491X) are used, you can't
stop the conduit short and use a grommet
Plastic conduit is only sometimes used in domestic, 20-25mm oval is
flatter.
Steel conduit is very rarely used in domestic re expensive tools &
labour.
You can buy 20mm oval-to-round adapters, MK do them.
- Trading Depot might list them, £0.80-1.00 each
- Cable only passes easily through them one way
- Ok for oval-in-plaster-to-round-in-stud-wall-cavity runs
If you need to run a cable outside a Zone.
1 - Consider if a wiring accessory can be added to create a Zone.
2 - Use BS8436 cable such as Prysmian Flexishield or Earthshield
The problem with BS8436 is £120-180 for 1.5-2.5mm/100m.
Example of where BS8436 is useful:
- Light switch below chimney, no-where else to fit it
- a) BS8436 b) MK Echo (£180) c) Occupancy PIR (£50 + £50 for spare)
- Option a) is best because a switch is more reliable
Example of where BS8436 is useful:
- Room has sloping ceiling so no 150mm HORIZONTAL zone, solid floor
- BS8436 is a lot simpler than wiring accesory route-markers
everywhere
TLC are not carrying BS8436 (I asked, they asked NICEIC). No-one else
does.
Surprised, because "25m" would be a low risk investment for someone to
carry.
OP questions indicate he needs to read John Whitfield's book. Go to
Amazon UK.
>Go buy John Whitfield electrical guide.
Thanks, that's a lot of very good advice.