On 25/07/2022 19:21, rick wrote:
> 2 parts to an earth rod Q.
>
> On advice on another forum - I need to install an Earth rod when a new
> TT circuit is installed.
ok
> What size earth rod do I need ? Looking at some of the the information I
> have it seems to be that an 8' rod is needed ?
It will largely depend on your local soil conditions. In these parts
(Essex clay soil) 4' will get you down into permanently damp soil and a
Ze of under 10 ohms typically.
In different soil you may need longer.
..... how is this
> achieved if you use for example the standard TLC 3/8" (9mm) rod which is
> only 1.2m long ?
You can use additional parallel electrodes if you space them out enough
so that they are not in each others resistance zones.
> It has no threaded section so you can't join them together like you can
> with 5/8" rod
Indeed, so if you need more than 1.2m, the opt for the thicker rod. (you
may have trouble driving the thinner rod to adequate depth without it
bending if you could extended it anyway.
> Or is 4' (1.2m) long enough for domestic install ?
IME yup, but YMMV
> The 2nd part is where every post I have found gives a different answer -
> the protective earth cable from the rod (in its inspection box) will be
> 6491X single cored green/yellow PVC insulated, and carried in flexible
> conduit to the termination point about 2m in total. So at no time is it
> in contact with the ground though for about 1m the flexible conduit is
> buried, as it routes to the termination point.
> I see cable size stated from 2.5 to 16 mm2
The decision list is:
http://wiki.diyfaq.org.uk/index.php/TT_Earthing#Connecting_to_your_earth
So that sounds like buried, protected from corrosion, but no mechanical
protection, so 16mm^2
(assuming that your Ze is 1 ohm or greater)
> The TT circuit it is protecting is 6mm2 32A (via SWA underground cable)
> RCD protected
> What is the correct size earthing conductor to use ?
You don't strictly speaking need a dedicated earth conductor. You would
normally just have 2 core SWA, with the armour connected at the source
end to the supply earth (to ensure the cable has fault protection), and
then the armour would be isolated at the far end (plastic gland), and
the TT Earth connected to the installation earth instead.
> Or as some time in future there may be a need to export PME ... should I
> use 10mm ? as that is minimum.
Depends on if you need to export the equipotential zone as well. If
there is no access to anything local that could be at earth potential,
then you may not. If there is local access to an independent earth (or
extraneous metalwork that would normally need to be bonded) then your
CPC will need to meet the requirements of a main bonding conductor as
well and that would mean 10mm^2 minimum.
http://wiki.diyfaq.org.uk/index.php/Taking_electricity_outside#Exporting_an_Equipotential_Zone
http://wiki.diyfaq.org.uk/index.php?title=Earthing_and_Bonding#Bonding_practice_and_technical_data
--
Cheers,
John.
/=================================================================\