On 20/06/2015 10:19, AL_n wrote:
> John Rumm <see.my.s...@nowhere.null> wrote in
>
news:RvGdnYUq5ryEGhnI...@brightview.co.uk:
>
>>> 13.5mm wide and 7.5mm thick.
>>
>> If you go from the overall size, and compare with the figures in the
>> last column of the table here:
>>
>>
http://wiki.diyfaq.org.uk/index.php?title=Cables#Cable_Sizes
>>
>> That suggests something around the 6mm^2 mark, or its imperial equal.
>
>
> I measured another piece of this cable. I am relying on a tape-measure, not
> a micrometer; the OD appears to be to be possibly 7mm x 13.5mm, which is
> close to the '6.8 x 13.1' stated as the OD of 6mm^ cable. However, would
> the insulation thicknesses be the same in the 1970s/1980s as it is today?
For PVC they are likely to be similar - but the overall cable sheath
size was not standardised then or now - so its not a cast iron
guarantee. You will need to get a calliper on the conductors to be sure.
> Somewhere buried in my house, I have an imperial micrometer. If I can
> somehow manage to find it, I'll be able to measure the exact thicknesses of
> the copper wires.
Yup, that's what you need to be certain.
> 6mm^ certainly does ring a mental bell. ISTR seeing a lot of it in the late
> 1980s. ISTR using it to run power to a Baby Belling (small) cooker back in
> the early 1990s..
Yup, its commonly used for cookers, and used to be used for showers when
they were more modest in power than many modern ones.
> Anyway, assuming it is 6mm^, and I use a circuit breaker at the end of my
> 12m run, I would like to use it to feed a 7.5kw shower.
You will need RCD protection now (17th edition rules) as well.
To check any cable for adequacy, run through the procedure described here:
http://wiki.diyfaq.org.uk/index.php?title=Calculating_A_Cable_Size
> I have some vague recollection of hearing someone say it was frowned-upon
> to connect two or three shorter lengths of this stuff together, when
> feeding a high-wattage appliance. It that a hard-and-fast rule, or is it
> okay to have a couple or more joints using those round, hard plastic 30A
> junction boxes?
With high current circuits, you have most risk of heating at the
termination points. So the more you have, the more "risk" if you like.
However if you do the job correctly and make the terminations tightly
(or better still crimp or solder them), there there is no problem
joining cables.
You will have difficulty getting 2 x 6mm^2 into many junction boxes, so
look for one of the high current ones designed for the application.
Something like:
https://www.tlc-direct.co.uk/Products/LB9065.html
may be a better bet.