Covering An Earth Conductor

603 views
Skip to first unread message

Stuart

unread,
Jul 26, 2006, 2:11:44 PM7/26/06
to
I have to cover the earth wire in my shower switch etc and it is 10mm sq cable(
old colours) and there is no way that I can get earth sleeving on it ( unless
any of you know a way) .Is it O.K. to use tape ( green and yellow) .I presume
that's what it is made for .?


Stuart

Andrew Gabriel

unread,
Jul 26, 2006, 3:39:44 PM7/26/06
to
In article <aubfc2tnc70v6g9p0...@4ax.com>,

I believe that would be fine providing it's done well enough to
be regarded as permanent, and isn't going to fall off after 10
years. The purpose of the sleeving is to identify the conductor
as an earth, not to insulate it. Note that you must use a single
green and yellow tape -- mixing separate green and yellow tape
to create the same effect is specifically forbidden somewhere in
the wiring regs (green might come off, leaving yellow which looks
like a phase conductor identifier).

Of course, sleeving is available in just about any size. If you
go to an electrical wholesaler, they might well give you a few
inches for free. I have some which is large enough for 16mm T&E
somewhere.

--
Andrew Gabriel

Stuart

unread,
Jul 26, 2006, 4:07:19 PM7/26/06
to

I am sure I have some yellow and green somewhere but cant lay my hands on it so
will need to buy anothe roll. .I've looked around for larger bore sleeving but
can't see anywhere selling much above 5mm sq'd


Stuart


Andy Wade

unread,
Jul 26, 2006, 6:17:40 PM7/26/06
to
Stuart wrote:

> I am sure I have some yellow and green somewhere but can't lay my hands on it so


> will need to buy anothe roll.

No, sorry, tape isn't allowed for this. Reg. 543-03-02 specifically
requires the use of sleeving complying with BS 2848.

> .I've looked around for larger bore sleeving but
> can't see anywhere selling much above 5mm sq'd

I think you're confusing area and diameter there. The largest 'earth'
that requires sleeving is 6 mm^2 (area). This has a diameter over the
seven wire strands of just over 3 mm - so readily available 4mm (i/d)
sleeving is fine.

--
Andy

Stuart

unread,
Jul 26, 2006, 8:10:08 PM7/26/06
to
On Wed, 26 Jul 2006 23:17:40 +0100, Andy Wade <spamb...@ajwade.clara.co.uk>
wrote:

I'm not sure what exactly you mean when you say "the largest earth that requires
sleeving is 6mm sq (area) " Do you mean the earth within 6mm sq T+E cable .?
If you do mean that then what about larger capacity cable .? You seem to be
suggesting it does not need sleeving .

The cable I am using is 10mm sq T+E and so far I haven't been able to get any
sleeving that will look anywhere near to going on this ,even warming it doesn't
help.


Stuart

meow...@care2.com

unread,
Jul 26, 2006, 8:28:02 PM7/26/06
to
Stuart wrote:

> The cable I am using is 10mm sq T+E and so far I haven't been able to get any
> sleeving that will look anywhere near to going on this ,even warming it doesn't
> help.
>
>
> Stuart

probably quicker to get a little tin of humbrol yellow for 50p and
paint a few lines on. Household gloss topcoat should stick very well.


NT

Stuart

unread,
Jul 26, 2006, 8:33:57 PM7/26/06
to

Or get two lengths of sleeving and slice them each lengthways then put one
length on then glue the other on top over the opening of the first length .

S

Stuart

unread,
Jul 26, 2006, 9:15:01 PM7/26/06
to
On Wed, 26 Jul 2006 23:17:40 +0100, Andy Wade <spamb...@ajwade.clara.co.uk>
wrote:

>Stuart wrote:

Further to my other posts I've found some other sleeving that I managed to get
on to the earth conductor so that sorts that problem

thx again


S

Christian McArdle

unread,
Jul 27, 2006, 5:47:10 AM7/27/06
to
> I'm not sure what exactly you mean when you say "the largest earth that
requires
> sleeving is 6mm sq (area) " Do you mean the earth within 6mm sq T+E cable
.?

No. The earth within T&E cable is (more the larger sizes) of much smaller
area than the live conductors. I can't remember the exact size of the earth
within 10mm T&E, but wouldn't fall on the floor with shock if it happened to
be 6mm.

Christian.

Richard Conway

unread,
Jul 27, 2006, 8:05:44 AM7/27/06
to

There's a joke in there somewhere.

zikkim...@connectfree.co.uk

unread,
Jul 27, 2006, 8:27:57 AM7/27/06
to

Stuart wrote:
> On Wed, 26 Jul 2006 23:17:40 +0100, Andy Wade <spamb...@ajwade.clara.co.uk>
> wrote:
>
> >Stuart wrote:
> >
> >> I am sure I have some yellow and green somewhere but can't lay my hands on it so
> >> will need to buy anothe roll.

<snip>

Good to hear the OP has solved this, but just in case others come
googling.......

Would it be permissable to untwist the earch conductor, re twist it
into two thinner "wires" sleave each of them and then connect them as
one (you could even recombine the twists at this point) into the
accessory?

Andy Wade

unread,
Jul 29, 2006, 7:09:43 AM7/29/06
to
Stuart wrote:

> On Wed, 26 Jul 2006 23:17:40 +0100, Andy Wade <spamb...@ajwade.clara.co.uk>
> wrote:
>>I think you're confusing area and diameter there. The largest 'earth'
>>that requires sleeving is 6 mm^2 (area). This has a diameter over the
>>seven wire strands of just over 3 mm - so readily available 4mm (i/d)
>>sleeving is fine.
>
> I'm not sure what exactly you mean when you say "the largest earth that requires
> sleeving is 6mm sq (area) " Do you mean the earth within 6mm sq T+E cable .?
> If you do mean that then what about larger capacity cable .? You seem to be
> suggesting it does not need sleeving .

No, I mean that the requirement to fit sleeving only applies to earths
that are themselves of a size up to and including 6 mm^2. All sizes of
T&E need their CPC (earth) conductor to be sleeved. The largest size of
T&E is 16 mm^2 (with 6 mm^2 CPC). In general the CPC in T&E is two
steps smaller than the L & N conductors - the only exceptions are 2.5
mm^2 which has a 1.5 mm^2 CPC and both 1.5 and 1.0 mm^2 which have 1.0
mm^2 CPCs.

> The cable I am using is 10mm sq T+E and so far I haven't been able to get any
> sleeving that will look anywhere near to going on this ,even warming it doesn't
> help.

I really don't understand why you're having this problem. Adequately
sized sleeving is readily available - e.g. here:
http://www.tlc-direct.co.uk/Main_Index/Cable_Accessories_Index/Sleeving/index.html

--
Andy