I have a open pumped CH/Gravity HW system. I need to refill with inhibitor,
but am confused if which I should use.
Fernox produce MB1 and F1 but it is not clear what the
advantages/disadvantages of each are? Alternativly I have looked at Screwfix
No Nonsense range.
The house is a 4 bed, with 11 rads. How much inhibitor should I be using? I
am guess at 1 bottle of MB1/F2, or using 2 for screwfix.
What is the consensus on which inhibitor to use here?
Fernox - no question.
Likely 1 bottle is OK.
Check with their excellent support for true dosage, recommended product etc.
The other rated inhitor is Sentinel but I have found better results with
Fernox.
No commercial interest, just satisfied customer (along with many other
members of this group)
Phil
> Fernox - no question.
> Likely 1 bottle is OK.
> Check with their excellent support for true dosage, recommended product
> etc.
Is the MB1 or F1?
Andy
On this subject of central heating, how long can I leave cleaner in my
system?
Dave
A HAH! a little rummage gets me a safety data sheet.
MB-1 contains 1-5% triethanolamine
(so 40-200 ml active ingredient per bottle)
F1 contains:
triethanolamine 20-30%
boric acid 15-20%
2,2'-iminodiethanol 1-5%
1h-benzotriazole 1-5%
molybdenum trioxide 1-5%
(which is 100-150ml triethanolamine per bottle, plus the other stuff,
for about the same price...)
Andy