Heating two indirect hot water cylinders

209 views
Skip to first unread message

Geoff Pearson

unread,
Jan 2, 2013, 12:22:02 PM1/2/13
to
I have a hot water cylinder upstairs which is heated from my boiler,
controlled by a thermostat on the tank and a fully pumped central heating
system.

I have another bathroom downstairs, with its own hot water cylinder, cold
tank etc, entirely independent of the rest of the house - its water is
heated by an immersion heater, although there is an unused indirect coil in
the cylinder.

I know want to add this cylinder to the main system. I plan to use a
thermostat on it, similar to the first one, connect it with 22 mm to the
same circuit as the first one, in parallel. Both might take a hot feed at
the same time or either one call for heat. Twin port valve to each
controlled by the thermostats?

Any problems with this plan?

Geoff

John Rumm

unread,
Jan 2, 2013, 1:47:45 PM1/2/13
to
The normal solution would be to make it a S+ plan system with a two port
valve for each zone. So in your case, one heating zone and two hot water.

So similar to:

http://wiki.diyfaq.org.uk/index.php?title=Central_Heating_Controls_and_Zoning#Multiple_heating_zones:_S_Plus-plan

but with two cylinders and one set of rads.

--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

meow...@care2.com

unread,
Jan 2, 2013, 2:42:34 PM1/2/13
to
I'd plumb the heating coils in parallel and connect the cylinder stats in parallel, so if either calls for heat, both get it. This means one will overshoot the target temp, but only upto at worst the temp of the primary circuit. The cooler cyl will be heated more than the hotter one, since the delta T across the exchanger is greater.


NT

John Rumm

unread,
Jan 2, 2013, 2:47:52 PM1/2/13
to
The risks of that could include one cylinder getting upto 85 degrees
depending on the flow temp. This is risks to the users of the water if
there are no blending valves, and can also make scaling of the cylinder
more rapid and pronounced in hard water areas.

harry

unread,
Jan 3, 2013, 5:25:14 AM1/3/13
to
You will need valves to balance the heating water flow between the two
tanks in exactly the same way as radiators.

It will have quite a long recovery period. (ie warming up from cold).

Richard Conway

unread,
Jan 3, 2013, 6:02:58 AM1/3/13
to
How about using the closed live output from one of the valves to trigger
the second valve (via the thermostat) - that way you could give one tank
priority over the other, so from cold you could use one bathroom first.

--- news://freenews.netfront.net/ - complaints: ne...@netfront.net ---

meow...@care2.com

unread,
Jan 3, 2013, 1:37:25 PM1/3/13
to
On Wednesday, January 2, 2013 7:47:52 PM UTC, John Rumm wrote:
> On 02/01/2013 19:42, meow...@care2.com wrote:
>
> > On Wednesday, January 2, 2013 5:22:02 PM UTC, Geoff Pearson wrote:
>
> >
>
> >> I have a hot water cylinder upstairs which is heated from my
>
> >> boiler, controlled by a thermostat on the tank and a fully pumped
>
> >> central heating system. I have another bathroom downstairs, with
>
> >> its own hot water cylinder, cold tank etc, entirely independent of
>
> >> the rest of the house - its water is heated by an immersion heater,
>
> >> although there is an unused indirect coil in the cylinder. I know
>
> >> want to add this cylinder to the main system. I plan to use a
>
> >> thermostat on it, similar to the first one, connect it with 22 mm
>
> >> to the same circuit as the first one, in parallel. Both might take
>
> >> a hot feed at the same time or either one call for heat. Twin port
>
> >> valve to each controlled by the thermostats? Any problems with this
>
> >> plan? Geoff
>
> >
>
> > I'd plumb the heating coils in parallel and connect the cylinder
>
> > stats in parallel, so if either calls for heat, both get it. This
>
> > means one will overshoot the target temp, but only upto at worst the
>
> > temp of the primary circuit. The cooler cyl will be heated more than
>
> > the hotter one, since the delta T across the exchanger is greater.
>
>
>
> The risks of that could include one cylinder getting upto 85 degrees
>
> depending on the flow temp. This is risks to the users of the water if
>
> there are no blending valves, and can also make scaling of the cylinder
>
> more rapid and pronounced in hard water areas.

I guess it depends whether the OP wants water that hot or not. I had it hotter at one place to get enough capacity


NT

Dave Liquorice

unread,
Jan 3, 2013, 5:02:25 PM1/3/13
to
On Wed, 2 Jan 2013 17:22:02 -0000, Geoff Pearson wrote:

> I know want to add this cylinder to the main system. I plan to use a
> thermostat on it, similar to the first one, connect it with 22 mm to
> the same circuit as the first one, in parallel. Both might take a hot
> feed at the same time or either one call for heat. Twin port valve to
> each controlled by the thermostats?
>
> Any problems with this plan?

That is what I would do with the addition of another channel of time
control for the second cylinder. Keeping a cylinder of hot water hot
"just in case" is a good way to burn more gas than you have too. The heat
time of a single cylinder from cool shouldn't be more than 30 minutes,
it's not difficult to "pop the water on" 30 plus mins before you want to
use it. If if both cylinders are cold the reheat time might be an issue
but again a simply manual priority switch (set the relevant programmer to
OFF) solves that.

--
Cheers
Dave.