Wiring Up Garages

116 views
Skip to first unread message

Drumtochty

unread,
Apr 30, 2013, 2:51:48 PM4/30/13
to
I have a 100 Amp supply into the house and at peak use we maybe get to 25 Amps in the house. No electric showers or hob.

I want to take a 40 amp supply to the garage via a 10 sqmm three core SWA cable around 30m long buried for 20 mtrs.

Please advise if I am getting this correct.

As I will have a car lift it needs a 32amp type D mcb in the garage.

At the house consumer unit the swa is earthed to the consumer unit as well as using one of the conductors to run the earth. The house consumer unit mcb for the garage will be 50 amp type D. It will be on the earth leakage side of the house consumer unit.

At the main garage consumer unit, SWA will not be connected. The three conductors will be connected phase, neutral and earth.

The lights in the main garage will be on the non earth leakage side of the garage consumer unit. The following will be connected to the earth leakage side of the main garage consumer unit.

Sockets 32A mcb type B with max load of a compressor 10 amps.

Car Lift 32A mcb type D, 25 amp at start up but load while lifting 15 amps.
So only used for a two minutes at a time.

Heating 32A mcb type B with at max a 20 amp load but very well insulated garage so hopefully 10 amps most of the time.

Garage 2

This is half way between the house and main garage. At most lighting and a compressor. Max load 12 amps usually nearer 0.5 amps.

Lights on garage 2 non earth leakage side of garage 2 consumer unit.
Sockets in garage 2 on the earth leakage side of garage 2 consumer unit.

The 15mtr long 2.5 sqmm SWA three core cable will not have the SWA connected to earth at garage 2 consumer unit but will have at the other side. It will be buried

It suits me better to take the garage 2 supply from the main garage rather than the house consumer unit. I assume it should be fed from the earth leakage side of the main garage consumer unit. A 32 Amp type B mcb.

Comments please.



John Rumm

unread,
Apr 30, 2013, 6:04:03 PM4/30/13
to
On 30/04/2013 19:51, Drumtochty wrote:

> I have a 100 Amp supply into the house and at peak use we maybe get
> to 25 Amps in the house. No electric showers or hob.
>
> I want to take a 40 amp supply to the garage via a 10 sqmm three core
> SWA cable around 30m long buried for 20 mtrs.

This is a detached garage I take it?

What earthing system does the house have [1]?

What type of CU do you currently have (e.g. split load with single RCD etc?)

> Please advise if I am getting this correct.
>
> As I will have a car lift it needs a 32amp type D mcb in the garage.
>
> At the house consumer unit the swa is earthed to the consumer unit as
> well as using one of the conductors to run the earth. The house

Why are you using a conductor as well as the armour? (i.e. is it
intended to be a "belt & braces" or are you planning to export a PME
equipotential zone and hence need the effective CSA?)

> consumer unit mcb for the garage will be 50 amp type D. It will be on
> the earth leakage side of the house consumer unit.

Do you mean in will be on the RCD protected side? If so then that would
not be a good plan, since any trip at the head end will isolate the
garage completely - potentially creating a hazardous situation with loss
of lighting in the garage.

Also if you want a 40A supply, why are you using a 50A MCB?

(at 50A, the voltage drop on an 30m XLPE SWA would be over your
allowable 3% for lighting circuits - so you would need to go to 16mm^2)

> At the main garage consumer unit, SWA will not be connected. The
> three conductors will be connected phase, neutral and earth.

I can't see the logic for not connecting the armour, if you are
exporting the earth from the house down a core in the cable.

This sort of arrangement makes sense when you are not exporting the an
earth, and making the garage a TT earthed installation in its own right.


> The lights in the main garage will be on the non earth leakage side
> of the garage consumer unit. The following will be connected to the
> earth leakage side of the main garage consumer unit.

Note that if the feed itself is RCD protected (and the RCD is not a time
delay RCD) then any further segregating into RCD and non RCD circuits
makes little sense. Since any trip would be equally likely to take out
the head end RCD.

> Sockets 32A mcb type B with max load of a compressor 10 amps.
>
> Car Lift 32A mcb type D, 25 amp at start up but load while lifting 15
> amps. So only used for a two minutes at a time.

Sounds like a 16A type D would be more in keeping here? Presumably the
lift motor will be an induction motor. Their inrush will normally be in
the range of 5 to 9x the nominal load. A type D breaker will permit an
inrush of up to at least 10x the nominal current.

> Heating 32A mcb type B with at max a 20 amp load but very well
> insulated garage so hopefully 10 amps most of the time.

ok

> Garage 2
>
> This is half way between the house and main garage. At most lighting
> and a compressor. Max load 12 amps usually nearer 0.5 amps.
>
> Lights on garage 2 non earth leakage side of garage 2 consumer unit.
> Sockets in garage 2 on the earth leakage side of garage 2 consumer
> unit.
>
> The 15mtr long 2.5 sqmm SWA three core cable will not have the SWA
> connected to earth at garage 2 consumer unit but will have at the
> other side. It will be buried
>
> It suits me better to take the garage 2 supply from the main garage
> rather than the house consumer unit. I assume it should be fed from
> the earth leakage side of the main garage consumer unit. A 32 Amp
> type B mcb.
>
> Comments please.

Could I suggest having a look at:

http://wiki.diyfaq.org.uk/index.php?title=Taking_electricity_outside

and note the sections on exporting earths and equipotential zones.

What you describe here sounds like a classic scenario for not exporting
the house earth, and going TT in the garage(s) [2]

Thus you would typically use a 2 core SWA with the armour connected at
the head end. The SWA fed from a non RCD protected MCB (assuming the
house is not already TT, or a type S time delay RCD if it is). The
garage can then be configured as a TT installation, with an insulated
(i.e. plastic) 17th edition style split load CU (or better a high
integrity type, or all RCBO CU [3]) connected to just the L&N feeds, and
a separate connection to an earth stake.

(Note also I have not checked all your proposed cable sizes for
suitability).

[1] http://wiki.diyfaq.org.uk/index.php?title=Earthing_Types

[2] http://wiki.diyfaq.org.uk/index.php?title=TT_Earthing

[3] http://wiki.diyfaq.org.uk/index.php?title=17th_Edition_Consumer_Units



--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Stewith

unread,
Apr 30, 2013, 6:43:30 PM4/30/13
to
Its very likely that the the short circuit fault current will not be
suffucient to trip the
A D50 mcb at the house end quickly enough, and also unlikely to be enough
for the
D32 at the other end.
It also sounds like you are going to have 2 RCD's in series so unless you
are going to
TT the garage,the garage lights will still take out the RCD in the house.






"Drumtochty" <auche...@gmail.com> wrote in message
news:3a282bc1-81d0-4e4d...@googlegroups.com...

Drumtochty

unread,
Apr 30, 2013, 7:38:40 PM4/30/13
to
The house earthing is TN-S
The main switch on the consumer unit is a double pole 100 Amp.
The fuse rail is split into two, one side having no RCD protection, the other side is though a Votex VR63 63 A capacity 30 mA RCD
I thought using both the swa and the conductor for earth would be belts and braces.

I will read the linked documents tomorrow and come back tomorrow evening. Thanks so far guys.

John Rumm

unread,
Apr 30, 2013, 10:52:57 PM4/30/13
to
On 01/05/2013 00:38, Drumtochty wrote:

> The house earthing is TN-S

That makes life a bit easier, since if you did choose to export the
earth, you would not also need to export the equipotential zone with it
(and hence main bonding conductor etc).

> The main switch on the consumer unit is a double pole 100 Amp.
> The fuse rail is split into two, one side having no RCD protection, the other side is though a Votex VR63 63 A capacity 30 mA RCD
> I thought using both the swa and the conductor for earth would be belts and braces.

In which case you can take the SWA feed from the non RCD side, and that
saves problems with having any cascaded RCDs. If exporting the earth,
then a 2 core SWA, using the armour for earth, connected to a metal CU
in the garage. If going the TT route, then similar except an insulated
CU in the garage so that the armour is in effect only earthed at one end.

> I will read the linked documents tomorrow and come back tomorrow evening. Thanks so far guys.