On 30/04/2013 19:51, Drumtochty wrote:
> I have a 100 Amp supply into the house and at peak use we maybe get
> to 25 Amps in the house. No electric showers or hob.
>
> I want to take a 40 amp supply to the garage via a 10 sqmm three core
> SWA cable around 30m long buried for 20 mtrs.
This is a detached garage I take it?
What earthing system does the house have [1]?
What type of CU do you currently have (e.g. split load with single RCD etc?)
> Please advise if I am getting this correct.
>
> As I will have a car lift it needs a 32amp type D mcb in the garage.
>
> At the house consumer unit the swa is earthed to the consumer unit as
> well as using one of the conductors to run the earth. The house
Why are you using a conductor as well as the armour? (i.e. is it
intended to be a "belt & braces" or are you planning to export a PME
equipotential zone and hence need the effective CSA?)
> consumer unit mcb for the garage will be 50 amp type D. It will be on
> the earth leakage side of the house consumer unit.
Do you mean in will be on the RCD protected side? If so then that would
not be a good plan, since any trip at the head end will isolate the
garage completely - potentially creating a hazardous situation with loss
of lighting in the garage.
Also if you want a 40A supply, why are you using a 50A MCB?
(at 50A, the voltage drop on an 30m XLPE SWA would be over your
allowable 3% for lighting circuits - so you would need to go to 16mm^2)
> At the main garage consumer unit, SWA will not be connected. The
> three conductors will be connected phase, neutral and earth.
I can't see the logic for not connecting the armour, if you are
exporting the earth from the house down a core in the cable.
This sort of arrangement makes sense when you are not exporting the an
earth, and making the garage a TT earthed installation in its own right.
> The lights in the main garage will be on the non earth leakage side
> of the garage consumer unit. The following will be connected to the
> earth leakage side of the main garage consumer unit.
Note that if the feed itself is RCD protected (and the RCD is not a time
delay RCD) then any further segregating into RCD and non RCD circuits
makes little sense. Since any trip would be equally likely to take out
the head end RCD.
> Sockets 32A mcb type B with max load of a compressor 10 amps.
>
> Car Lift 32A mcb type D, 25 amp at start up but load while lifting 15
> amps. So only used for a two minutes at a time.
Sounds like a 16A type D would be more in keeping here? Presumably the
lift motor will be an induction motor. Their inrush will normally be in
the range of 5 to 9x the nominal load. A type D breaker will permit an
inrush of up to at least 10x the nominal current.
> Heating 32A mcb type B with at max a 20 amp load but very well
> insulated garage so hopefully 10 amps most of the time.
ok
> Garage 2
>
> This is half way between the house and main garage. At most lighting
> and a compressor. Max load 12 amps usually nearer 0.5 amps.
>
> Lights on garage 2 non earth leakage side of garage 2 consumer unit.
> Sockets in garage 2 on the earth leakage side of garage 2 consumer
> unit.
>
> The 15mtr long 2.5 sqmm SWA three core cable will not have the SWA
> connected to earth at garage 2 consumer unit but will have at the
> other side. It will be buried
>
> It suits me better to take the garage 2 supply from the main garage
> rather than the house consumer unit. I assume it should be fed from
> the earth leakage side of the main garage consumer unit. A 32 Amp
> type B mcb.
>
> Comments please.
Could I suggest having a look at:
http://wiki.diyfaq.org.uk/index.php?title=Taking_electricity_outside
and note the sections on exporting earths and equipotential zones.
What you describe here sounds like a classic scenario for not exporting
the house earth, and going TT in the garage(s) [2]
Thus you would typically use a 2 core SWA with the armour connected at
the head end. The SWA fed from a non RCD protected MCB (assuming the
house is not already TT, or a type S time delay RCD if it is). The
garage can then be configured as a TT installation, with an insulated
(i.e. plastic) 17th edition style split load CU (or better a high
integrity type, or all RCBO CU [3]) connected to just the L&N feeds, and
a separate connection to an earth stake.
(Note also I have not checked all your proposed cable sizes for
suitability).
[1]
http://wiki.diyfaq.org.uk/index.php?title=Earthing_Types
[2]
http://wiki.diyfaq.org.uk/index.php?title=TT_Earthing
[3]
http://wiki.diyfaq.org.uk/index.php?title=17th_Edition_Consumer_Units
--
Cheers,
John.
/=================================================================\