In article <Igyiw.45126$Kl4....@fx01.am4>, The Medway Handyman
<
davi...@blueyonder.co.uk> writes
>No 1 daughter has bought a fancy metal chandelier for the dining room
>and asked me to fit it.
>
>Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
>switch either, so I'm guessing the wiring dates from when lighting
>circuits weren't earthed?
>
>I've told her it can't be fitted. No 1 daughter, like most females, is
>not easily dissuaded once she has made her mind up...
>
>What are the dangers of a class 1 lighting fitment not being earthed, so
>I can reinforce my argument?
>
The short answer is that Class 1 equipment _must_ be earthed, it will
say so in the instructions. Otherwise there is a risk to the user of
electrocution if there a fault.
The long answer is that the designer made reliance on an earth
connection to guarantee its safe operation. It is likely that a single
fault within the appliance (eg. chafing of a single layer of insulation)
could result in the metalwork becoming live and so to cover that failure
mode it is earthed to protect the user. Without the earth, in those
circumstances, the user could receive a fatal electric shock.
You can get metal cased class 2 lamps/products too but they have been
designed in such a way that a single fault will not expose the user to a
risk of shock. They are designed such that it would take 2 distinct and
separate failures[1] to put the user at risk. As a result they are much
safer and so can be used without an earth. This is represented in the
class 2 'double insulated' square within a square symbol.
Having heard you mention your daughter's background here before I was
surprised that she would be so carefree about a safety related issue.
Rules and procedures, sod it, just slap the defib on and set to max,
CLEAR, nah, that's for wooses . . . .
[1] technically it is possible to use 'reinforced' insulation where it
is not practical to use 2 separate ones.
--
fred
it's a ba-na-na . . . .