A couple of thoughts. The solenoid on the front of your generator pulls
back a lever to enable the generator to start and run. If you watch the
solenoid, it should pull in when you are cranking the engine with the
starter. If it does not do anything then check to see if it is getting
12 volts. If you manually pull the solenoid in and try to start the
generator it should start and run until you release the solenoid.
The solenoid has two coils. The pull coil is stronger and pulls more
amps and pulls in the solenoid. The hold coil is weaker, pulls less amps
and holds the solenoid plunger. The switch is internal and those are the
contacts mentioned by Jorge. One source of failure is that the pull
portion stays engaged and overheats the solenoid. The pull portion is
meant to be only momentarily engaged until the hold portion takes over.
The hold portion is engaged as long as the generator is running.
You can get more info on this at BoatDiesel.com. You have to pay $25
annually but they have a huge amount of info in their forums on diesel
engines and generators and it is well worth the money.
FWIW if the solenoid is bad I would certainly use the cheaper one.
Good luck
Frank Burrows 79 43' Viking Piney Narrows Chesapeake Bay
On 3/14/2018 7:35 PM, Alan Shapiro via Trawlers-and-Trawlering wrote:
> Thanks to all for their suggestions, although I would still like to
> know if the later solenoid would do the job.
>
> In the meantime I can say with certainty that the problem is not the
> battery nor is it the glow plug (which is not in the block but rather
> is in the air intake and can be seen to be working properly).
Onan Generator Fuel Stop Solenoid