Kris,
You are getting yourself confused by the units.
Your device is drawing 50W. It is running off 240V. Therefore it is drawing about (50 / 240) or 0.2 Amps (I say “about” because of the power factor that Ada already mentioned – but let’s assume a resistive load for the moment).
This is simply worked out from P=IV (or Power equals Current multiplied by Voltage).
So we now know how much it draws from the supply (both “Power” and “Current”) at every instant in time. Both Power and Current are instantaneous values – there is no concept of “time” with either value.
Now you want to know how long it will last. To do that, just multiply the above values by the time you are interested in – in this case 16 hours.
Power multiplied by time gives you energy*. Energy can be measured in Watt-Hours (that is Watts *times* Hours – not Watts *per* Hour) or in Watt-Seconds, which are also known as Joules. Most science and engineering will talk about energy in Joules, but we buy our electricity in kW-Hr. You are still buying energy, not power.
So over the 16 hour period your device will consume (50 * 16) or 800 Watt-Hours, which can also be written as 0.8 kW-Hr. It could also be written as (50 * 16 * 60 * 60) or 2.88 Mega Joules.
We also know that over 16 hours it will draw (0.2 * 16) or 3.2 Amp-Hours. So assuming everything had perfect efficiency, your device could be run from a 3.2 Amp-Hr battery.
In reality there is a lot of conversions going on here – you are converting from AC to DC; 240 V to 12 V; electrical energy to chemical energy; etc. There will be some loss in each step of the process.
When you are working out what size UPS you need there are 2 factors to consider:-
1. How much power is drawn (instantaneous);
2. How much energy in total can be delivered.
Your load is only 50W, so the first condition would be easily met by an off-the-shelf 1000VA UPS. For the moment let’s assume the UPS is rated for 10 minutes of run time at full load (this is a fairly typical figure for small desktop UPS’es – they are really only designed to run a PC for long enough to shut it down cleanly).
If the UPS can run 1000W (again assuming resistive load**) for 10 minutes, then it could run 50W (1/20th of 1000W) for 20 times as long. So your device could be powered for around 200 minutes, or 3 hours & 20 minutes. Not long enough for your application. And again, in reality things do not always scale linearly, so the real time if you tested this would probably be anywhere from 2 hours to 4 hours – but hopefully you get the picture.
So if a 1000VA UPS won’t cut it, you obviously need a bigger UPS, right? NO! (or at least not necessarily). You could buy a bigger UPS, say 5000VA, still with a run time of 10 minutes at full load. This would then run your 50W load for (theoretically) 1000 minutes, or just over 16 ½ hours. But if you did this you would be paying more money for the bigger electronics need to supply 5000VA of (instantaneous) power, as well as for the extra energy (batteries) that you need to run the load for the full 16 hours.
The better option is to look for a UPS that can supply at least 2 to 4 times your instantaneous power (let’s say a minimum of 200VA), but with bigger, or expandable, battery capacity.
Hope that helps clear up some of the confusion.
Regards,
Aaron.
* Mathematically, it is the integral of power over time ( S P dt )
** I’ve been very sloppy here with equating VA to Watts. They both refer to volts multiplied by amps, but when you are working out Watts you only consider the current that is “in phase” with the voltage. It gets complicated, but basically if you draw a right-angled triangle the current used in calculating the VA rating would be the hypotenuse of the triangle. The current used in calculating the Watt rating would be one of the other (shorter) sides. Thus the VA rating is always higher. So a 1000VA UPS is usually only capable of running around 800W of computer equipment. Since manufactures like to quote the bigger numbers on their glossy brochures, UPS’es are usually sized in VA.
And one last thing – it has been a while since I worked in this space, but there used to be fairly strict restrictions on what you could connect to your off-peak meter. Even getting to the connections can be tricky as they are usually sealed by you energy supplier.
--
Sorry – when I said 3.2 Amp-Hr battery, that is at 240V, so you would need a string of 20 by 12V batteries (impractical) or a single 12V battery 20 times as big (64 Amp-Hr). (I knew something didn’t quite sound right, but was concentrating on something else)
Aaron.