I think that works out to about 90% of the sunlight's heat not getting past the roof surface or getting into the attic.
So far I have been astonished to find that my attic temperatures trending only about 2º warmer than the conditioned spaces below the attic. The under side of the roof decking runs about 1º warmer than the attic air temperature.
On a recent 94º day the second floor of the house was 74º (maintained with mechanical cooling) - the attic air temperature was 76º - and the underside of the wooden roof decking was 77º.
stephen
-----------
Do you recall what the temperatures were like before the new roofing? A good
deal higher I take it?
What part of the country are you in?
How do you like the roof all around? Aesthetics? Noise? Shows dirt?
If you are up for it, we could do a page on it with a few pictures and your
measurements?
Best,
Gary
Everyone asks me about the noise. <g> So far as I can tell there is no difference in noise levels. I think people picture what a plain metal roof unsupported over purlins sounds like. Like a shed or industrial building. With this metal being screwed down solidly to wood decking it's not like that.
I was ready to be impressed but I am really astonished. When I first went up into the attic this summer, on a 90+ degree day, I thought the air ducts had come apart and that I was air conditioning the attic. <g>
Luckily it was very pleasant up there crawling around searching air duct leaks. When I didn't find any (and I couldn't imagine how Allen Funt could be hiding anywhere) I laid there a minute to ponder it. Then I thought to reach up and touch the roof decking - and I found it cool to the touch. <g>
That's what made me go up next time with a thermocouple to actually measure.
My attic temps used to trend about 30-50º over ambient in the summer so it was common to find the attic 130-140º on a hot day.
Another problem I found with asphalt shingles is their thermal mass. I don't know their specific heat but they weigh about 30 lbs. per square foot per roof layer. And many roofs are double layered - as mine was. Triple layered in some places.
The metal roofing weighs about 1 lb. per square foot I think. Although mine weighs less as I used aluminum rather than aluminized steel. With shingles they are a huge hot mass of stored heat for much of the night too. After midnight my shingled roof was very warm to the touch.
I am fond of the look of the new roof. Here are some pics taken as we were installing it. I think I have some pics showing it now but I'll have to track them down.
I'll get a remote reading thermometer and install it with the display down in the hallway. I use them all the time on my hot water solar system anyway.
BTW: I also reduced my A/C capacity from 6 tons to 3 tons and the units still cycle off on 100º days - so they are still oversized for the cooling load. I am going to replace the first floor furnace as soon as the weather is cooler so I think I'll try a 1 ton compressor in the downstairs condensing unit.
stephen
-----------
| If one can get an air wash under the white metal ... even better --- On Tue, 7/26/11, CJE <cje...@verizon.net> wrote: |
|
But my eventual conclusion was that having the air space requires the assumption that the underside of the metal will be above the outdoor temperature.
And that didn't seem likely to be the case - if I was going to be reflecting/emitting over 90% of the sunlight away from the metal.
Venting the underside of the metal would keep the roof decking at about outdoor ambient temperature - which is exactly what I was trying to avoid.
What do you picture the gain to underside venting to be?
stephen
-----------
| quicker cooling when the sun goes down ? better night time cooling ? |
90 lbs per bundle - four bundles per square - plus tarpaper and nails. But the 300 lbs per square number I used came from measured dumpster weights from stripping various roofs.
Oh wait - I'll have to go check - maybe I am wrong about the metal weight too. <g>
stephen
----------
. On Jul 26, 2011, at 10:54 AM, Gary BIs wrote: Hi Stephen, That's pretty impressive. Do you recall what the temperatures were like before the new roofing? A good deal higher I take it? What part of the country are you in? How do you like the roof all around? Aesthetics? Noise? Shows dirt? If you are up for it, we could do a page on it with a few pictures and your measurements? Best, Gary On 7/26/2011 7:58 AM, CJE wrote:
I bought the remote / indoor temperature stat today but I didn't get it installed in the attic here yet. I used it all day to see the difference between my truck's interior and the air coming out of the vents. <g>
I e-mailed Sheffield to ask how much the metal weighs too. Although my concern for thermal mass was pretty much for nothing anyway - because if no heat comes through the Cool/R metal, then the asphalt shingles won't store any heat anyway. The installers told me that 99% of the time they just go right over the asphalt shingles. That seemed crazy to me but now that I can measure the results - it doesn't seem that crazy anymore. <g>
Still; I didn't want all the old roofing up there anyway - so I stripped it all down to the wood decking.
stephen
----------
----- Original Message -----
From: "nick pine" <ni...@early.com>
To: "sunspace" <suns...@googlegroups.com>
Sent: Sunday, August 07, 2011 7:45 AM
Subject: Re: anti solar - preemptive cooling - 2