>... we might well solar heat an existing house without architectural changes or loss of floorspace by:
> 1. Measuring its thermal conductance by looking at fuel bills and indoor electrical use, or by heating it with electric space heaters with thermostats for a while and reading the house electric meter; and
>
> 2. Lowering that conductance with airsealing, more insulation, or seasonal foamboard window inserts; and
After blower door testing and airsealing the uninsulated 2x4 walls
with a dense pack cellulose insulation retrofit, Terri's 100-year-old
house (photo on page 8 of
http://sbse.org/newsletter/issues/newsf08.pdf
) used 208 therms of natural gas at 95% efficiency (19.8 million Btu)
and 551 kWh of electricity totaling 21.6 million Btu in January of
2011, when the average outdoor temp was 32 F, so the house conductance
is now 21.6M/(65-32)/31d/24h = 881 Btu/h-F, so it would need
24h(65-36.6)881 = 600KBtu for an average 36.6 F December day near NYC.
Indoor electrical use provided about 61K Btu, leaving a need for 538K
Btu/day of solar heat in an average year, including gas water heating
energy.
> 3. Adding enough solar siding to heat it for 24 hours on an average December day, if possible; and
PVWATTS says the southeast and southwest walls receive 685 and 701 Btu/
ft^2 of sun on an average December day, with an average 40 F daytime
temp and a potential solar siding gain of 0.8x685-6h(70-40)1ft^2/R2 =
458 Btu/ft^2 on the southeast and 471 for the southwest. An 8'x40'
patch of SE siding would contribute 147K Btu/day, with 151K for SW.
> 4. Adding a solar yard furnace with enough glazing to heat the house on an average December day (if steps 2 and 3 won't accomplish that) and enough heat storage to keep the house warm and heat water for showers for 5 cloudy days in a row.
According to PVWATTS, an R2 twinwall yard furnace roof with 80% solar
transmission and a 60 degree tilt would receive 967 Btu/ft^2 on an
average December day. It could collect about 0.8x967-6h(70-40)1ft^2/R2
= 684 tu/ft^2 of heat.
With no solar siding, the yard furnace roof could be 538K/684 = 787
ft^2, eg 40'x20'. Adding 320 ft^2 of SE solar siding above the porch
roof would reduce this to (538K-147K)/684 = 572 ft^2, eg 32'x20'.
Adding 320 ft^2 of SW siding above the driveway would reduce the yard
furnace roof size to (538K-147K-151K)/684 = 351 ft^2, eg 24'x16'.
But Terri would like to enclose the whole south wall in a transparent
lean-to sunspace. It might have a $4500 40'x36' clear vinyl panel from
http://www.farmtek.com/farm/supplies/prod1;ft1_canopies_tents;pg105657_105659.html
that rolls down a quarter-cylindrical frame made with 6 $5 double
curved 1x3 beams on 8' centers with a 22' radius connecting the 2nd
floor eave with the ground 14' to the south of the porch. My first
sunspace had a $50 32'x24' piece of cloudy 4-year polyethylene
greenhouse film in lieu of vinyl.
Alternatively, Terri could have a sunspace like my current version,
with a low-slope 40'x12' corrugated polycarbonate roof extending 16'
to the south of the 2nd floor eave 8' above the flat porch roof, which
connects to a 40'x16' vertical wall made with 20 $100 4'x8' flat 10
mil HP92 polycarbonate double-glazed panels gently inflated with
welding argon via tire valves. The roof and wall would collect
0.8x40'x16'(510+685) = 612K Btu/day and lose 6h(70-40)640ft^2/R2 =
58K, for a net gain of 554K. Twinwall endwalls would collect more. It
would be easy to add more insulation to the outside of the enclosed
existing house walls.
This would enclose the existing porch and add 8'x40' of enclosed deck
roof floorspace and enclose 8'x40' on the ground, which might include
a picnic table with an awning and a December tomato and herb and red
bell pepper garden and a patio over a heat store, which might also
supply heat to a hot tub.
The house needs 5dx538K = 2.7 million Btu for 5 cloudy 36.6 F December
days with about 97% solar house heating in December. The sunspace
could have 2.7M/(140-80)/62 = 720 ft^3 of water cooling from 140 to 80
F in a well-insulated 8'x16'x6'-tall tank with a $300 folded 20'x32'
EPDM liner, dug 6' into the ground.
Nick