You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/640814f7-ab6a-4876-a284-e8942a025aa6%40googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/cd999fa2-4e21-471b-b0a8-0077bb21db56%40googlegroups.com.
Hi Antonino,
Does this code any check on execution of a command?
The suggested way is a timeout for any command that has been send, if an incoming frame for that ID is not received within the timeout, the message is sent out again.
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/640814f7-ab6a-4876-a284-e8942a025aa6%40googlegroups.com.
At this moment the plugin does not do any check.
We will remember for next enhancements.
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPLH17F6sPpuZobtYQSue_fDPAi%3DL_iHSc9ZqP3t%2B-A_JQ%40mail.gmail.com.
Hi Juan,
The User and Node Index MUST be different for each user interface, so shall not be the same of SoulissApp.
Consider that SoulissApp define those two randomly based on the sim serial number.
The Node number is the actual number of nodes in your installation and not the maximum number set in MaCaco.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/bef38287-6875-486c-96fc-9e43823cd502%40googlegroups.com.
Ty Dario, I'll try later but the error on the app still here. I think that more configuration needed on sites folder.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPLKUyvJ-H5ZABEMyEQvj3s0ynvauRmWji_4BAwSFMCP_w%40mail.gmail.com.
I cannot help on the binding.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAN5yH6Gb4wZeU451FtxkyHtP3fztK3mAWrncv2rYbTJEX%3DhUkQ%40mail.gmail.com.
Have you tried on browser at link
http://YOUROHSERVER:8080/openhab.app?sitemap=YOURSITEMAPNAME
At the moment T12 isn't fully supported by OH. The binding provides only ON/OFF funcionality.
You can look at configuration file commands_OHtoSOULISS.properties, inside the jar file.
You can modify at line
#Typical 12 : ON/OFF Digital Output with AUTO mode
0x12_ON=0x02
0x12_OFF=0x04
You can change the ON or OFF value with 0x08, that is the auto command code.
Not tested.
Let me know.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/611bb580-63bc-42e9-9e12-e22975f21ef3%40googlegroups.com.
@Antonino and Fulvio,
Can openHAB be triggered remotly? I mean, using a frame from a node to start a sequence.
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/fa4f8603-2b69-4e97-9239-ad2c51d62f83%40googlegroups.com.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/7beaf6fd-9f76-460c-a7a1-e6ff0aa848db%40googlegroups.com.
Hi. Yes 255 is very good.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/7beaf6fd-9f76-460c-a7a1-e6ff0aa848db%40googlegroups.com.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/7beaf6fd-9f76-460c-a7a1-e6ff0aa848db%40googlegroups.com.
You want do this via openHAB or SoulissApp?
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/cd6a7019-aee6-4fe5-b499-f697ac679ee2%40googlegroups.com.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPLKX%3DgzWOEE0fO3CxjM1QsB0keR9Mz7u6WE6zN%3Du2t8WQ%40mail.gmail.com.
Is expected to go as fast as SoulissApp, please do test over long enough time to check if it stops.
Please use both OA and SoulissApp and check if both stops as per the problem that you have reported in the past.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAHuJBZGEZ0sP4AYrbRewB0jgXQ%2B2a%2B6Wi5E%2BKDnZbREts%3D1Xkw%40mail.gmail.com.
10:22:20.040 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_RS_CAVETTO = A0.53r|11:17|6.77681|0|2|10:22:21.700 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - INGRESSO_CAMINGRESSO = 36.8110:22:22.205 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_RS_PH = 6.7768110:22:22.358 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_MACLIST = assoclist 48:02:2A:42:93:4A10:22:22.368 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_MARCO = Assente10:22:22.385 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_ANTO = Assente10:22:22.773 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CALDAIA_TERMOSTATO = 010:22:23.535 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_TF_RABB = 010:22:23.808 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CALDAIA_SENSOREGAS = 010:22:24.708 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_TF_LIV = 110:22:24.872 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CAMERA_PWS_SVEGLIA = 010:22:25.841 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_RS_LIV = 110:22:25.932 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - INGRESSO_CURRENT_TEMP = 19.3110:22:26.980 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_RS_RABB = 010:22:26.983 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CALDAIA_CONTROLLO = 010:22:28.018 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CALDAIA_T_RITORNO = 25.0510:22:28.084 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - ACQUARI_TF_FAN = A0.53t|11:15|6.57391|0|2|10:22:28.237 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_MACLIST = assoclist 48:02:2A:42:93:4A10:22:28.242 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_MARCO = Assente10:22:28.244 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - PRESENZA_ANTO = Assente10:22:29.042 INFO o.o.b.s.i.SoulissBinding[:248]- receiveUpdate - CALDAIA_T_MANDATA = 23.94
Let's wait Antonino, he can help us on that problem.
Your OA isn't working as expected.
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/571fdb73-310b-498d-a4b4-4750d732c423%40googlegroups.com.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPKnrWVoq%3DGQfow0X7_7bYXW9vt-C8j5vkdww7VNGAWiBQ%40mail.gmail.com.
10:32:48.082 DEBUG o.o.b.s.i.n.t.StateTraslator[:28]- translate commands: OFF -> 0x0410:32:48.083 DEBUG o.o.b.s.i.n.u.SoulissCommGate[:47]- sendFORCEFrame - HEX: [33 00 00 03 01 04 ], soulissNodeIPAddress: 192.168.1.129, soulissNodeIPAddressOnLAN: 192.168.1.12910:32:48.084 DEBUG o.o.b.s.i.n.u.SendDispatcherThread[:40]- Push10:32:48.085 DEBUG o.o.b.s.i.n.u.SendDispatcherThread[:89]- Add frame: HEX: [0D 0C 17 81 00 86 47 33 00 00 03 01 04 ]10:32:48.131 DEBUG o.o.b.s.i.n.u.SendDispatcherThread[:126]- Pop frame HEX: [0D 0C 17 81 00 86 47 33 00 00 03 01 04 ] - Delay for 'SendDispatcherThread' setted to 100 mills.10:32:48.132 DEBUG o.o.b.s.i.n.u.SendDispatcherThread[:143]- SendDispatcherThread - Functional Code 0x33 - Packet: HEX: [0D 0C 17 81 00 86 47 33 00 00 03 01 04 ] - Elementi rimanenti in lista: 0
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/cd6a7019-aee6-4fe5-b499-f697ac679ee2%40googlegroups.com.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMLDvsd7G2u-0qbH71sgmo87XXVJ5fGAb00oWEiA7iSDHmn%3Dfg%40mail.gmail.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAHuJBZF_jXC%3DJ__fnj21dyg2vEthq_g%3DLEr8GRJKmGj0r4BGOw%40mail.gmail.com.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMP%2B34iSBTnMXb2aqHhSdkr3mGVRs7MKczT23DSHAwOD1Mw%40mail.gmail.com.
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMLDvsd1kBpjhg%2BohO4vSJ4cO3QkS6F4F7M0h5fT4AE-PBqeHw%40mail.gmail.com.
You can probably do this directly via openHAB because the binding get those values.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAHuJBZE-3_tOqVUBYF62AhuphpqvkaJBnpX-UUpf2COoY-j2tg%40mail.gmail.com.
@Fulvio, I cannot reduce the numebr of item in my OpenHab config, Half of my house (Heater, Lights, and Christmas Tree :)) ) depend from OpenHAB. Now Binding is working like expected, last night did only few test. Now we have an harder tester, my wife with Christmas Tree. I'll back with result.
@Dario, could we open a new forum into mysouliss.eu dedicate to OA Binding?
Regards
Marco
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/43b482c2-bf52-4853-bab6-0293b1da857a%40googlegroups.com.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMP%2Br5gX0qKhGsmNb8L%3D7Oej2JGBO4AK5a-ZxZ7sD_yPbwQ%40mail.gmail.com.
Great beta tester! Good luck!
Siamo lieti di aprire alla ML il progetto del binding Souliss per Openhab.In attesa di scrivere una wiki esauriente sull'argomento tenterò di dare qualche indicazione sul suo funzionamento.Per la configurazione del binding occorre eseguire qualche modifica ai file di configurazione di openhab. Al riguardo prevediamo di fornire prestissimo un piccolo software per l'autoconfigurazione.----We are pleased to open to ML the project of Souliss binding for Openhab .We going to write a exhaustive wiki, but just for now I will try to give some instructions. We hope to release soon a autoconfiguration software.For start you have to add some text to OH configuration files:1) .\openhab\configurations\openhab.cfgAggiungere in fondo - Add at the bottom:################################ Souliss Binding ############################################ Souliss## For ITEM defination in file .item#{souliss=<Typical>:<nodeID>:<slot>:[<bit>]}souliss:IP_WAN=192.168.1.105souliss:IP_LAN=192.168.1.105souliss:USER_INDEX=71souliss:NODE_INDEX=134#SERVERPORT - Leave empty for casual portsouliss:SERVERPORT=#time in millssouliss:REFRESH_DBSTRUCT_TIME=600000souliss:REFRESH_SUBSCRIPTION_TIME=120000souliss:REFRESH_HEALTY_TIME=60000souliss:REFRESH_MONITOR_TIME=500souliss:SEND_DELAY=1500souliss:SEND_MIN_DELAY=100souliss:NODE_NUMBERS=4###########################################################################################SARA' NECESSARIO PERSONALIZZARE SOLTANTO - You need to change only:-IP_WAN-IP_LAN-NODE_NUMBER2) .\openhab\configurations\items\defaultSitemap.itemsdefinire i propri items ed aggiungere alla fine di ogni riga di definizione - define your items and add to the end of each line of definition{souliss=<Typical>:<nodeID>:<slot>:[<bit>]}dove TYPICAL ha la forma: T11, T12, T13, T16, T1A, T22, T51, T52, T53, T57, D98, D99 (questi per il momento sono i tipici supportati) (for the moment these are the typical supported)-nodeID e slot hanno il significato che l'utente Souliss ormai conosce bene.-bit è utilizzato per il tipico T1A (riceve un byte in ingresso, ed il bit indicato definisce il valore ON/OFF oppure OPEN/CLOSE dell'item)ES:Switch LuceSogg "LuceSogg" (GF_Soggiorno, TechnicView_Node0) {souliss="T11:0:6", autoupdate=false}Number Temperature_GF_Soggiorno "Temperatura Soggiorno [%.1f °C]" <temperature> (temperature, GF_Temperature, TechnicView_Node0) {souliss="T52:0:0", autoupdate=false}Number Umidita_GF_Soggiorno "Umidità Soggiorno [%.1f %%]" <temperature> (temperature, GF_Temperature, TechnicView_Node0) {souliss="T53:0:2", autoupdate=false}Number Consumo_GF_Soggiorno "Consumo [%.1f W]" <energy> (GF_Temperature, TechnicView_Node0) {souliss="T57:0:4", autoupdate=false}Rollershutter Shutter1_GF_Soggiorno "Tenda1" (GF_Soggiorno, TechnicView_Node3 {souliss="T22:3:0", autoupdate=false}Contact ContattoTest "Contatto" (GF_Soggiorno, Lights) {souliss="T13:0:1", autoupdate=true}Contact C2 "BIT 3" (GF_Soggiorno, TechnicView_Node3) {souliss="T1A:3:5:2"}Contact C3 "BIT 4" (GF_Soggiorno, TechnicView_Node3) {souliss="T1A:3:5:3"}Color RGB_Led_Strip_1 "RGB Led Strip 1" <slider> (GF_Soggiorno) {souliss="T16:0:2", autoupdate=false}TIPICI DI SERVIZIO - SERVICE TYPICALSAbbiamo introdotto due tipici di servizio - We introduced two service typicals: D98 (Health) e D99 (Timestamp), definiti in questo modo{souliss="D98:<nodeNumber>:998"}{souliss="D99:<nodeNumber>:999"}ES:Number HEALTNodo1_GF_Servizio "Health Nodo 1 [%1d]" <keyring> (Diagnostic, TechnicView_Node0) {souliss="D98:0:998"}String TIMESTAMP_Nodo1_GF_Servizio "Timestamp Nodo 1 [%1$td.%1$tm.%1$tY %1$tk:%1$tM:%1$tS]" <keyring> (Diagnostic, TechnicView_Node0) {souliss="D99:0:999"}3) Aggiungere il fileorg.openhab.binding.souliss_1.5.0.201411250242.jar nella cartella .\openhab\addonsAdd attached file in directory .\openhab\addons4) Riavviare OH - Restart OHNota: contrariamente a quanto annunciato qui (post Binding vNet/MaCaco per openHAB) in questa prima versione il binding non comunica direttamente coi nodi ma si serve, così come SoulissApp del Gateway di Souliss.Siamo a disposizione per chiarimenti, segnalazioni di bug, proposte e suggerimenti.In this first version the native binding does not communicate directly with nodes but it need to communicate with souliss gateway (how does SoulissApp).
We are available for questions , bug reports , proposals and suggestions.
Tonino
Match it with T22.
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/b812fb78-dc67-4832-a343-d06308be4b5b%40googlegroups.com.
Can you test using T22?
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
OK,
I will update my code to T22.
BTW
I noticed that operating from OH (in my case is the native Android app) is slower than SoulissApp.
For slow I mean that turning on the light you wait from 1/2 sec to 5 seconds to see the light on.
The lag increase even more when tapping fast on more than a control (e.g. to turn on more than a light quickly)
I did not have the time to test if it could be related to the limited calculation power of the RaspberryPI.
Do you experience the same ?
Thanks,
Gab
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/3ab07981-356c-4a68-be2e-0b307df31d78%40googlegroups.com.
Gabriele you don't need to update your boards, just declare your t21 as t22 in openHAB.
Dario.
From Mobile.
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMpKdYTdYrRfGBKkN0eOnbiBObg_WES%3DcAz6VdqaJRX%3DATAX_w%40mail.gmail.com.
BTW
I noticed that operating from OH (in my case is the native Android app) is slower than SoulissApp.
For slow I mean that turning on the light you wait from 1/2 sec to 5 seconds to see the light on.
The lag increase even more when tapping fast on more than a control (e.g. to turn on more than a light quickly)I did not have the time to test if it could be related to the limited calculation power of the RaspberryPI.
Do you experience the same ?
Hi Gabriele,
Have a try and run it on a PC, you just have to the change the node and vnet index. This will give you three interfaces running at same time to have a performance comparison.
Regards,
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/6e2dea4d-60df-45f4-be2b-d5b8534adce3%40googlegroups.com.
The lag increase even more when tapping fast on more than a control (e.g. to turn on more than a light quickly
Ciao Dario,
I've done this...
The rolleshutter does not move.
Gab
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPKJyC7FvAwZNwCpT6uYmtMd0OeAzsV%2BSd%2BUzkmbX8FoWQ%40mail.gmail.com.
@Antonino,
Could you please highlight the code changes to get this queue mechanism?
It would be nice import those changes back in SoulissApp.
Regards,
Dario.
From Mobile.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/73458bce-b2b1-4c5c-978e-9042e5fd9ea6%40googlegroups.com.
Ok,
I will investigate.
Thanks
Gabriele
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/6e2dea4d-60df-45f4-be2b-d5b8534adce3%40googlegroups.com.
Ok.
@Antonino, as far as I can remember add typicals require only to update s text file without compile it.
Could you please explain how to add the T21 starting from the T22? So that we can use that description even for the wiki.
@Fulvio,
There is a starting page on the wiki, could you please check if is ok?
Thanks,
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMpKdYTjCYnED277TyHBjbRPF_tzCSKrnJN6JJZss_xgn%3DmKEQ%40mail.gmail.com.
I have OA in raspberry too, it is true, is very slowly,specially at the startup, OA take about 2 minutes, and for example don't load gcal binding, i must investigate....
I've never overclock , but i can try, i think i must change so with a distro lighter than raspbian.
OA on a pc is more responsive but, one pc power on h24 is much expansive....
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/6e2dea4d-60df-45f4-be2b-d5b8534adce3%40googlegroups.com.
No one has tried a Beagle Bone?
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMLDvsf4JZta5LQ-wC_u_g3Z_xm3tGye6-UMPgmmXZhmMaTkmQ%40mail.gmail.com.
I have aone beaglebone and one beagleboard.
But i've never tried....I can try....
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPKue_g3OgRFSVnBM-YqCTY7FSt%3DjSO5Pt1-BTcGHociHQ%40mail.gmail.com.
Also I have OA in Raspberry pi with Raspian. It is slowly at startup and sometime (rarely) sleep for some seconds.
I tried with raspbmc and it is not usable, must slow.
Now I use OH on raspian distribution, with 4 nodes: 3 T22 curtains, 5 T11 switch , 2 DHT22 (temp+humidity), 1 power mesurement, 1 RGB T16, 1 dimmer led T19, 1 T1A (casually updated every 10 seconds), and it work good and responsive.
In effect, when I tested it with T1A updated every 3 second, it become dramatically slowly.
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMLDvsf4JZta5LQ-wC_u_g3Z_xm3tGye6-UMPgmmXZhmMaTkmQ%40mail.gmail.com.
In effect, when I tested it with T1A updated every 3 second, it become dramatically slowly.
Remember that the T1A fires up to 8 updates at same time. In my log i find true "update storms" :-)
f
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/709ef33f-e7e8-4c75-a631-a3d2f895a1a8%40googlegroups.com.
Dario,
why it should be different ?
To me garage doors and windows should work the same.
Do you mind if I try to add toggle to T22 logics ?
Gab
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPLe1HuCFm5egzOWEUBQDkNPzFX50boabjig6sF16yEoJw%40mail.gmail.com.
The main difference is that you just fully open or close with T21, rather T22 allow middle position.
If you need it, build a T22bis with all modification that fits for you.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMpKdYRsOw5xcHYGRdv55E7akv%2B2mpOvTwYRoEqz6C%3DMQMyJ2g%40mail.gmail.com.
It can be an option. You can push your working code on Git using a new branch, then I will merge it.
Regards,
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/0058c735-c9a6-4044-8d66-cf0b521ac08f%40googlegroups.com.
--
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/9968bdbf-5054-4f0a-b6a6-9dcf54b5f42d%40googlegroups.com.
Hi Gabriele,
1) An easy way suggested by Fulvio is add in your sketch somenthing like:
if(ssDigIn(pin, Toggle, 0))
{
if(Souliss_Output(memory_map, slot) == Close || == Closing || == LimitSwitchClse)
SoulissInput(,)= OpenCmd;
similar for Open
}
You should not care for the stop, is done in the typical's code.
2) Is a bug, it should compare with the costant value (that is the default delay time) but with the value from the header of the function.
Can you fix it and push the code on a dedicated branch?
Thanks,
Dario.
From Mobile.
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMpKdYQwSk2bbx6SQ1FLpqPKERf-G4FX9AcUEcxen2HC9SHu2w%40mail.gmail.com.
Googling doesn't give an answer, if you have yet an HDMI stick you can have a try and let us know the result.
This link can give some information
https://github.com/openhab/openhab/wiki/Hardware-FAQ
Dario.
From Mobile.
First off all hanks Antonino for the work, even for me, without any previous Openhab experience I got it up and running in a weakened. Now I starting to learn possibilities of Openhab and I love it more and more thanks that You made it possible.Now I considering on what to run it permanently. RPi is an option, but as mentioned previous it is a bit sluggish. Does someone tried to run Openhab on one of those Android PC sticks like MK808 with Linux image? Compared to Rpi it has more "juice" 1.6GHz dual-core, 1GB RAM, Wifi, Bluetooth and it can easily be plugged in monitor without any additional wires (except power).
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/ba664a4c-1e14-4084-b5f3-9d03d660b101%40googlegroups.com.
First off all hanks Antonino for the work, even for me, without any previous Openhab experience I got it up and running in a weakened. Now I starting to learn possibilities of Openhab and I love it more and more thanks that You made it possible.Now I considering on what to run it permanently. RPi is an option, but as mentioned previous it is a bit sluggish. Does someone tried to run Openhab on one of those Android PC sticks like MK808 with Linux image? Compared to Rpi it has more "juice" 1.6GHz dual-core, 1GB RAM, Wifi, Bluetooth and it can easily be plugged in monitor without any additional wires (except power).
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/ba664a4c-1e14-4084-b5f3-9d03d660b101%40googlegroups.com.
A raw value is given by the max W from the power supply. I guess 100 W.
Dario.
From Mobile.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAMLDvsfvS%2BzmyKU_s3o224NrDu_ZkRXmDs90pR58OCw-eNHUXQ%40mail.gmail.com.
I've a MK802IV with Android, it works as media center streaming from a network drive.
I haven't a Linux distro to test it out and generally I don't know if those are well supported.
Antonino has one of this also, but also in his case with Android.
Dario.
From Mobile.
At this point I do not own one of those Mini Android Pc's or RPI. Just considering what to buy for OH server. As Dario says goggling does not seem to say anything about that, and I am suprised about that, can not believe that anyone tried it. Will look at Fulvio's suggestion about java, but real test probably would be better than that. So if anyone has stick Pc please feel free to test and let us now.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/5e2e4165-0468-47d8-89a4-245059cc77ea%40googlegroups.com.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/4133adc3-6941-45aa-8efd-176090052d55%40googlegroups.com.
Linux support for USB pc's is relativly new, but some of them now ships with blinux. I will do more googling later, there should be someone who has tried rhis.
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPKjwF4Pkoia0DZEGdtWcpSMeGefX%2BUrtDL%3D1fmMN8kq1A%40mail.gmail.com.
Send him an email or an hangout, is on G+ :)
Dario.
From Mobile.
Finally found some people maetioned it can run OH, and here is also one tutorial how to get it up and runnig http://projectsbymartin.blogspot.com/2013/12/installing-openhab-on-android-tv-stick.htmlsadly nothing mentioned about performance.
--
You received this message because you are subscribed to the Google Groups "souliss" group.
To unsubscribe from this group and stop receiving emails from it, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/19ac3399-b75a-4a1e-9695-f433e071343e%40googlegroups.com.
At this moment I use Raspberry Pi with raspian.
It work well and fast with basic configuration without persistence macro and rules.
I have to do some test for persistence and graph.
My notes: http://www.xorse.it/raspberry-installare-openhab.html
You received this message because you are subscribed to a topic in the Google Groups "souliss" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/souliss/eU6XF8Ebwc4/unsubscribe.
To unsubscribe from this group and all its topics, send an email to souliss+u...@googlegroups.com.
To post to this group, send email to sou...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/souliss/CAKGhMPKjwF4Pkoia0DZEGdtWcpSMeGefX%2BUrtDL%3D1fmMN8kq1A%40mail.gmail.com.