It seems that this meter has almost the same scripting commands as SDM530. I am using the following script and it seems to be ok (I have just connect the 1st phase for testing):
>D
>B
->sensor53 r
>M 1
+1,3,M,0,9600,MODBUS,1,1,2A040000,2A040002,2A040004,2A040008,2A04000A,2A04000C,2A040010,2A040012,2A040014,2A040016,2A040018,2A04001A,2A04001C,2A04001E,2A04002A,2A04002C,2A04002E,2A040036,2A040100,2A040400
1,2A0404ffffffff@i0:1,Voltage P1,V,Voltage_P1,2
1,2A0404ffffffff@i1:1,Voltage P2,V,Voltage_P2,2
1,2A0404ffffffff@i2:1,Voltage P3,V,Voltage_P3,2
1,2A0404ffffffff@i3:1,Current P1,A,Current_P1,2
1,2A0404ffffffff@i4:1,Current P2,A,Current_P2,2
1,2A0404ffffffff@i5:1,Current P3,A,Current_P3,2
1,2A0404ffffffff@i6:1,Total Active Power,KWh,Total_Power,2
1,2A0404ffffffff@i7:1,Active Power P1,KWh,Power_P1,2
1,2A0404ffffffff@i8:1,Active Power P2,KWh,Power_P2,2
1,2A0404ffffffff@i9:1,Active Power P3,KWh,Power_P3,2
1,2A0404ffffffff@i10:1,Total Reactive Power,KWh,Total_Reactive_Power,2
1,2A0404ffffffff@i11:1,Reactive Power P1,Var,Reactive_Power_P1,2
1,2A0404ffffffff@i12:1,Reactive Power P2,Var,Reactive_Power_P2,2
1,2A0404ffffffff@i13:1,Reactive Power P3,Var,Reactive_Power_P3,2
1,2A0404ffffffff@i14:1,Power Factor P1,,Power_Factor_P1,2
1,2A0404ffffffff@i15:1,Power Factor P2,,Power_Factor_P2,2
1,2A0404ffffffff@i16:1,Power Factor P3,,Power_Factor_P2,2
1,2A0404ffffffff@i17:1,Frequency,Hz,Frequency,2
1,2A0404ffffffff@i18:1,Total Active Elec Power,KWh,Total_Elec_Power,2
1,2A0404ffffffff@i19:1,Total Reactive Elect Power,KWh,Total_Reactive_Elec_Power,2
#
Please note that my meter modbus address is 42 which in hex is 2A.
I am getting the readings except for the following 2:
- All power factor readings are 0. Perhaps I need to connect all phases and the load.
- There is no last line for "total reactive electric power".
I have compiled the firmware with SML_MAX_VARS=24 and SML_BSI=54 but I still don't get the last line.
Thanks