Quote: |
Quote: |
Akshay, Whatever you are suggesting is absolutely right for the structure in which weight of vessel is less than 25% seismic weight of structure. But the structure i am considering is having different configuration. About structural configuration - It has 16m x 16m table top (Slab thickness - 3m) supported on 12 columns. Height of the table top is 8.3m It supports 13m dia vessel (height of vessel is 40m) which has 25000 kN (2500 ton) weight. But weight of the table top is 15000 kN only. Our interpretation - Due to this structural configuration and loading mode shapes will be governed by vessel only. This is very similar to vessel supported on rigid support / ground (Table top will be very rigid and will have very less time period) In this case mass will be concentrated on table top and vessel will be vibrating as cantilever fixed at table top. Hence lumping of mass at CG will not be justified. At the same time, if we lump the mass at the table top, then it will lead to wrong time period estimation. Hence we have found out time period of combined system and fixed the seismic force percentage and followed the procedure given in my query on 7th August. Query - Based on this, can you suggest me whether i should go with the seismic force given by vessel group or i should go with lumping the mass at CG / table top. (In the first case, again question arises about whether we should use their forces as it is or we should factor them by appropriate factor to take care of R) |