ASCE 7 Wind Loads on Bare Steel Framing - Opinions Wanted

506 views
Skip to first unread message

bi...@polhemus.cc

unread,
Mar 4, 2009, 9:07:38 AM3/4/09
to sea...@seaint.org

Lots of pipe racks to look at. Very fascinating.

(P.S. Not really).

Years ago when the ASCE 7 standard was focused almost exclusively on building structures, we used to have rules of thumb for applying wind loads to these kinds of "lattice" structures like pipe racks and large structural steel bare frames. There were all sorts of arguments about "shielding" of one member from another, for example.

ASCE published a guideline back in the 90s ("Wind Loads and Anchor Bolt Design for Petrochemical Facilities") to help establish some consensus regarding how to apply loads to these structures. It was based on the state of the art at that time - ASCE 7-93 or -95 IIRC - which of course has changed quite a bit since then.

ASCE 7-05 was significant in that it added quite a few commonly-seen but previously unaddressed systems, like canopy roofs and braced steel towers, to the provisions for calculating wind loads. But there are still some questions in my mind at least.

It seems easy enough to apply provisions for "Open Signs and Lattice Frameworks" (ASCE 7-05 Fig. 6-22) and "Trussed Towers" (Fig. 6-23), for example, but it is NOT obvious that these are correct.

It seems to me that a colleague and I did a comparison with the ASCE "Petrochemical Facilities" publication procedure, and ASCE 7-05 using Fig. 6-22, and it came pretty darn close. I have been a proponent of going with ASCE 7-05 but I have "older" colleagues who don't much like change, and insist that since the older ASCE "Petrochemical Facilities" publication was good enough "then," it should be good enough now.

Opinions?

Conrad Harrison

unread,
Mar 4, 2009, 11:22:03 PM3/4/09
to sea...@seaint.org
Bill,

From the commentary to ASCE7-05, apparently AS1170.2 is one of the sources
of coefficients for canopies: from what I can tell those coefficients have
been in AS1170.2 since the 1970's: so some history of being reasonable.
AS1170.2 also includes drag coefficients for airflow over corrugated and
ribbed cladding for walls and roofs. I cannot seem to find equivalent in
ASCE7-05.

As for open frames AS1170.2 contains drag force coefficients for various
structual sections: I-beams, channels, etc. The code also permits shielding,
but when the wind is at 45 degrees to the orthogonal axes of the structure
little shielding is available for simple rectangular frames (eg. carport, or
building frames during construction).

I cannot find similar coefficients in ASCE7-05, it seems to be focused on
the section of the chimney, or tower. It seems to me such approach may under
estimate the forces on the individual framing elements.

Drag forces on individual elements or whole frames can be high. I've seen a
photo of 6 gable frames (in the UK), they were left over the weekend:
Monday morning they were all folded to the ground about the I-beam weak
axis. (The beams looked fairly large about 610mm deep, possibly bigger.)

If I could find the picture again it would be good to show the builders who
keep telling me: for 30 years they've never had a problem so why should they
prop and brace the frames during construction.

As for which code to use. I prefer at least two approaches where possible.
Older codes hopefully provide calibration for newer codes. If the older code
produces more conservative results go with the older code: at least the
older code is tried and tested in the field. Often reduction in newer codes
are a consequence of missing out important constraints and conditions, which
are later reinstated. If newer code more conservative go with that.

Otherwise it's a risk management issue, if there is no mandated legal
requirement to use one code or the other. If older code easier to use, and
faster, and more expertise available to check its application, then the
older code may be the better choice. Possibly incorporate additional design
factor of ignorance to allow for what don't know about the new code.

It also depends on the critical factor. In Australia wind loading in
AS1170.2 is ultimate strength. Separate codes for cranes, antennas, power
poles, and industrial racking define serviceability requirements. The wind
loads in these codes seem low, but when the deflection limits imposed are
taken into account the ultimate strength of the structure can end up much
greater, than if we started the design with ultimate strength load: but not
always the case. Since 2002, AS1170.2 has permitted the calculation of basic
wind speed for any return period or annual probablity of exceedance. I
expect the more specialised codes to remove their low design wind speeds,
which tend to be seen as non-compliance with AS1170.2 and replace with
probability requirements. Thus achieving inceased consistency.

The way I see it, in similar manner to AS1170.2, ASCE7-05 is becoming a
single point reference for all loading requirements: the expected reference
to be used by all structural engineers. The market for engineering services
is variable, an engineer who can only use simplifications in IBC, would take
time to get upto speed when building market drops and industrial market
expands. If only use the one code than already upto speed. Also the market
place for engineering services is becoming more international, and ASCE7-05
is more aligned with the ISO guidelines: thus AS1170.2 and ASCE7-05 are
similar but not equal. Thus industrial/petrochemical structures designed to
ASCE7-05 in the USA and imported into Australia likely to be found compliant
with AS1170.2, those designed to UBC/IBC: more likely to be rejected or
involve extensive recalculation before accepted.

So whilst have the experience available for the older code and experience of
acceptable design-solutions, run with the new code (ASCE7-05), check and
calibrate design-solutions against the old code (ASCE Petrochemical
facilities), and where necessary set company policy and design procedure:
assuming resources permit. Thus eventually move over to ASCE7-05 and be
better placed internationally.

Just a few thoughts for consideration.

Regards
Conrad Harrison
B.Tech (mfg & mech), MIIE, gradTIEAust
mailto:sch.te...@bigpond.com
Adelaide
South Australia


******* ****** ******* ******** ******* ******* ******* ***
* Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
* This email was sent to you via Structural Engineers
* Association of Southern California (SEAOSC) server. To
* subscribe (no fee) or UnSubscribe, please go to:
*
* http://www.seaint.org/sealist1.asp
*
* Questions to seai...@seaint.org. Remember, any email you
* send to the list is public domain and may be re-posted
* without your permission. Make sure you visit our web
* site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********

Harold Sprague

unread,
Mar 5, 2009, 2:03:03 AM3/5/09
to sea...@seaint.org
The drag coefficients developed in the ASCE Wind Loads and Anchor Bolt Design for Petrochemical Facilities should still be valid.  However there have been many advances in wind pressure development including the wind velocities.  In the ideal world, we would have an updated version of the ASCE Wind Loads and Anchor Bolt Design for Petrochemical Facilities.  However, we are not there yet.  I would opt for a blend. 
 
Remind your colleague about the difference in the fastest mile vs. the 3 second gust change that happened with the ASCE 7-95. 

Regards, Harold Sprague


 

From: bi...@polhemus.cc
To: sea...@seaint.org
Subject: ASCE 7 Wind Loads on Bare Steel Framing - Opinions Wanted
Date: Wed, 4 Mar 2009 09:07:38 -0500

Windows Live™ Contacts: Organize your contact list. Check it out.

Gary L. Hodgson and Assoc.

unread,
Mar 5, 2009, 7:56:19 AM3/5/09
to sea...@seaint.org
A lot of wind load studies came out of the University of Western Ontario
doing wind tunnel tests on models of structures, under Dr Davenport in
the 60's thru 70's. Others also were doing similar tests elsewhere, but
I think Davenport was one of the first. All of these tests have been
reflected in the codes along with results from testing in actual
structures. This does not help but gives a little perspective.
Gary

******* ****** ******* ******** ******* ******* ******* ***

Bill Polhemus

unread,
Mar 5, 2009, 10:22:25 AM3/5/09
to <seaint@seaint.org>
I personally think all this stuff should be in ASCE 7 and Commentary. Harold, don't you still do a lot of industrial stuff? Are you currently on ASCE 7 committee? Should I volunteer?

William L. Polhemus, Jr. P.E.
Via iPhone 3G

Harold Sprague

unread,
Mar 6, 2009, 2:18:49 AM3/6/09
to sea...@seaint.org
Bill,
Yes.  I do a lot of industrial stuff.  I serve on several committees including the Seismic Task Committee of ASCE 7.  I would like to see more in the commentary especially when it comes to industrial structures. 
 
I would encourage anyone that wishes to contribute to do so. 

Regards, Harold Sprague


 

From: bi...@polhemus.cc
To: sea...@seaint.org
Subject: Re: ASCE 7 Wind Loads on Bare Steel Framing - Opinions Wanted
Date: Thu, 5 Mar 2009 09:22:25 -0600

Express your personality in color! Preview and select themes for Hotmail®. See how.

Jim Getaz

unread,
Mar 6, 2009, 9:35:48 AM3/6/09
to sea...@seaint.org

        Bill,

                Anyone that has his companys support to contribute a lot all at once or less, but over a period of years should volunteer. Its tough to contribute for long enough to really help when times like these occur. Companies scale back unessential activities.

                More power to you and all that are at work on those committees.

        Jim Getaz