250 microns is about right for the mineral oils.. I am not sure about
PAG oils, but I have heard that PAG is much more volatile..
Deep vacuum will not screw up mineral oils, you can pump for
days, and only boil out a teaspoonfull or less, which contaminates
your vac pump oil, and this self limits the vac to 250 microns.
--ghg
The POEs are less volatile than most mineral oils. As example, during
processing (manufacture) the final vacuum drying step uses high vacumm at
temperatures up to 400 deg. F. The vapor pressure is so low at 100 def. F.
that it is essentially not measurable. We often measure vapor pressure at 400
deg. F. as low as .0001 mm hg. Generally, the higher the viscosity of the
POE, the lower the vapor pressure. Thus and ISO Viscosity Grade 68 has a
lower vapor pressure (less volatile) than an ISO VG 22. Also, most
manufactures use a small amount of inhibitor to prevent oxidation in handling.
In fact, POEs can be used as vacuum pump oils provided they contain inhibitors
A note to others who have responded: POE is polyol ester, PAG is
polyalkyleneglycol. POEs have much less affinity to moisture than PAGs
Glenn Short ASHRAE TC 3.4 (lubricants) Chairman