Equipment Over-Voltage

0 views
Skip to first unread message

rowb...@666telusplanet.net

unread,
Apr 3, 1999, 3:00:00 AM4/3/99
to
xrAl6H),0*]Q~0:e}1o27s"oP

Earlier I had posted a question about operating with a ground fault on a
system where the capacitance and inductance vectorially added up to a
value that would cause ringing.

I suggested that it should be possible to calculate the values of
capacitance and Induction so that the system characteristics would not add
vectorially to a magnitude that would cause problems for the system..

We did a calculation and it appears that under the circumstances of a
phase to ground fault the voltage that would appear upon the system would
be 7.8 kV for a 4.16kV system.

Now while this may be acceptable for a small duration of time, I am not
certain of the consequences of impressing this over voltage upon a system
where the first phase to ground fault may stay on the system for a matter
of weeks... What would happen to a motor if it had that magnitude of over
voltage impressed upon it for a week or two?

Thanks again, gentlemen.

HR.
--
wotthehell wotthehell archie wotthehell wotthehell
(remove the devilish trio before responding.)