On Fri, 16 Jan 2015 22:50:01 -0600, Martin Eastburn
<
lion...@consolidated.net> wrote:
>On 1/16/2015 11:59 AM, Cydrome Leader wrote:
>> I'm going to be setting up shop of sorts in a commercial space with some
>> dodgy electrical service that's been tinkered with over the years. It has
>> 208 volt 3 phase, which I wish to extend into my space.
>>
>> There should be a A, B and C legs, but how is this order determined by
>> testing? I've not seen any electricians carry around an oscilloscope, so
>> there has to be an simpler way. Grab a small 3 phase motor and put
>> alligator clips on it and fuss around until it spins in the right
>> direction?
>>
>If you are concerned with rotation issue - just swap two and it reverses.
>
>There might be a 'wild' leg, might not. Put wild on lights and heaters...
>
>Use the two good and a wild for real 3 phase. If you put a computer
>on a wild phase you can have issues...
>
>Martin - 377 three phase in shop from my 208 single phase.
Sure. And just in case you've scared the fire department, maybe here's how to tidy things up to standard per code:
"The high leg service conductor of a 4-wire, 3-phase, delta connected service must be permanently marked orange or identified by other effective means [NEC Article 230-56], and must terminate according to the following: meter termination: ANSI requires termination on the C phase; panelboard and switchboard termination on the B or center phase [NEC Article 384-3(f)]. "