http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
There's many such ratings and you'll have to determine what you want.
Google for "fusing current" to find one extreme.
Actual current in an application depends on ambient temperature,
conduit and another conductors in the conduit, wire insulation,
insulation type, desired life of insulation, etc.
If the wire is wound into coils (like for a motor or resistor or
inductor) then geometry becomes crucial.
1.5sq mm wire seems to be about like 22 gauge which is sometimes
optimistically rated for 5 amps (it will be getting warm at that
current).
Tim.
As Tim says,there are many ratings for any given cable - see section 4
of
http://www.kevinboone.com/cableselection_web.html.
However for a rule of thumb in domestic installation, cables burried in
plaster or clipped to joists and not covered by insulation 1.0sq is
rated at 15amps, 1.5sq at 20 amps and 2.5 at 27 amps.
Standard radial circuits usually fuse 1.0 at 5 or 6amps ,1.5 at 10 or
15 amps and 2.5 at 20amps. Ring circuits in 2.5 are usually fused at
30amps.
Contrary to Tim's post 1.5sq is a litttle larger than 16swg.
Also, in the case of an extension cable, beware of max length
due to earth fault loop impedance. In the case of an extension
cable fused at 13A, that is 15m for 1.5 mm² and 25m for 2.5 mm².
Any longer than these values and you need to ensure the cable
is protected by an RCD, or reduce the value of the fuse
protecting the cable proportionally below 13A.
--
Andrew Gabriel
And the larger sizes of cable won't go in a 13A plug anyway (unless you
terminate the sheath short of the plug, a naughty wicked sinful and
depraved technique used only by hacksaw-wielding plantpots and building
site electricians).
Owain
Possibly -- it depends on a lot of things.
Also, quite apart from the earthing problems with long cables,
you might be dropping a significant proportion of the mains
voltage across the cable when the mower is running. Most electric
mowers use cheap universal motors which won't mind this too much,
but better quality mowers use induction motors, which don't like
running at reduced voltage on-load (could overheat).
> I used a properly sealed connector to "puddle-proof" the joint between
> the cables (I can't remember the IP rating of the connector, but it was
> suitable for regular immersion to a couple of metres, but not for
> diving with. I'd have to cultivate an ROV technician to obtain higher
> ratings. Which could be done.). The cost of a 30 or 50m reel of mains
> flex at B+Q was considerably higher (as in, times several) than the
> cost of 2 X 15m extension leads.
Yep -- you would do better at an electrical wholesaler for that.
(Conversely, they'll charge much more for the extension leads;-).
> The risk is what? That in the event of a fault at the remote
> socket, current travelling back down the earth line will raise the
> potential of the remote end of the earth (Ohms Law), which leaves the
> person at the remote end holding something live while standing in a
> puddle?
Yes. Also the resistance of the long conductors will reduce the
fault current which flows so it takes significantly longer to
blow the fuse (or in really bad cases, might not blow the fuse
at all).
> 90% of the time I remember to plug the extension lead into an
> RCD through-plug before I take the lawn mower out of the cellar. Maybe
> I'd better tie-wrap or gaffer-tape the extension lead and RCD together
> to make it 100% (including when the wife/ daughter does the lawn while
> I'm away).
Yes.
Better still, mount an RCD-protected socket outside, so you are
always going to use an RCD protected supply outdoors. (I would
suggest using a separate RCD and socket, with the RCD mounted
inside in the dry, and a plain waterproof socket outdoors. That
way, if moisture does get into the outdoor part which it often
does eventually, you don't also write off an expensive outdoor
RCD socket.)
--
Andrew Gabriel
> Also, quite apart from the earthing problems with long cables,
But in the lawnmower context, (a) the mower will almost certainly be a
Class 2 (double insulated) appliance so it won't rely on earthing, and
its metal frame won't rise in voltage relative to the ground during a an
earth fault should you mow through the 3-core cable: (b) the extension
lead should be plugged into an RCD-protected socket, so the earth fault
loop impedance issue becomes largely irrelevant, provided that the earth
isn't completely o/c. If the house electrical installation is old and
doesn't have RCD-protected sockets then use an plug-in RCD adaptor, as
Andrew said.
> you might be dropping a significant proportion of the mains
> voltage across the cable when the mower is running. Most electric
> mowers use cheap universal motors which won't mind this too much,
> but better quality mowers use induction motors, which don't like
> running at reduced voltage on-load (could overheat).
We don't know what cable size was used - but 30 m of 1.0 mm^2 flex will
only be just over 1 ohm and I can't see that causing too much in the way
of problems. In 0.75 mm^2 though things will be getting rather marginal.
--
Andy