In article <ubdr64$2duqe$
1...@dont-email.me>,
Jerry Peters <je...@example.invalid> wrote:
> In theory, the Neutral and the Ground should be at equal potential -
>thereby avoiding false trips - as that is what the GF device is looking
>for - current going to Ground (or somewhere), not Neutral. If the Ground
>and Neutral are not at equal potential - there may be something for the
>GF device to detect.
That's almost exactly backwards, in practice.
When the system is in use (that is, when the Hot line is drawing
current), the Neutral and Ground wires are at the same potential
*ONLY* at points where they are actually bonded together - that is, at
the panel or sub-panel or transformer.
At other points (for example, at the outlet) they won't be at the same
potential. They can't be, because the neutral wire is carrying
current and has non-zero resistance, and thus has a significant
voltage drop between the outlet and the panel. The protective-ground
wire won't be carrying current, and thus has no voltage drop between
the outlet and the panel.
So, if a GFI considered "ground and neutral wires are not at equal
potential" to be a fault condition, it would trip every time somebody
turned on a light or appliance.
If you want to see this demonstrated, it's not difficult to do, if
you have an AC voltmeter with properly-shrouded insulated test leads.
Using one half of a standard outlet, measure the voltage between the
neutral and ground contacts. If nothing on that circuit is drawing
current, it should read 0 volts, or within noise-factor of that.
Then, plug a 15-amp space heater into the other half of that outlet,
and turn it on. You'll almost certainly see a significant voltage
develop between ground and neutral, caused by the current flowing
from the outlet back to the panel through the neutral wire. I'd
expect something on the order of a volt or so to show up on
the meter.
If you don't see a voltage drop between ground and neutral under
these conditions, it may very well mean that your outlet is
mis-wired, and has ground and neutral connected together at
the outlet... which is a definite no-no.