On Sat, 25 Oct 2014 12:50:52 +0300,
upsid...@downunder.com wrote:
>On Fri, 24 Oct 2014 17:41:43 -0700 (PDT), Phil Allison
><
palli...@gmail.com> wrote:
>
>>
upsid...@downunder.com wrote:
>>
>>>
>>> This applies both to 120/240 V antiphase feeds in the US as well as to
>>> three phase 230/400 V systems in the rest of the world.
>>>
>>> The principal idea in both systems is that with _balanced_ loads, the
>>> neutral wire current cancels and the neutral wire potential is the
>>> same as the ground electrode potential all over the place.
>>
>> ** No one who is not insane ever assumes that nonsense to be the case.
>>
>>Neutral current is assumed to be either the same or somewhat more than the maximum current in one phase. Max voltage drops along cables can be computed from this.
>>
>>
>>> Assume an apartment building with two stairs with separate feeders
>>> along the stairs. There are going to be unequal voltage drops in the
>>> phase as well as neutral conductor at both stairs.
>>>
>>> At some higher floor, measure the mains neutral/ground connector
>>> potential against the potential of the same floor of the adjacent
>>> stairs. With absolutely equal and symmetrical load, the neutral/ground
>>> potential would be equal.
>>>
>>> In practice, this is not the case. Connect an unisolated RS-232 or
>>> USB cable between the stairs and the shields might quite well be 1-5
>>> Vrms at different potential.
>>
>>** What halluncinary drugs are you on today ??
>>
>> No-one connects signal grounds to the damn NEUTRAL !!!
>>
>> Doing that would be CRIMINAL !!
>>
>>
>>>
>>> Guess what is going to happen if you connect the shields together ?
>>
>>
>> ** Nothing - cos the earth conductor carries virtually no current and so has no voltage drops.
>>
>>
>>> With a bad unbalance load between the stairs feeders, a huge amount
>>> (several amperes) may flow from staircase 1 to staircase 2 neutral
>>> through your signal cable shield, causing _a_lot_ havoc to your
>>> communication.
>>
>>
>>** What halluncinary drugs are you on today ??
>>
>> No-one connects signal grounds to the damn NEUTRAL !!!
>
>Not directly of course, but look at the big picture.
>
>Take a look at
en.wikipedia.org/wiki/Earthing_system and especially
>TN-C-S
>
>Do you expect that the Neutral (N) and protective ground (PE) wires
>would run the whole way back to the power plant. That would be a true
>TN-S system with total of 5 wires. In practice the distribution system
>is some form of TN-C-S, in which the PEN (combined protective earth
>and neutral starts at the distribution transformer star point. This
>PEN conductor is split into PE and N at some point towards the
>customer.
>
>This splitting point could be at the main distribution panel, in any
>sub distribution panel or in apartment specific distribution panel. It
>would not at all be strange to have a common PEN conductor in the
>raiser cables in two separate stairs and hence different ground
>potential between stairs.
>
>Some older regulation allow the PEN to PE and N in each mains socket.
>Thus, the equipment mains cord, is the only -S part in TN-C-S
>
>If the equipment signal ground or shield are connected to the
>equipment local PE ground, there may be ground potential differences
>between devices even in the same room, same apartment and at least
>between buildings.
>
>>
>> Doing that would be CRIMINAL !!
>>
>>
>>>
>>> For this reason, one should avoid connecting cable shields together.
>>>
>> ** More insane crap.
>>
>> You need kicking off this NG pal.
>>
>>
>>> >When you connect a signal generator to an oscilloscope with a BNC-BNC
>>> >coax cable, do you strip out the shield on the scope end of the cable?
>>>
>>> As long as you are using a single mains outlet to feed a grounded
>>> extension cable for these two devices, the device ground potentials
>>> should be within a few millivolts.
>>
>> ** Same goes for any AC power outlet in the same premises.
>>
>>Neutral current is not involved unless there is a dangerous fault in the AC supply wiring.
>>
>>
>>.... Phil
>>
>>
Once again Phil Allison gets outside his demesnes and speaks incorrectly
again. Phase imbalances are really quite frequent and the reason that
neutral conductors are the same size as phase conductors today in the NEC
and related standards and regulations.
?-)