>> >> >> And then somebody plugs it into daisy-chained extension cords and your 'safety
>> >> >> device' burns down the building. Brilliant all round. :(
>> >>
>> >> >don't implement it stupidly. The current limiter must have overheat protection.
>> >>
>> >> How are you going to do that if you don't know how it's connected?
>>
>> >I'm not making sense of that question
>>
>> So I gather. See the comment about daisy-chained extension cords above. That's a well-known way of burning down buildings, even without deliberately shorting the mains to ground.
>
>Phil, (or someone) can you explain about the daisy chained power strips.
>We got yelled at, at a trade show, but never quite understood the explanation.
>
>There's a short in something on the end of the chain...
>Then.?
An ordinary fuse needs a short circuit current that is several times
the fuse nominal current in order to blow in a few seconds. With only
twice the nominal current, it takes many minutes before the fuse
blows.
The short circuit current depends on the distribution transformer
secondary output voltage and the _total_ loop resistance. The worst
case loop resistance consist of the transformer to house, internal
wiring in the house to the mains socket, the extension cord(s)
resistance to the load connected to last extension cord. Multiply this
resistance by two, to include both the Live and Neutral wire. With a
short at the furthest point, this is the total loop resistance as seen
from the distribution transformer.
Assuming that a 5x nominal current will blow the fuse fast enough, in
230 V land with typically 10 A fuses, the _total_ loop resistance must
be less than 5 ohms.
In some countries it is assumed that there is a single maximum length
extension cord in the longest in-house wire to a socket for a specific
cross section (both in-house and extension cable). Plugging multiple
extension cords in series, especially with smaller cross section, will
increase the loop resistances too much.
As such, plugging multiple short (say 3 m) extension cords in series
with sufficient cross section is not a big problem.
One way to indirectly measure th total loop resistance is to plug an
incandescent lamp at the end of the last extension cord and then plug
in and out some big load and observe how the lamp flickers during the
transition. Incandescent lamps are very sensitive to small voltage
variations. A strong variation will indicate a relatively high loop
resistance.