HVAC capacitor questions

1,415 views
Skip to first unread message

mook johnson

unread,
Aug 5, 2012, 11:57:14 AM8/5/12
to
I have a 4 ton Carrier A/C that the original GE cap (Dual 60uF/5uF 440VAC)
went out last summer in ~May. It was about 6 years old. The top was bulged
badly so it was pretty clear the capacitor was bad.

Went to granger and found a Dayton capacitor that had the same ratings but
slightly smaller diameter (2.5 vs 2.75").

http://www.grainger.com/Grainger/DAYTON-Dual-Motor-Run-Capacitor-2MEK6

For $25 I figured what the heck. Cap worked great through the drought and
100+ Houston TX temperatures of 2011 and the temperatures of this summer,
not as hot but it is south Texas.

Well that cap died last night and of course on a Sunday granger is closed so
a borrowed window unit is keeping life support for now.

My question is:

Dual caps have essentially two caps in one package. My understanding this
is just for convenience of mounting and shortened assembly/repair times.

Looking at single 60uF 440V caps they are almost the same size as the dual
capacitor I have now. Do you think going with two separate capacitors would
be more reliable than going back with a Dual cap since not tradeoffs need to
be made to fit in a certain package size?

I found that Granger now stocks the GE dual cap (Genteq)
http://www.grainger.com/Grainger/GENTEQ-Motor-Run-Capacitor-5CNC5


These are the two separate single caps. Costs more but if its more reliable
I'll give it a try.
http://www.grainger.com/Grainger/GENTEQ-Motor-Run-Capacitor-5CNC4

http://www.grainger.com/Grainger/GENTEQ-Motor-Run-Capacitor-5CMY2



What do you guys think?



Joerg

unread,
Aug 5, 2012, 1:03:28 PM8/5/12
to
Not sure which quality is better. But ... methinks ... this time you
should buy _two_ sets so that when it goes kablouie on a hot Friday
night the missus ain't gonna be unhappy. Then you could walk out there,
fix it in minutes, and be the family hero :-)

Note to self: Got to buy spare float valve for evap cooler. Same reason.

--
Regards, Joerg

http://www.analogconsultants.com/

John Larkin

unread,
Aug 5, 2012, 3:01:51 PM8/5/12
to
On Sun, 05 Aug 2012 10:03:28 -0700, Joerg <inv...@invalid.invalid>
wrote:
Yeah, always buy two of anything that breaks.


--

John Larkin Highland Technology Inc
www.highlandtechnology.com jlarkin at highlandtechnology dot com

Precision electronic instrumentation
Picosecond-resolution Digital Delay and Pulse generators
Custom timing and laser controllers
Photonics and fiberoptic TTL data links
VME analog, thermocouple, LVDT, synchro, tachometer
Multichannel arbitrary waveform generators

mook johnson

unread,
Aug 5, 2012, 4:40:46 PM8/5/12
to

"John Larkin" <jjla...@highNOTlandTHIStechnologyPART.com> wrote in message
news:6ogt181jan59jpa3k...@4ax.com...
That is the plan. Being the perpetual cheapo I fond something that will
satisfy the cheapo in me and get the redundancy I need for next time.

I going the easy route and getting the dual Genteq tomorrow for ~$35 then
trying this guy as a backup

http://www.ebay.com/itm/Run-Capacitor-60-5-MFD-370-440V-New-/120959715983?pt=LH_DefaultDomain_0&hash=item1c29c2ca8f

I tool a look at QE Quality capacitors website and it look pretty decent.
Assuming its all true.

Not bad for a backup to allow me to get through a weekend before I get a new
replacement.




Tim Williams

unread,
Aug 5, 2012, 5:00:40 PM8/5/12
to
Obvious answer.. don't be the cheapo, buy a real film cap that'll last ten
years. It won't even cost ten times more!

Tim

--
Deep Friar: a very philosophical monk.
Website: http://webpages.charter.net/dawill/tmoranwms

"mook johnson" <mo...@mook.net> wrote in message
news:501e97dc$0$30768$882e...@usenet-news.net...

mook johnson

unread,
Aug 5, 2012, 5:31:02 PM8/5/12
to

"Tim Williams" <tmor...@charter.net> wrote in message
news:jvmmtq$pa4$1...@dont-email.me...
> Obvious answer.. don't be the cheapo, buy a real film cap that'll last ten
> years. It won't even cost ten times more!
>
> Tim
>

Suggestions? What is a real film cap? Are you talking about the black
plastic bricks with the cap potted inside

http://www.sourcingmap.com/larger_image.php?products_image=ux_a12062100ux0202_ux_&p=236842&products_imageType=jpg


I have wondered about the internal construction of metal packaged A/C caps
vs the potted film run capacitors. The metal can ones are sometimes
referred to as film as well.

I wondered if it wise to use these with an outside A/C unit.

My understanding is that the traditional metal can A/C caps are built that
way so when they fail the tops bulge out and break the electrical
connections inside thereby isolating the fault.

Would those black plastic ones just catch on fire when hooked to a 40A
circuit?






John Larkin

unread,
Aug 5, 2012, 5:55:28 PM8/5/12
to
On Sun, 5 Aug 2012 15:40:46 -0500, "mook johnson" <mo...@mook.net>
wrote:
Those run caps seem to fail when it's the hottest outside. That makes
sense.

It's a scorcher here right now. Full sunlight, no fog, 67 F. We don't
have AC.

Joerg

unread,
Aug 5, 2012, 6:14:37 PM8/5/12
to
And write down where it was purchased and file that into a manila folder
that says "A/C" or something on there. I neglected to do that on faucet
rubbers because when moving to the US I could only by a 25-pack (only
one faucet leaked when we bought the house). So I thought this is going
to last a lifetime ... *wrong* ... used the last one a while ago. The
water here is so chlorinated it literally eats rubber.

Luckily we have the oldest hardware store west of the Mississippi right
here. If they ain't got it then it doesn't exist :-)

http://www.flickr.com/photos/fountain-tallman/
http://moonshinejunkyard.blogspot.com/2010/08/tuesdays-in-my-town-placerville.html

Nico Coesel

unread,
Aug 5, 2012, 6:24:45 PM8/5/12
to
"mook johnson" <mo...@mook.net> wrote:

>
>"John Larkin" <jjla...@highNOTlandTHIStechnologyPART.com> wrote in message
>news:6ogt181jan59jpa3k...@4ax.com...
>> On Sun, 05 Aug 2012 10:03:28 -0700, Joerg <inv...@invalid.invalid>
>> wrote:
>>
>>
>> Yeah, always buy two of anything that breaks.
>>
>
>That is the plan. Being the perpetual cheapo I fond something that will
>satisfy the cheapo in me and get the redundancy I need for next time.

Can't you remodel it to use an inverter? When I had to replace our
central ventilation unit I choose a model with an inverter. I replaced
the capacitors on the previous one several times.

--
Failure does not prove something is impossible, failure simply
indicates you are not using the right tools...
nico@nctdevpuntnl (punt=.)
--------------------------------------------------------------

Michael A. Terrell

unread,
Aug 5, 2012, 9:27:53 PM8/5/12
to
'Dayton' is Grainger's house brand. Seperate caps are OK< if you
have room for thmem. I would just buy the OEM part and a spare.

Tim Williams

unread,
Aug 6, 2012, 12:10:06 AM8/6/12
to
"mook johnson" <mo...@mook.net> wrote in message
news:501ee619$0$11672$882e...@usenet-news.net...
> I have wondered about the internal construction of metal packaged A/C caps
> vs the potted film run capacitors. The metal can ones are sometimes
> referred to as film as well.
>
> I wondered if it wise to use these with an outside A/C unit.
>
> My understanding is that the traditional metal can A/C caps are built that
> way so when they fail the tops bulge out and break the electrical
> connections inside thereby isolating the fault.
>
> Would those black plastic ones just catch on fire when hooked to a 40A
> circuit?

AFAIK, film caps (the film-in-oil, metal can type) last essentially forever.
I don't know about 40A, but I'd be surprised if a film cap operated at 140F
ambient didn't last more than 20 years.

The small physical size suggests to me that, at least the start section, is
a bipolar electrolytic, which is typically used for motor-start
applications, and short lived (not only at the >40A surge, but even just
being at 140F ambient for a few years).

The 30uF 370V can I've got sitting in my junk box is about 1-1/4" thick,
2-1/2" wide (oval shape) and 4" tall. Unless they've really changed the
game with film thickness these days, I don't see 60uF 440V fitting in a much
smaller package unless it's electrolytic. (The run part might still be film
though.)

Obviously, you'd need the space to fit such a capacitor...

miso

unread,
Aug 6, 2012, 2:06:26 AM8/6/12
to

>
> Those run caps seem to fail when it's the hottest outside. That makes
> sense.
>
> It's a scorcher here right now. Full sunlight, no fog, 67 F. We don't
> have AC.
>
>

It was damn cold on Saturday even deep inland in the bay area. I was in
Livermore freezing in the sub-70 deg F weather. Brrrr!

When I see those tubby nudists in the fog on Baker Beach, I have to say WTF.

miso

unread,
Aug 6, 2012, 2:13:52 AM8/6/12
to

I never heard of an inverter in an air conditioner, but the wiki seems
to make sense:
> http://en.wikipedia.org/wiki/Air_conditioner_inverter

I suspect the air conditioning itself is better since it is a continuous
flow versus duty cycle modulation. [There are some high end
refrigerators that run continuously with what I guess is a similar scheme.]

Those AC caps fail a lot. I know quiet a few Ca to Nv transplants, and
they are routinely replacing the AC cap. Since an air conditioner really
only lasts about 15 years, it would be wise to go inverter for the
replacement. I assume heat pumps have similar schemes.

mook johnson

unread,
Aug 6, 2012, 4:06:34 PM8/6/12
to

"Tim Williams" <tmor...@charter.net> wrote in message
news:jvng31$kit$1...@dont-email.me...
Something like these? Price isn't too bad.


http://www.cde.com/catalogs/SF.pdf



Tim Williams

unread,
Aug 6, 2012, 7:53:38 PM8/6/12
to
Yes, and many others; I believe mine are old (not PCBs-old) GE parts (which
I guess are Genteq or something now).

Tim

--
Deep Friar: a very philosophical monk.
Website: http://webpages.charter.net/dawill/tmoranwms

"mook johnson" <mo...@mook.net> wrote in message
news:502024b8$0$2322$882e...@usenet-news.net...

mook johnson

unread,
Aug 7, 2012, 7:21:04 AM8/7/12
to

"Tim Williams" <tmor...@charter.net> wrote in message
news:jvple7$vgp$1...@dont-email.me...
Just realized I got snookered by Grainger. They labeled the cap Genteq when
actually they are Proline. Both made by the same manufacturer that makes GE
but the lifetime spec on the Genteq is 60K hours while the lifetime spec on
the Proline is 10K hours. :(


Let see, 8700 hours in a year... Houston tx,..figure 5000 hours a year run
time... 2 years before I can expect this guy to pop IF it meets its
specifications. Genteqs sell for the same price ~$35 on other places
besides Grainger.


Oh well. I have my $11 china cheapo (Qe Quality) will be arriving Friday as
a backup. Next purchase will be something like the CDE caps. At least a
known name in the capacitor business.




whit3rd

unread,
Aug 8, 2012, 3:36:48 PM8/8/12
to
On Tuesday, August 7, 2012 4:21:04 AM UTC-7, mook johnson wrote:
> "Tim Williams" <tmor...@charter.net> wrote in message
>
>
>
> Just realized I got snookered by Grainger. They labeled the cap Genteq when
>
> actually they are Proline. Both made by the same manufacturer that makes GE
>
> but the lifetime spec on the Genteq is 60K hours while the lifetime spec on
>
> the Proline is 10K hours. :(

> Let see, 8700 hours in a year... Houston tx,..figure 5000 hours a year run
>
> time... 2 years before I can expect this guy to pop

No, it's not that bad. This is a STARTING capacitor, not a run capacitor; it gets
ten seconds of use four times a day.

In unrelated news, the pressure life of an artillery barrel is about four seconds...

NM5K

unread,
Aug 8, 2012, 3:52:43 PM8/8/12
to
On 8/8/2012 2:36 PM, whit3rd wrote:

>
>> Let see, 8700 hours in a year... Houston tx,..figure 5000 hours a year run
>>
>> time... 2 years before I can expect this guy to pop
>
> No, it's not that bad. This is a STARTING capacitor, not a run capacitor; it gets
> ten seconds of use four times a day.


Nope.. That's a run cap. A start cap would be the type used
with a hard start kit.
The caps they make these days are cheap and don't last.
Even the better brands are pretty much junk these days.
One thing I would do is use 440v rated caps vs 370v.
I think they tend to last a bit longer before going kaput.



Michael A. Terrell

unread,
Aug 8, 2012, 7:18:53 PM8/8/12
to
He stated: Dual 60uF/5uF 440VAC in the original post. The 60uF is
the starting cap, the 5uF is the run cap.

NM5K

unread,
Aug 9, 2012, 12:56:06 AM8/9/12
to
On 8/8/2012 6:18 PM, Michael A. Terrell wrote:
>

>
>
> He stated: Dual 60uF/5uF 440VAC in the original post. The 60uF is
> the starting cap, the 5uF is the run cap.
>

Nope... The 60 mf is the run cap for the compressor. The 5 mf
is the run cap for the fan motor.



Michael A. Terrell

unread,
Aug 9, 2012, 11:11:27 AM8/9/12
to
Did he say that?

NM5K

unread,
Aug 9, 2012, 1:35:30 PM8/9/12
to
Not that I recall.. I said it though. Why? Because one
said the cap was a start cap, which it is not, and then
you claimed that the 5 mf was the run cap, and the 60 mf
was a start cap. Neither statement was correct.
And we don't want no incorrectness on this here interweb,
now do we. :)




Michael A. Terrell

unread,
Aug 9, 2012, 6:55:52 PM8/9/12
to
So, you've never seen a split phase motor with two capacitors?

NM5K

unread,
Aug 9, 2012, 8:56:41 PM8/9/12
to
On 8/9/2012 5:55 PM, Michael A. Terrell wrote:
>
> NM5K wrote:

>> Not that I recall.. I said it though. Why? Because one
>> said the cap was a start cap, which it is not, and then
>> you claimed that the 5 mf was the run cap, and the 60 mf
>> was a start cap. Neither statement was correct.
>> And we don't want no incorrectness on this here interweb,
>> now do we. :)
>
>
> So, you've never seen a split phase motor with two capacitors?
>

That is not what he has. Why would I care about obtuse examples
that have nothing to do with what he has?



Michael A. Terrell

unread,
Aug 9, 2012, 11:05:21 PM8/9/12
to
Obtuse? How do you know what he has, if you haven't seen the
hardware? Two capacitor motors aren't obtuse. Lots of compressor
motors use them.

NM5K

unread,
Aug 10, 2012, 5:15:14 AM8/10/12
to
On 8/9/2012 10:05 PM, Michael A. Terrell wrote:

>>
>> That is not what he has. Why would I care about obtuse examples
>> that have nothing to do with what he has?
>
>
> Obtuse? How do you know what he has, if you haven't seen the
> hardware? Two capacitor motors aren't obtuse. Lots of compressor
> motors use them.
>

I know *exactly* what he has. He told us in the first post.
I Quote..

"I have a 4 ton Carrier A/C that the original GE cap (Dual 60uF/5uF 440VAC)"

And for the usual residential type condensing unit, yes, a
compressor motor with two run caps would be quite obtuse.
Like a pretty much zero chance of seeing one.

Almost all modern compressor motors use a single run cap,
and if starting is an issue, they add a start kit, which is a
start cap with a potential relay. Or they can slap a single
piece start kit with a start cap and a S/S relay built on top.
Not two run caps!

None of the usual fan motors in a modern condensing unit use two run
caps. Zero. None. Nada.

I don't know where you get your information, and I really don't care.
I've been working on air conditioners since 1977.
Only for a couple of years in the late 80's, when I owned a different
business, did I take a break from working on air conditioners, from the
overall time period 1977 until 2012.

I currently work on air conditioners, and I change out so many caps
that's it's almost become a new sideline due to the pathetic quality of
caps in the last few years. I make a lot of money due to these cheap
ass caps. :) Easy money my man, very easy money... :)

I've been in business long enough to remember when you rarely saw
bad caps.
I change some poor bastards, or bastardette, if they don't have
hairy legs, blown out A/C cap almost every single freakin day!!!
Some days, more than one case.
I change so many that I have to keep a complete stock of every common
value on the truck to avoid making store runs, and to make sure I have
one when it's 8:39 in the PM and after store hours.
How many A/C caps do you change out a week?

Why do you insist on humping my legs over silly ass A/C caps?
Sometimes when I'm in some bastards backyard changing an A/C cap, dogs
try to do that... :/ I think from now on, I'll ask them..
Hey doggy! are you happy to see me, or is your name Michael A. Terrell?

































Michael A. Terrell

unread,
Aug 10, 2012, 9:05:29 AM8/10/12
to

NM5K wrote:
>
> On 8/9/2012 10:05 PM, Michael A. Terrell wrote:
>
> >>
> >> That is not what he has. Why would I care about obtuse examples
> >> that have nothing to do with what he has?
> >
> >
> > Obtuse? How do you know what he has, if you haven't seen the
> > hardware? Two capacitor motors aren't obtuse. Lots of compressor
> > motors use them.
> >
>
> I know *exactly* what he has. He told us in the first post.
> I Quote..
>
> "I have a 4 ton Carrier A/C that the original GE cap (Dual 60uF/5uF 440VAC)"
>
> And for the usual residential type condensing unit, yes, a
> compressor motor with two run caps would be quite obtuse.
> Like a pretty much zero chance of seeing one.
>
> Almost all modern compressor motors use a single run cap,
> and if starting is an issue, they add a start kit, which is a
> start cap with a potential relay. Or they can slap a single
> piece start kit with a start cap and a S/S relay built on top.
> Not two run caps!
>
> None of the usual fan motors in a modern condensing unit use two run
> caps. Zero. None. Nada.


Where did I say the fan did?


> I don't know where you get your information, and I really don't care.
> I've been working on air conditioners since 1977.
> Only for a couple of years in the late 80's, when I owned a different
> business, did I take a break from working on air conditioners, from the
> overall time period 1977 until 2012.
>
> I currently work on air conditioners, and I change out so many caps
> that's it's almost become a new sideline due to the pathetic quality of
> caps in the last few years. I make a lot of money due to these cheap
> ass caps. :)


Motor caps see rough service. Caps are always a weak link in
circuits. There are a hell of a lot more A/C systems these days and a
lot are sized to be barely adequate, so the compressors run harder than
one than one that can handle the load. The thing that kills the
capacitors is heat. They are mounted next to the compressor, inside the
hottest point in the system. Designs that could be a lot better, but
aren't.


Easy money my man, very easy money... :)


Typical HVAC attitude. My dad had his central fail recently. The
SOB he called wire tied the wires to the fan to the grill. The idiots
that installed the unit here set it on a tree stump. SO far, I've used
3/4 ton of marble chips to level it. They change their name about every
six months, so you can't track them down. HVAC are the biggest bunch of
thieves I've ever had the misfortune to work with. The last round was
on a new college campus where I was installing the commercial fire
alarms. Eight systems in two equipment rooms, and they couldn't even set
them where they were told to. They were against the back wall, where it
would be nearly impossible to service, and they tried to do the
electrical work themselves on a state job. The state required duct
detectors on all eight systems, but I was told they would murder me if I
touched the ductwork. The general contractor and architectural firm had
to intervene and tell them that they would be responsible for all fees
for work that wasn't completed on time. They were only there about five
hours a day, and lazy SOBs.

I had one local company call me 17 times in one day to offer me 'A
special rate on my central A/C'. I didn't have A/C and they were tying
up my business phone so I told them that I would call a bunch of
retirees and have them call about quotes, or to ask endless questions to
tie up their phone line if they called me again.


> I've been in business long enough to remember when you rarely saw
> bad caps.


When was that? I've seen them since the '60s.


> I change some poor bastards, or bastardette, if they don't have
> hairy legs, blown out A/C cap almost every single freakin day!!!
> Some days, more than one case.


No different than the old tube type TV days. The difference was
that some of them exploded and blew the back off the set or blew a hole
in it. The inside of the set was full of aluminum foil, shredded paper
and oil.


> I change so many that I have to keep a complete stock of every common
> value on the truck to avoid making store runs, and to make sure I have
> one when it's 8:39 in the PM and after store hours.


So you carry some stock. What repair business doesn't? We used to
stock over 2000 different parts on our TV service trucks. When I did
industrial electronics I carried complete panels to get customers back
on line in a hurry. If the on site repair would take too long, I
offered a fixed rate exchange.


> How many A/C caps do you change out a week?


I no longer work on motor controls other than my own. I'm retired,
but still work on some computers as a hobby. How many low ESR caps do
you change on computer motherboards each day? They don't plug in, and
you can't use a pair of rusty Klein pliers to hammer them into place.


> Why do you insist on humping my legs over silly ass A/C caps?
> Sometimes when I'm in some bastards backyard changing an A/C cap, dogs
> try to do that... :/ I think from now on, I'll ask them..
> Hey doggy! are you happy to see me, or is your name Michael A. Terrell?


Yawn. Typical response from your trade. Bad attitude and a fake
screen name.

NM5K

unread,
Aug 10, 2012, 10:15:06 AM8/10/12
to
On 8/10/2012 8:05 AM, Michael A. Terrell wrote:

>
>> Why do you insist on humping my legs over silly ass A/C caps?
>> Sometimes when I'm in some bastards backyard changing an A/C cap, dogs
>> try to do that... :/ I think from now on, I'll ask them..
>> Hey doggy! are you happy to see me, or is your name Michael A. Terrell?
>
>
> Yawn. Typical response from your trade. Bad attitude and a fake
> screen name.
>

No, a typical response to a person that repeatedly tries to hump
my legs.
All I said to the other poster was that it was not a start cap,
but actually a run cap, and that caps in general are cheap and of
poor quality. And you seem to have some problem, and keep asking me
idiotic questions about parts that don't exist for the persons unit.

You don't know me for jack, and you have no idea what the quality
of my work is.
Almost everyone I do work for calls me back, and I get many
referrals. I have enough work just from existing customers that
know us, I don't have to advertise. And my prices to change a cap
are probably among the lowest in this city. I know some companies
that charge ridiculous prices. We don't. It's still good money
being it takes about 3 minutes to do.
All of the new equipment I install is permitted and inspected by the
city, and trust me, if something is not kosher, they will let you know
about it.

You are the one with the bad attitude. You obviously got bent over
by some unscrupulous moron HVAC tech, and you think everyone operates
that way. I'm sure you could also say the same thing about certain
TV techs too..
Fake screen name? Chortle.. You kill me, you really do. :|



bloggs.fred...@gmail.com

unread,
Aug 10, 2012, 3:07:41 PM8/10/12
to
On Sunday, August 5, 2012 11:57:14 AM UTC-4, mook johnson wrote:
> The top was bulged
>
> badly so it was pretty clear the capacitor was bad.


Uh-huh, sounds like the internal interrupter opened just in time:
"- U.L. registered internal current interrupter designed to disconnect the capacitor element if excessive pressure develops inside casing from misapplication"


> What do you guys think?

You're throwing good money after bad with those caps. Purchase a separate 5UF for the fan, but then /maybe/ get a 'hard start kit' for the compressor start cap.
http://www.grainger.com/Grainger/supco/ecatalog/N-1z1340f/Ntt-Hard+Start+Kit?Ndr=textsearchesinbase%2Btrue&ef_id=VGxPqVYTdX0AAF0N%3A20120810185439%3As&gclid=CJCsrILe3bECFYOc7QodnkAArg&sst=subset
Contact either SUPCO or Carrier to determine the kit most appropriate for your unit and area. Your 4-ton should be 4HP. Both of those manufacturers are rock solid performers in the industry.

mook johnson

unread,
Aug 11, 2012, 3:26:36 PM8/11/12
to

<bloggs.fred...@gmail.com> wrote in message
news:c8d9b571-14ea-4693...@googlegroups.com...
Do that hard start caps replace the 60uF compressor run cap or go in
parallel with it until the compressor starts then drops out?

I've heard some negative pres about kickstart caps causing more problems
than they fix. Do you have experience with these lasting long term?



bloggs.fred...@gmail.com

unread,
Aug 11, 2012, 8:21:40 PM8/11/12
to
They replace the start capacitor. Your problem is the excessive heat down there making that compressor start up against 500 psi internal pressures. This explains why the caps blow during the heat waves. The compressor is probably tripping out on overload until the condenser fan air can bring the pressure down.I would go one step further and add a time delay relay between the thermostat and the contactor. The time delay relay delays powering the contactor for a full 5 minutes. Then an aux relay takes the t-stat voltage and turns on the condenser fan immediately. This is a common technique used in extreme conditions like rooftop units and trailer a/c's. When you do the rewire use their 10000V HV wire or whatever it is.

Please view in a fixed-width font such as Courier.

.
.
.
.
.
.
.
. +---------+ +---------+
. | | | cndnsr |
. Tstat>--+-----| aux rly |------+ fan |
. | | | | |
. | +---------+ +---------+
. |
. |
. | +----------+
. | | 5 min | +-----------+ +----------+
. | | | | | | |
. -----+ delay +----| contactor |-----| cmprssr |
. | | | | | |
. | on make | +-----------+ +----------+
. | |
. +----------+
.
.
.

Tim Williams

unread,
Aug 11, 2012, 11:57:55 PM8/11/12
to
Also, if the thermostat doesn't do it already, a similar "remain on for 5
minutes" relay is a great idea for the ventilation fan itself.

Tim

--
Deep Friar: a very philosophical monk.
Website: http://webpages.charter.net/dawill/tmoranwms

<bloggs.fred...@gmail.com> wrote in message
news:5185f68c-f3a7-47a2...@googlegroups.com...

bloggs.fred...@gmail.com

unread,
Aug 12, 2012, 12:39:24 AM8/12/12
to
The delay-on-make delays the application of the input voltage to the output for the specified time interval, and thereafter remains on indefinitely as long as the input voltage is present. The output voltage is removed instantly with the input voltage. Not sure about the effect of a 5 minute run-on for an A/C evaporator fan, have never seen it applied, which doesn't mean it doesn't exist. If there is a problem with liquid refrigerant accumulation in the evaporator, it is usually handle by an inline device called an accumulator of all names :-), a standard component for automotive A/C. Medium temperature refrigeration, such as walk-in coolers, do use fan run-on the evaporator to eliminate frost build-up.

bloggs.fred...@gmail.com

unread,
Aug 12, 2012, 12:53:19 AM8/12/12
to
On Saturday, August 11, 2012 3:26:36 PM UTC-4, mook johnson wrote:
My suggestion assumes you haven't done something artistic like enclose your outdoor unit with an air-obstructing fence/lattice or located it underneath a deck, or something careless like clogged your condenser fins with grass clippings or something like that.

NM5K

unread,
Aug 12, 2012, 10:46:38 AM8/12/12
to
On 8/11/2012 2:26 PM, mook johnson wrote:

>
> Do that hard start caps replace the 60uF compressor run cap or go in
> parallel with it until the compressor starts then drops out?
>
> I've heard some negative pres about kickstart caps causing more problems
> than they fix. Do you have experience with these lasting long term?
>

Myself, I do not recommend using a hard start kit unless you
actually need a hard start kit.
IE: expansion valve instead of flow rater, has trouble starting, etc.
If it doesn't need one, I don't use them. I've got many condensing
units I've installed around town that have been in service for 15-25
years.
I was just on a call the other day to change a combo run cap on a unit I
installed 19 years ago.
It's never had a hard start kit and still runs like a champ.