On Fri, 17 Oct 2014 11:05:08 +0200, Fitzgerald
<
john....@mailinator.com> wrote:
>Where could I find requirements for creepage and clearance distances for
>electronics in a vacuum (1e-5 mbar) environment? The EN-IEC 61010-1
>specifies these distances for use in air and also lists derating factors
>for use at altitudes up to 5000 m (reduced pressure) but vacuum
>conditions are not mentioned at all.
The conductivity (ionization) of air increases rapidly with dropping
pressure, peaks at about 2 Torr and rises very rapidly as the vacuum
increases. Above about E-4 Torr the limit is point electron emission.
Beyond my capabilities to calculate but I know that some 5kV rated
vacuum relays I have separate the contacts by less than a mm.
I don't know of any standards but NEMA would most likely have some
specifications for such things as MHV and UHV (500-750kV) utility
breakers.
>
> From experience I can tell that a few kV/mm is easily doable, but I
>guess that my experience alone is not sufficient for certification :).
>Can anyone point me to a relevant standard?
You didn't mention what you're doing but you might want to consider
SF6 fill instead of a vacuum. Much easier to fill and maintain in the
enclosure plus SF6 will provide at least a little cooling. Though its
thermal conductivity is quite low, it's better than a vacuum.