On 5/21/2021 8:45 AM, Seattlemusic wrote:
> I have four 1/2” screw eyes going into 2 x12s which are running
> perpendicular to 5x12 glulams holding up about 250 pounds total (hanging
> a cluster in a music studio). It seems rock solid but I have heard some
> say the break strength of ANY screw eye in wood of any type is 75
> pounds. So yes technically it can hold it even with those numbers but
> not nearly at the safety margin I want. I will be sitting under this
> cloud/cluster often.
> Curious if this is sufficient or if I should open up the ceiling and get
> up higher with a through hole or something that won’t have a risk of
> wood + bolt failure.
A screw eye is more like a lag screw thread than an ordinary wood screw.
The maximum direct withdrawal load of lag screws from side grain of
seasoned wood is
p=8100 G^(3/2) D^(3/4) L
where
p = Max withdrawal load, lbf
D = Shank diameter, in
G = Specific gravity of the wood based on oven dry weight and volume
at 12% moisture content
L = Length of penetration of threaded part, in.
For SYP assuming it is 1/2" shank (not clear) and 1" penetration, it's
about 3,500 lbf for each.
If it is symmetrically-shared load, each is only about 60-65 lbf loading
presuming your estimate of the total load is approximately correct.
Again, the above also presumes a properly-sized pilot hole and installation.
<
https://www.engineersedge.com/calculators/lag_screws_in_wood_pullout_resistance_15390.htm>
Can't really envision the physical arrangement of these 2x12 with
respect to the glulams; are they inserts and if so, how are they being
supported? There _might_ actually be the weak point, depending...
--