Ed, N5EI
Your local hardware store should have them.
Peter
"Edward A. Feustel" <efeu...@ists.dartmouth.edu> wrote in message
news:3C04E009...@ists.dartmouth.edu...
In particular, you can find the standard NEMA socket configurations
at:
http://www.leviton.com/sections/techsupp/nema.htm
and
http://www.quail.com/locator/nema.htm
(and probably some others!)
Personally, I'd go with the 250V 20A grounding one, NEMA 6-20R. Note
that it will accomodate either a 20A or a 15A plug. 20A@240V =
4800VA, and that seems like it should give enough margin for most
amplifiers. (But good practice is to plan for ~20% more capacity
than the maximum expected load.) You could go for a feed that could
accomodate higher current in the future if you end up needing it, and
then only have to change the socket and breaker. 10 gauge wire would
normally get you to 30A, unless there are extenuating circumstances,
and gives you lower drop under load for your 20A service than the
default 12ga would. Of course, if you know the amplifier of your
dreams will take 4500VA, you should probably go ahead with the 30A
service to start with. FWIW, I'd also put in at least one dedicated
20A 120V circuit to the hamshack, and plenty of outlets.
Cheers,
Tom
zulu <zu...@zulu.com> wrote in message news:<3C04878A...@zulu.com>...
--
Crazy George
Remove NO and SPAM from return address
zulu <zu...@zulu.com> wrote in message news:3C04878A...@zulu.com...
http://www.leviton.com/sections/techsupp/nema.htm
If a long run (for the 20 amp feed) from the main breaker panel to your
location, consider 10-3/with Ground
gb
"Tom Bruhns" <tom_b...@agilent.com> wrote in message
news:3832adca.01112...@posting.google.com...
The standards dictate that you shouldn't have a preference. For "x"
amps use "x" receptacle. A savvy insurance company can nail you on that
when your Xmas tree catches fire. "House suffered improper electrical
installation".
-:-)
Bill