But at the scrap yard, I ran across a 1/2 hp three phase motor that
had a key taped in place on the shaft. May not have ever been used.
There were no wire nuts on the power leads and it did not look like
they had ever had a wire nut on them.
So can you run an unloaded motor off a VFD that is only rated at half
the motors hp? Well the answer is that you can not at least with the
VFD that I was trying. After a second or so, the vfd would stop and
show an error code. But wait, the motor can be connected for either
240 or 480 volts. Meaning it has two sets of windings. Connect is
parallel for 240 volts and in series for 480 volts.
Or you can connect just one set of windings, and voila a 1/4 hp
motor. Works with the VFD just fine.
Dan
I had the same result trying a 5 hp. VFD on a 7.5 hp motor.
Karl
<dca...@krl.org> wrote in message
news:c61cf887-5bff-48b7...@g11g2000yqe.googlegroups.com...
>Or you can connect just one set of windings, and voila a 1/4 hp
>motor. Works with the VFD just fine.
Do the VFD's have any provison to sync two together? If so, you could use
one on each winding set....
--
A host is a host from coast to coast.................wb8foz@nrk.com
& no one will talk to a host that's close........[v].(301) 56-LINUX
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433
I will have to look at the manual again, but I do not think there is
any way to sync the VFD's.
Dan
Bob Swinney
"Karl Townsend" <karltown...@embarqmail.com> wrote in message
news:4ba5443b$0$65832$892e...@auth.newsreader.octanews.com...
Jon
Jon
Most VFDs incorporate over current protection for the output transistors. A
large motor
will be seen as a overload and shutdown the output. The inrush current looks
like a short
circuit to the vfd and it shuts down.
Best Regards
Tom.
>> Do the VFD's have any provison to sync two together? If so, you could use
>> one on each winding set....
>NEVER, EVER, try this, unless you like BIG sparks! There are modular
>VFDs, usually in hundred HP sizes, that can be paralleled and synched
>for larger motors. otherwise, they will not tolerate this AT ALL!
Even when they say so? Note I was asking.,,,
(I used to work on low megawatt UPS's, built out of 10KW power
modules.)