h200

unread,
Oct 5, 2012, 3:54:44 PM10/5/12
to
Hi.

I have 11kw 3 phase motor controlled by variable frequency drive (
siemens micromaster).

The drive can be powered with one phase ( with little pcb change ) and
it can give 3 phase output. So i was thinking to connect one phase to
the drive to see how much power can i get on motor side.

My question would be, how to calculate maximum horsepower or KW used by
3 phase motor, if he is be connected to 220 / 50 HZ - 8KW source ?

Can he run on half of the power or maybe 6 - 7kw ?


Regards !

Michael A. Terrell

unread,
Oct 5, 2012, 4:59:08 PM10/5/12
to
No. TANSTAAFL.

dca...@krl.org

unread,
Oct 5, 2012, 5:23:47 PM10/5/12
to
On Oct 5, 3:54 pm, h200 <hub...@net.com> wrote:
> Hi.

> My question would be, how to calculate maximum horsepower or KW used by
> 3 phase motor, if he is be connected to 220 / 50 HZ - 8KW source ?
>
> Can he run on half of the power or maybe 6 - 7kw ?
>
> Regards !

Not sure I understand what you are asking.

A three phase motor can be run on a single phase and will deliver
about 2/3 the power it would have on three phase. And you can do this
without any variable frequency drive. But you have to have a way to
get the three phase motor to rotate.

I would not recommend using a VFD to run a three phase motor. I
suspect it would ruin the VFD and maybe also the motor. Depends on
how fast the circuit breaker acts.

Do some searches on " phase converter.

Dan.

Pete C.

unread,
Oct 5, 2012, 5:47:05 PM10/5/12
to
Either 2/3 or full power depending on the drive. It should say what it's
rating is on single phase input in the specs.

PrecisionmachinisT

unread,
Oct 5, 2012, 5:54:26 PM10/5/12
to

<dca...@krl.org> wrote in message news:3914f044-ac01-4388...@c2g2000yqe.googlegroups.com...

> I would not recommend using a VFD to run a three phase motor. I
> suspect it would ruin the VFD and maybe also the motor. Depends on
> how fast the circuit breaker acts.

Bath salts ?

et...@whidbey.com

unread,
Oct 5, 2012, 6:04:59 PM10/5/12
to
Dan, you know better. VFD drives are almost exclusively used to run
three phase motors. Perhaps responding to political posts has warped
your mind. Or maybe you are just "taking the piss" as folks say on the
other side of the pond.
Eric

Lloyd E. Sponenburgh

unread,
Oct 5, 2012, 6:55:46 PM10/5/12
to
"PrecisionmachinisT" <123mac...@notmail.com> fired this volley in
news:rb-dnbqvAbiByvLN...@scnresearch.com:

> Bath salts ?

GOTTA be. I run several machines in my shop on VFDs, because POWCO "don't
deliver no three wires" to my locale (that's a quote).

Lloyd


dca...@krl.org

unread,
Oct 5, 2012, 8:10:53 PM10/5/12
to
On Oct 5, 6:04 pm, e...@whidbey.com wrote:


>
> >I would not recommend using a VFD to run a three phase motor.  I
> >suspect it would ruin the VFD and maybe also the motor.  Depends on
> >how fast the circuit breaker acts.
>
> >Do some searches on " phase converter.
>
> >                                                       Dan.
>
> Dan, you know better. VFD drives are almost exclusively used to run
> three phase motors. Perhaps responding to political posts has warped
> your mind. Or maybe you are just "taking the piss" as folks say on the
> other side of the pond.
> Eric

I do know better. I am a slow typist and often get my thoughts way
ahead of what I have typed.
In this case, I meant " I would not recommend using a vfd to run a
three phase motor on one phase." Three little words left out and the
whole meaning is changed.

I have a three phase motor on my lathe and use a VFD to power the
motor. Also got a 3 phase bench grinder recently and am going to use
a VFD on that too.


Dan

Gunner

unread,
Oct 5, 2012, 8:39:40 PM10/5/12
to
The average VFD, on single phase... will deliver about 75-80% of the
rating of it being run on 3phase

Gunner

The methodology of the left has always been:

1. Lie
2. Repeat the lie as many times as possible
3. Have as many people repeat the lie as often as possible
4. Eventually, the uninformed believe the lie
5. The lie will then be made into some form oflaw
6. Then everyone must conform to the lie

Gunner

unread,
Oct 5, 2012, 8:41:50 PM10/5/12
to
On Fri, 5 Oct 2012 14:23:47 -0700 (PDT), "dca...@krl.org"
<dca...@krl.org> wrote:

Most...not all..but most VFD manufactures approve of running them on
single phase, with the caveat that they do drop at least 25% of their
capacity when doing so.

Bob La Londe

unread,
Oct 5, 2012, 8:42:12 PM10/5/12
to
<dca...@krl.org> wrote in message
news:450c0e52-0302-47a4...@o8g2000yqh.googlegroups.com...
Lots of VFDs out there that document using single phase in 3 phase out. I
have three motors in my shop configured that way. Drives Warehouse even
lists one that only has connections for single phase and its rated for a
full 5HP. (About 3.7Kw) What I have not seen is a VFD rated for single to
three phase for more than 3.7kw. The OP says 11Kw. That is one big honking
motor.

et...@whidbey.com

unread,
Oct 7, 2012, 2:11:02 PM10/7/12
to
Greetings Dan,
I use a VFD on my band saw. The saw came with a single phase motor but
I replaced it with a three phase motor and a VFD. So now I can cut
steel and aluminum with the same blade without changing belts.
Eric

Jon Elson

unread,
Oct 8, 2012, 4:19:53 PM10/8/12
to
Gunner wrote:


> The average VFD, on single phase... will deliver about 75-80% of the
> rating of it being run on 3phase
Some VFDs are set up to alarm if they don't have all 3 phases.
Most under 10 KVA will run on single phase input. If you load
them to 100% rating on single phase it can damage the rectifier and
will certainly shorten the life of the capacitor bank (unless the
manufacturer has specifically over-designed these parts to permit
full power on single phase.) Some people recommend a 50% derating
for single phase, but I think your 75% is a good number for typical
shop use, where the 75% rating is rarely needed.

I have a 1 HP rated VFD on my 1 HP Bridgeport, and it has run perfectly
for over a decade. I got this before I knew about the derating
issue, but I'm getting away with it in light home-shop use.

Jon

Paul Hovnanian P.E.

unread,
Oct 9, 2012, 2:55:34 PM10/9/12
to
I think (correct me if I'm wrong), the OP wants to run the input of the VFD
on single phase.

It all depends on the design and rating of the input stage of the VFD. Some
are rated explicitly for this mode of operation. They have beefier input
rectifiers to allow for full power draw by a single (line to line) phase
input.

Most VFDs are an AC to DC power supply (a rectifier array and some power
factor regulation switching). Following this DC stage, the VFD has a three
phase bridge, which 'chops' the DC to produce the variable frequency and
duty cycle pulses. This output stage doesn't care where its DC input comes
from. As long as the input rectifier can take it, you can put out full
power.

Never run a VFD with an output phase disconnected (VFD to motor). There
might be a few strange beasts that will tolerate this. But they are rare.

The beauty of a VFD is that they DO allow the use of three phase motors
where only single phase is available. Better efficiency and starting
characteristics, not to mention the speed control feature.

--
Paul Hovnanian mailto:Pa...@Hovnanian.com
------------------------------------------------------------------
"The day Microsoft makes something that doesn't suck is probably the day
they start making vacuum cleaners" - Ernst Jan Plugge

Lloyd E. Sponenburgh

unread,
Oct 9, 2012, 3:00:15 PM10/9/12
to
"Paul Hovnanian P.E." <pa...@hovnanian.com> fired this volley in news:ef-
dnTftFOPv7-nNn...@giganews.com:

> The beauty of a VFD is that they DO allow the use of three phase motors
> where only single phase is available. Better efficiency and starting
> characteristics, not to mention the speed control feature.
>

Since PowCo won't install "three wires" (their quote) to my shop, that's
how all my three-phase equipment runs. It's WAY cheaper than a rotary
converter.

LLoyd