Cold Exchanger - Condensing Tube
Given: A [98% efficient] counterflow tube in tube exchanger flash condenses [from feed pump calculations: 22.352 grams per second] of saturated butane vapor at 20 psi [from ASHRAE butane tables at 25°C: vapor enthalpy 620.98 kJ/kg, liquid enthalpy 259.65 kJ/kg; and at 5°C: liquid density 595.1 kg/m3].
Find: What is the vapor to liquid latent energy in joules?
Find: What is the saturated liquid volume in centiliters?
1. Calculate the vapor to liquid latent energy in joules:
Since 22.352 grams = .022352 kilograms] and
Since [kilograms per second x (vapor enthalpy - liquid enthalpy) = latent energy in kilojoules],
then (.022352 x (620.98 - 259.65) = 8.0764 kilojoules).
{or 8,076.4 joules}.
2. Compensate for exchanger heat losses by 2%:
Since [joules x 1.02 = required heat out], then (8,076.4 x 1.02 = 8,237.9 joules latent energy).
3. Calculate the saturated liquid volume in centiliters per second:
Since 22.352 grams = .022352 kilograms] and
Since [1 / liquid density 595.1 kg/m3 = liquid volume .0016804 m3/kg] and
Since [kilograms per second x liquid volume m3/kg = volume in cubic meters],
then (.022352 × .0016804 = 0.000037560 cubic meters per second).
{or 3.76 centiliters per second}.
These calculation groups are correct to the best of my knowledge (version 2.8). I am willing to edit any errors and repost. Please verify. Better formulas, values or more detail may be developed - updating the model and version number.