FW: Request to Review Inverter-Integrated Meter Certification Requirements

2 views
Skip to first unread message

Baak, Jim

unread,
Mar 17, 2008, 5:44:19 PM3/17/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
FYI,

Here is the response from Bill Ash at IEEE.

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell: 415-328-1658
Fax: 415-973-2510

www.pge.com/solar
www.pge.com/selfgen

-----Original Message-----
From: w....@ieee.org [mailto:w....@ieee.org]
Sent: Monday, March 17, 2008 5:25 AM
To: Baak, Jim
Cc: thomas...@NREL.gov
Subject: Re: Request to Review Inverter-Integrated Meter Certification
Requirements

Dear Mr. Baak,
Thank you for your inquiry. I cannot speak to the technical content of
the documents you presented. As for copyright or intellectual property
right infringements, I do not see any issues presented here as all IEEE
material are referenced and are not incorporated in the documents

Are there any other documents to be used in conjunction with these
documents that incorporate text or material from any IEEE standards?

Regards
******************************************************
Bill Ash
Senior Program Manager
IEEE Standards Activities Dept.
445 Hoes Lane
Piscataway, NJ 08854
PH: 732-465-5828
Email: w....@ieee.org
http://standards.ieee.org/
*****************************************************

IEEE.. . Fostering technological innovation and excellence for the
benefit of humanity.

"Baak, Jim"

<J6...@pge.com>


To
03/14/2008 <w....@ieee.org>,

08:25 PM <thomas...@NREL.gov>


cc
<onboard...@googlegroups.com>,

"Hornbrook, Charles" <CL...@pge.com>,

<andrew....@xantrex.com>, "Baak,

Jim" <J6...@pge.com>,

<ben.g...@sce.com>, "Bob Botkin"

<Robert...@sce.com>, "Brian
Farhi"
<Brian...@sunpowercorp.com>,

<carissa...@sce.com>,

<cwi...@imsmeters.com>, "Ivan
Cooper"
<iv...@solarcity.com>,

<jber...@sma-america.com>, "Jeff

Newmiller"

<jeff.ne...@bewengineering.com>,

"Jerry Pilger"
<jerry....@sce.com>,
<jon.bon...@sdenergy.org>,
"Joseph
Fleshman"

<JFle...@energy.state.ca.us>,

<mdar...@enphaseenergy.com>,

<mlaf...@universalenergies.com>,

<n...@cpuc.ca.gov>,
<oba...@smud.org>,
<pat.ad...@veris.com>,

<Pnar...@energy.state.ca.us>,
"Raghu
Belur" <rbe...@enphaseenergy.com>,

<ri...@fatspaniel.com>,

<rjoh...@sunpowercorp.com>,

<roger...@pvpowered.com>,

<ste...@ccontrolsys.com>, "Tirona,

William" <WR...@pge.com>


Subject
Request to Review
Inverter-Integrated
Meter Certification Requirements

Bill and Tom,


On behalf of the California Solar Initiative's 5% Meter Certification
Working Group, I am contacting you with a request to review our proposed
5% Accuracy Certification Requirements and Testing Procedures for
Inverter-Integrated Meters. This effort was undertaken at the direction
of the California Public Utilities Commission to ensure the accuracy of
this category of meters in the absence of standards for these devices.


Please see the attached letter and table that describes this effort and
provides details on the specific tests the Working Group is proposing.
The proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE
1547, UL 1741, FCC Part 15 and Sandia/CEC Inverter Performance Test
Procedures.


<<Inverter_Integrated_5%_Meters - IEEE.doc>> <<Certification Tests for
Inverter Integrated Meters v1 0 2-7-08.doc>> We would greatly appreciate
if you could review the document to ensure there are no copywrite or
intellectual property right infringements or concerns on behalf of IEEE.
We are requesting a response from IEEE no later than 3/28/2008 so that a
final plan can be adopted as soon as possible.


Please contact me if you have any questions or comments on this request.


Kind Regards,


Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.
77 Beale Street, Room 2731B
San Francisco, CA 94105-1814


Mailing Address:
Mail Code B27P:
P.O. Box 770000
San Francisco, CA 94177-0001


Office: 415-973-1152
Cell: 415-328-1658
Fax: 415-973-2510
Email: j6...@pge.com


www.pge.com/solar
www.pge.com/selfgen

(See attached file: Inverter_Integrated_5%_Meters - IEEE.doc)(See
attached
file: Certification Tests for Inverter Integrated Meters v1 0
2-7-08.doc)

Inverter_Integrated_5%_Meters - IEEE.doc
Certification Tests for Inverter Integrated Meters v1 0 2-7-08.doc

Baak, Jim

unread,
Mar 18, 2008, 2:11:49 PM3/18/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
All,
 
FYI - from MET Labs.

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell:    415-328-1658
Fax:    415-973-2510

www.pge.com/solar
www.pge.com/selfgen

 


From: Kevin Mehaffey [mailto:Kmeh...@metlabs.com]
Sent: Tuesday, March 18, 2008 11:08 AM
To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification Requirements

Hello Jim,

I have received your email and would be happy to look at the standard you are working on.  I will send you my feedback by the requested date.  Thank you for this opportunity to provide input.

 

Regards,


Kevin Mehaffey

EMC Lab Manager

MET Laboratories

Baltimore

(410)949-1823


From: Baak, Jim [mailto:J6...@pge.com]
Sent: Friday, March 14, 2008 9:05 PM
To: Kevin Mehaffey
Cc: onboard...@googlegroups.com; Hornbrook, Charles; andrew....@xantrex.com; Baak, Jim; ben.g...@sce.com; Bob Botkin; Brian Farhi; carissa...@sce.com; cwi...@imsmeters.com; Ivan Cooper; jber...@sma-america.com; Jeff Newmiller; Jerry Pilger; jon.bon...@sdenergy.org; Joseph Fleshman; mdar...@enphaseenergy.com; mlaf...@universalenergies.com; n...@cpuc.ca.gov; oba...@smud.org; pat.ad...@veris.com; Pnar...@energy.state.ca.us; Raghu Belur; ri...@fatspaniel.com; rjoh...@sunpowercorp.com; roger...@pvpowered.com; ste...@ccontrolsys.com; Tirona, William
Subject: Request to Review Inverter-Integrated Meter Certification Requirements

 

Kevin,

On behalf of the California Solar Initiative's 5% Meter Certification Working Group, I am contacting you with a request to review our proposed 5% Accuracy Certification Requirements and Testing Procedures for Inverter-Integrated Meters.  This effort was undertaken at the direction of the California Public Utilities Commission to ensure the accuracy of this category of meters in the absence of standards for these devices.

Please see the attached letter and table that describes this effort and provides details on the specific tests the Working Group is proposing.  The proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE 1547, UL 1741, FCC Part 15 and Sandia/CEC Inverter Performance Test Procedures.

<<Inverter_Integrated_5%_Meters - MET Labs.doc>> <<Certification Tests for Inverter Integrated Meters v1 0 2-7-08.doc>>

We would greatly appreciate if you could review the document and provide comments and suggestions for the final certification requirements.  We are requesting a response no later than 3/28/2008 so that a final plan can be adopted as soon as possible.

Baak, Jim

unread,
Mar 18, 2008, 5:48:33 PM3/18/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
FYI, from Intertek (ETL).

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell:    415-328-1658
Fax:    415-973-2510

www.pge.com/solar
www.pge.com/selfgen

 


From: Tony Dorta Intertek [mailto:tony....@intertek.com]
Sent: Tuesday, March 18, 2008 2:35 PM

To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification Requirements

Jim, I am trying to get a copy of the standard and I will go over the changes proposed.  Thanks
 

Regards,

Tony Dorta 
Assistant Chief Engineer
Intertek
Phone: (206) 248-8160
Fax: (503) 626-7328
Email Address: tony....@intertek.com
Website: www.intertek-etlsemko.com

 This e-mail transmission is strictly confidential and is intended solely for the identified person at the identified organization to whom it is addressed. This e-mail may contain privileged and confidential information. If you are not the intended recipient you must not copy, print, distribute or take any action in reliance upon this e-mail. If you have received this e-mail in error then please notify us as soon as possible and delete this e-mail.


Although Intertek Group plc believes this e-mail and any attachments to be free of any virus or other defect which may affect your computer, it is the responsibility of the recipient to ensure that it is virus free and Intertek Group plc does not accept any responsibility for any loss or damage arising in any way from its use."




From: Baak, Jim [mailto:J6...@pge.com]
Sent: Friday, March 14, 2008 6:30 PM
To: Tony Dorta Intertek
Cc: onboard...@googlegroups.com; Hornbrook, Charles; andrew....@xantrex.com; Baak, Jim; ben.g...@sce.com; Bob Botkin; Brian Farhi; carissa...@sce.com; cwi...@imsmeters.com; Ivan Cooper; jber...@sma-america.com; Jeff Newmiller; Jerry Pilger; jon.bon...@sdenergy.org; Joseph Fleshman; mdar...@enphaseenergy.com; mlaf...@universalenergies.com; n...@cpuc.ca.gov; oba...@smud.org; pat.ad...@veris.com; Pnar...@energy.state.ca.us; Raghu Belur; Rich Eckman; rjoh...@sunpowercorp.com; roger...@pvpowered.com; ste...@ccontrolsys.com; Tirona, William

Subject: Request to Review Inverter-Integrated Meter Certification Requirements

Tony,

On behalf of the California Solar Initiative's 5% Meter Certification Working Group, I am contacting you with a request to review our proposed 5% Accuracy Certification Requirements and Testing Procedures for Inverter-Integrated Meters.  This effort was undertaken at the direction of the California Public Utilities Commission to ensure the accuracy of this category of meters in the absence of standards for these devices.

Please see the attached letter and table that describes this effort and provides details on the specific tests the Working Group is proposing.  The proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE 1547, UL 1741, FCC Part 15 and Sandia/CEC Inverter Performance Test Procedures.

<<Inverter_Integrated_5%_Meters - ETL.doc>> <<Certification Tests for Inverter Integrated Meters v1 0 2-7-08.doc>>

We would greatly appreciate if you could review the document and provide comments and suggestions for the final certification requirements.  We are requesting a response no later than 3/28/2008 so that a final plan can be adopted as soon as possible.

Please contact me if you have any questions or comments on this request.

Kind Regards,

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.
77 Beale Street, Room 2731B
San Francisco, CA 94105-1814

Mailing Address:
Mail Code B27P
P.O. Box 770000
San Francisco, CA 94177-0001

Office: 415-973-1152
Cell:    415-328-1658
Fax:    415-973-2510
Email: j6...@pge.com

www.pge.com/solar
www.pge.com/selfgen




CONFIDENTIALITY NOTICE

This email may contain confidential or privileged information, if you are not the intended recipient, or the person responsible for delivering the message to the intended recipient then please notify us by return email immediately. Should you have received this email in error then you should not copy this for any purpose nor disclose its contents to any other person.
www.intertek.com <http://www.intertek.com>

Baak, Jim

unread,
Mar 20, 2008, 5:34:09 PM3/20/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
From KEMA.

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell:    415-328-1658
Fax:    415-973-2510

www.pge.com/solar
www.pge.com/selfgen

 


From: Baumstark, Pete [mailto:Pete.Ba...@us.kema.com]
Sent: Thursday, March 20, 2008 2:28 PM

To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification Requirements

Looks fine to me.
 

Pete Baumstark, PE
Energy Engineer

KEMA Services, Inc.
492 Ninth Street
Suite 220
Oakland, CA 94607
T (510) 891-0446, x-4111
F (510) 891-0440
pete.ba...@us.kema.com
Please visit our website www.kema.com  

This message may contain confidential or privileged information. If you are not the addressee, please return the message to its sender and delete it from your files.

 


From: Baak, Jim [mailto:J6...@pge.com]

Subject: Request to Review Inverter-Integrated Meter Certification Requirements

Pete,

On behalf of the California Solar Initiative's 5% Meter Certification Working Group, I am contacting you with a request to review our proposed 5% Accuracy Certification Requirements and Testing Procedures for Inverter-Integrated Meters.  This effort was undertaken at the direction of the California Public Utilities Commission to ensure the accuracy of this category of meters in the absence of standards for these devices.

Please see the attached letter and table that describes this effort and provides details on the specific tests the Working Group is proposing.  The proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE 1547, UL 1741, FCC Part 15 and Sandia/CEC Inverter Performance Test Procedures.

<<Inverter_Integrated_5%_Meters - KEMA.doc>> <<Certification Tests for Inverter Integrated Meters v1 0 2-7-08.doc>>

We would greatly appreciate if you could review the document and provide comments and suggestions for the final certification requirements.  We are requesting a response no later than 3/28/2008 so that a final plan can be adopted as soon as possible.

Baak, Jim

unread,
Mar 20, 2008, 7:03:01 PM3/20/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
FYI


Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

www.pge.com/solar
www.pge.com/selfgen

-----Original Message-----
From: Tony Dorta Intertek [mailto:tony....@intertek.com]

Sent: Thursday, March 20, 2008 3:50 PM
To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements

Jim, I see no issues with the changes except the fact that there are
requirements still being worked out. Once the final version is complete
I can see if any questions come up. We should be able to test to the new
updated standard right away. We have the EMC capabilities in several
labs already and inverter testing to UL 1741 can happen in out Cortland
lb for inverters up to 100kW. We also have the capacity to test at
client's site. The added testing per ANSI C12.1 is not an issue. Any of
our labs should be able to handle.
It would be ideal to have one of our test engineers present during the
test run so we iron out issues that only come up at the time of testing.

Tony Dorta
Staff Engineer
Intertek
Phone: (206) 248-8160
tony....@intertek.com
www.intertek-etlsemko.com

-----Original Message-----
From: "Baak, Jim" <J6...@pge.com>
To: "Tony Dorta Intertek" <tony....@intertek.com>
Cc: "onboard...@googlegroups.com"
<onboard...@googlegroups.com>; "andrew....@xantrex.com"
<andrew....@xantrex.com>; "Baak, Jim" <J6...@pge.com>;
"ben.g...@sce.com" <ben.g...@sce.com>; "Bob Botkin"
<Robert...@sce.com>; "Brian Farhi" <Brian...@sunpowercorp.com>;
"carissa...@sce.com" <carissa...@sce.com>;
"cwi...@imsmeters.com" <cwi...@imsmeters.com>; "Ivan Cooper"
<iv...@solarcity.com>; "jber...@sma-america.com"
<jber...@sma-america.com>; "Jeff Newmiller"
<jeff.ne...@bewengineering.com>; "Jerry Pilger"
<jerry....@sce.com>; "jon.bon...@sdenergy.org"
<jon.bon...@sdenergy.org>; "Joseph Fleshman"
<JFle...@energy.state.ca.us>; "mdar...@enphaseenergy.com"
<mdar...@enphaseenergy.com>; "mlaf...@universalenergies.com"
<mlaf...@universalenergies.com>; "n...@cpuc.ca.gov" <n...@cpuc.ca.gov>;
"oba...@smud.org" <oba...@smud.org>; "pat.ad...@veris.com"
<pat.ad...@veris.com>; "Pnar...@energy.state.ca.us"
<Pnar...@energy.state.ca.us>; "Raghu Belur" <rbe...@enphaseenergy.com>;
"ri...@fatspaniel.com" <ri...@fatspaniel.com>; "rjoh...@sunpowercorp.com"
<rjoh...@sunpowercorp.com>; "roger...@pvpowered.com"
<roger...@pvpowered.com>; "ste...@ccontrolsys.com"
<ste...@ccontrolsys.com>; "Tirona, William" <WR...@pge.com>
Sent: 3/20/08 9:34 AM


Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements

Tony,

Thank you very much for looking over these requirements. Are there
specific tests on which you have questions or comments? Once we get a
final version, how long would it take Intertek to get ready to conduct
the testing? What would you need from us to prepare?

Also, we have proposed looking for a NRTL and an inverter meter
manufacturer to do a "dry run" of the tests to iron out any issues and
establish a baseline of how the tests should be conducted and what
constitutes a "pass/fail". Do you have any suggestions for the group on
this? Would Intertek be interested in participating?

Regards,

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell: 415-328-1658
Fax: 415-973-2510

www.pge.com/solar
www.pge.com/selfgen

________________________________

From: Tony Dorta Intertek [mailto:tony....@intertek.com]
Sent: Wednesday, March 19, 2008 6:38 PM
To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements


Jim, I have gone through the changes to ANSI C12.1 and although some of
the requirements are still to be cleared up, Intertek can perform all of
the testing in this standard at several of our offices right now. We
have equipment and personnel to support these tests. Please feel free
to keep me updated on future changes and thank you for the email

Regards,

Tony Dorta
Assitant Chief Engineer

Intertek
Phone: (206) 248-8160
Fax: (503) 626-7328
Email Address: tony....@intertek.com

Website: www.intertek-etlsemko.com <http://www.intertek-etlsemko.com/>

This e-mail transmission is strictly confidential and is intended
solely for the identified person at the identified organization to whom
it is addressed. This e-mail may contain privileged and confidential
information. If you are not the intended recipient you must not copy,
print, distribute or take any action in reliance upon this e-mail. If
you have received this e-mail in error then please notify us as soon as
possible and delete this e-mail.


Although Intertek Group plc believes this e-mail and any attachments to
be free of any virus or other defect which may affect your computer, it
is the responsibility of the recipient to ensure that it is virus free
and Intertek Group plc does not accept any responsibility for any loss
or damage arising in any way from its use."

________________________________

From: Baak, Jim [mailto:J6...@pge.com]

Sent: Tuesday, March 18, 2008 2:48 PM
To: Tony Dorta Intertek

Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements


Thanks, Tony. I really appreciate your perspective on this,
particularly with respect to what is required for and how long it will
take Intertek to prepare for testing these inverter-integrated meters to
these requirements.

Regards,

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

Office: 415-973-1152
Cell: 415-328-1658
Fax: 415-973-2510

www.pge.com/solar
www.pge.com/selfgen

________________________________

From: Tony Dorta Intertek [mailto:tony....@intertek.com]
Sent: Tuesday, March 18, 2008 2:35 PM
To: Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements

Jim, I am trying to get a copy of the standard and I will go over the
changes proposed. Thanks

Regards,

Tony Dorta
Assistant Chief Engineer
Intertek
Phone: (206) 248-8160
Fax: (503) 626-7328
Email Address: tony....@intertek.com

Website: www.intertek-etlsemko.com <http://www.intertek-etlsemko.com/>

This e-mail transmission is strictly confidential and is intended
solely for the identified person at the identified organization to whom
it is addressed. This e-mail may contain privileged and confidential
information. If you are not the intended recipient you must not copy,
print, distribute or take any action in reliance upon this e-mail. If
you have received this e-mail in error then please notify us as soon as
possible and delete this e-mail.


Although Intertek Group plc believes this e-mail and any attachments to
be free of any virus or other defect which may affect your computer, it
is the responsibility of the recipient to ensure that it is virus free
and Intertek Group plc does not accept any responsibility for any loss
or damage arising in any way from its use."

________________________________

From: Baak, Jim [mailto:J6...@pge.com]

Sent: Friday, March 14, 2008 6:30 PM
To: Tony Dorta Intertek

Pnar...@energy.state.ca.us; Raghu Belur; Rich Eckman;


rjoh...@sunpowercorp.com; roger...@pvpowered.com;
ste...@ccontrolsys.com; Tirona, William
Subject: Request to Review Inverter-Integrated Meter Certification
Requirements

Tony,

On behalf of the California Solar Initiative's 5% Meter Certification
Working Group, I am contacting you with a request to review our proposed
5% Accuracy Certification Requirements and Testing Procedures for
Inverter-Integrated Meters. This effort was undertaken at the direction
of the California Public Utilities Commission to ensure the accuracy of
this category of meters in the absence of standards for these devices.

Please see the attached letter and table that describes this effort and
provides details on the specific tests the Working Group is proposing.
The proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE
1547, UL 1741, FCC Part 15 and Sandia/CEC Inverter Performance Test
Procedures.

<<Inverter_Integrated_5%_Meters - ETL.doc>> <<Certification Tests for


Inverter Integrated Meters v1 0 2-7-08.doc>>
We would greatly appreciate if you could review the document and provide
comments and suggestions for the final certification requirements. We
are requesting a response no later than 3/28/2008 so that a final plan
can be adopted as soon as possible.

Please contact me if you have any questions or comments on this request.


Kind Regards,

Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.
77 Beale Street, Room 2731B
San Francisco, CA 94105-1814

Mailing Address:
Mail Code B27P
P.O. Box 770000
San Francisco, CA 94177-0001

www.pge.com/solar <file://www.pge.com/solar>
www.pge.com/selfgen <file://www.pge.com/selfgen>

Baak, Jim

unread,
Mar 21, 2008, 5:06:00 PM3/21/08
to onboard...@googlegroups.com, andrew....@xantrex.com, Baak, Jim, ben.g...@sce.com, Bob Botkin, Brian Farhi, carissa...@sce.com, cwi...@imsmeters.com, Ivan Cooper, jber...@sma-america.com, Jeff Newmiller, Jerry Pilger, jon.bon...@sdenergy.org, Joseph Fleshman, mdar...@enphaseenergy.com, mlaf...@universalenergies.com, n...@cpuc.ca.gov, oba...@smud.org, pat.ad...@veris.com, Pnar...@energy.state.ca.us, Raghu Belur, ri...@fatspaniel.com, rjoh...@sunpowercorp.com, roger...@pvpowered.com, ste...@ccontrolsys.com, Tirona, William
More from IEEE. Note the reference corrections on 1547.


Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.

www.pge.com/solar
www.pge.com/selfgen

-----Original Message-----
From: Basso, Thomas [mailto:Thomas...@nrel.gov]
Sent: Friday, March 21, 2008 11:19 AM
To: w....@ieee.org; Baak, Jim
Subject: RE: Request to Review Inverter-Integrated Meter Certification
Requirements

Jim and Bill,

I don't see copyright and intellectual property issues the way Jim has
described their projected use of 1547 series of standards - but Bill is
the voice for the IEEE, not me.

In the table sent, there is only IEEE Std 1547 identified, but some of
those citations/references are actually to IEEE Std 1547.1.

Chuck Whitaker was involved in P1547.1 development so I'm sure he can
help sort out the details between 1547 and 1547.1.

Tom Basso - NREL Electric Systems Center Distributed Energy Systems
Integration
Thomas...@NREL.gov www.NREL.gov
Tel. 303 275-3753 Cell 303 514-0579 Fax 303 275-3835 NREL MS1614; 1617
Cole Blvd; Golden CO 80401

-----Original Message-----
From: w....@ieee.org [mailto:w....@ieee.org]

Sent: Monday, March 17, 2008 6:28 AM
To: Basso, Thomas
Subject: Fw: Request to Review Inverter-Integrated Meter Certification
Requirements


Hi Tom,
The first try didn't reach you. This one should.

Regards
******************************************************
Bill Ash
Senior Program Manager
IEEE Standards Activities Dept.
445 Hoes Lane
Piscataway, NJ 08854
PH: 732-465-5828
Email: w....@ieee.org
http://standards.ieee.org/
*****************************************************

IEEE.. . Fostering technological innovation and excellence for the
benefit
of humanity.

----- Forwarded by William A Ash/STDS/STAFF/US/IEEE on 03/17/2008 08:27
AM
-----

William A

Ash/STDS/STAFF/

US/IEEE
To
"Baak, Jim" <J6...@pge.com>

03/17/2008
cc
08:25 AM <thomas...@NREL.gov>


Subject
Re: Request to Review

Inverter-Integrated Meter

Certification Requirements(Document

link: William A Ash)

"Baak, Jim"

<J6...@pge.com>


To
03/14/2008 <w....@ieee.org>,

08:25 PM <thomas...@NREL.gov>


cc
<onboard...@googlegroups.com>,

"Hornbrook, Charles" <CL...@pge.com>,

<andrew....@xantrex.com>, "Baak,

Jim" <J6...@pge.com>,

<ben.g...@sce.com>, "Bob Botkin"

<carissa...@sce.com>,

<jber...@sma-america.com>, "Jeff

Newmiller"

<jeff.ne...@bewengineering.com>,

<JFle...@energy.state.ca.us>,

<mdar...@enphaseenergy.com>,

<mlaf...@universalenergies.com>,

<ri...@fatspaniel.com>,

<rjoh...@sunpowercorp.com>,

<roger...@pvpowered.com>,

<ste...@ccontrolsys.com>, "Tirona,

William" <WR...@pge.com>


Subject
Request to Review
Inverter-Integrated
Meter Certification Requirements

Bill and Tom,


On behalf of the California Solar Initiative's 5% Meter Certification
Working Group, I am contacting you with a request to review our proposed
5%
Accuracy Certification Requirements and Testing Procedures for
Inverter-Integrated Meters. This effort was undertaken at the direction
of
the California Public Utilities Commission to ensure the accuracy of
this
category of meters in the absence of standards for these devices.


Please see the attached letter and table that describes this effort and
provides details on the specific tests the Working Group is proposing.
The
proposed requirements make reference to ANSI/NEMA C12.1-2001, IEEE 1547,
UL
1741, FCC Part 15 and Sandia/CEC Inverter Performance Test Procedures.


<<Inverter_Integrated_5%_Meters - IEEE.doc>> <<Certification Tests for


Inverter Integrated Meters v1 0 2-7-08.doc>>

We would greatly appreciate if you could review the document to ensure


there are no copywrite or intellectual property right infringements or

concerns on behalf of IEEE. We are requesting a response from IEEE no


later than 3/28/2008 so that a final plan can be adopted as soon as
possible.


Please contact me if you have any questions or comments on this request.


Kind Regards,


Jim Baak
Senior Program Manager
Customer Generation
Pacific Gas & Electric Co.
77 Beale Street, Room 2731B
San Francisco, CA 94105-1814


Mailing Address:
Mail Code B27P:
P.O. Box 770000
San Francisco, CA 94177-0001


www.pge.com/solar
www.pge.com/selfgen

(See attached file: Inverter_Integrated_5%_Meters - IEEE.doc)(See
attached

file: Certification Tests for Inverter Integrated Meters v1 0
2-7-08.doc)