C# application to collect data from PAC3200 via MODBUS TCP

505 views
Skip to first unread message

David Ayala

unread,
Aug 19, 2010, 10:28:09 AM8/19/10
to NModbus
We need to develop a C# application for windows (xp, 7) to collect
data from several SENTRON PAC3200 devices. We are using an open source
Modbus driver, it has been downloaded from http://www.nmodbus.com/Default.aspx.htm.
Currently, I can connect to the device but then when I try to read
"InputRegiters" I get an exception indicating that 0 bytes have been
read from the device. Can you give any idea about how to proceed.

RaviKumar Balasubramaniam

unread,
Aug 22, 2010, 1:28:31 AM8/22/10
to nmodbus...@googlegroups.com
David,
 
Make sureyou are able to ping the modbus slave. Check the mosbus map of the vendor. Are you reading one register or two registers. I guess PAC3200 meter uses two registers for values.
 
-Ravi.


--