this is probably related to the deadband setting for your tags in the
tag configuration editor (TCE).
Here is an example:
tag update deadband = 1%
configured tag range = 0 to 100
real value range = 0 to 0.5
In this case the change in the value will never exceed 1% of the
configured range. Thus the engine will only update the tag once after
the engine launch.
Best regards,
Jochen Klier
NI-Germany
Change the OPC communication mode in DSC to synchronous communication
for the Kepware server(default is asynchronous and some OPC servers
don't work correctly using this method).
To do this navigate to Tools -> DSC Module -> Advanced -> Server
Browser and click on the button labeled "OPC Client Settings".
Then hit the "View All" button and select the Kepware server from the
list and hit the "Add" button.
Now your OPC server will appear in the Synchronous Communication list.
I hope this helps.
I've installed the Kepware OPC server and tried out the simulation
items. At first I had indeed the problem you are refering to in LV DSC
7.0 with LV 7. The tag gets only updated once. You need to change the
deadband but NOT the deadband you can find in: Edit
tag>Operations>engine> Update Deadband. The deadband you have to
change is: for example if you have the item:
Channel_0_User_Defined.Ramp.Ramp1 --> Go to Edit Tags> Connection
>Under I/O Group choose the Edit button> Change the deadband to zero.
Then it works fine.
Regards.
Joris Vanderschrick
Team Leader Application Engineering
NI Belgium